@johnmo no set backs in winter, just 24/7. I did get it to the point that it was working better but before that there were some days when it was very damp air and at 3/4 degrees just defrosting every 40 minutes or so all day so it struggled and then the outside temp would go to -5 at night.
it ended up OK but it’s clear that we have missed out by not having a LLH or volumiser fitted.
Posted by: @marvinator80@johnmo no set backs in winter, just 24/7. I did get it to the point that it was working better but before that there were some days when it was very damp air and at 3/4 degrees just defrosting every 40 minutes or so all day so it struggled and then the outside temp would go to -5 at night.
it ended up OK but it’s clear that we have missed out by not having a LLH or volumiser fitted.
The grant volumiser are quite good. Hook up as per their instructions think they say in the return pipes.
@dodgyknee hi, here's Group 46 parameters changed from default for me, default in [ ]
46 00 = 3 [0] heater enabled in supplementary mode
46 01 = 45.0 [50.0] set this to your maximum design LWT in heating
46 02 = 1 [5] 1 min delay on heater activation in defrost
46 05 = 0 [600] no integration time, there's already a 1min delay above
46 11 = -20 [5.0] don't want compressor to disable when heater enables!
46 13 = -5.0 [5.0] I only want immersion to boost heating when it gets really cold, below -5degC
46 14 = 2.0 [5.0] and switch off when outdoor temp rises to -3degC
46 20 = 3 [0] this enables the immersion heater to boost defrost function & be a second heat source in really cold weather.
46 23 = 38.0 [24.0] set higher than default, as I want the heater to come on 1m after defrost start, by which time the LWT is falling and soon reaches 38degC. If it doesn't energise until 24degC it's not really of any benefit.
Oh God.
I don’t know if I have done something to my Grant controller.
I held in the buttons to check LWT and parameters earlier and now when I do it it doesn’t seem to work. Just goes to resetting the date and time.
perhaps I am cracking up.
Oh God.
I don’t know if I have done something to my Grant controller.
I held in the buttons to check LWT and parameters earlier and now when I do it it doesn’t seem to work. Just goes to resetting the date and time.
perhaps I am cracking up.
and when I press the Return only button it just beeps and does nothing else. 😞
Posted by: @marvinator80Oh God.
I don’t know if I have done something to my Grant controller.
I held in the buttons to check LWT and parameters earlier and now when I do it it doesn’t seem to work. Just goes to resetting the date and time.
perhaps I am cracking up.
and when I press the Return only button it just beeps and does nothing else. 😞
Go on google (or other) and find and download a Chofu R32 installation manual. Everything you need to know will be in there.
Have you tried powering it down, counting to 10 and switching back on?
Posted by: @marvinator80@derek-m it worked. Thank you 🙏
You should always try the 'Universal' reset first if possible.
Unfortunately poorly written software can sometimes get its 'knickers in a twist' when buttons are pressed in the wrong sequence, rather than issuing the message 'what on Earth are you doing Dumbo'?
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 61 Online
- 5,662 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Does anyone have experience of a smart water meter?
Fortuitously I have a copy of a letter from the relevan...
By Transparent , 1 hour ago
-
Mitsubishi PAR-WT60R-E Wireless Controller installation
I asked a question about this previously, but things ha...
By DavidAlgarve , 2 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 21 hours ago
-
@bontwoody me too. I've contacted Heat Geek today, and ...
By Mars , 1 day ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 1 day ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 2 days ago
-
RE: Mitsu Wireless Controller and MelCloud
Well it has now become obvious that the installation of...
By DavidAlgarve , 2 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 3 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 4 days ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 4 days ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 5 days ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 5 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 6 days ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 7 days ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 7 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 7 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 1 week ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 1 week ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 1 week ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 1 week ago