Is it KISS or constant – weather compensation vs. set flow temperature?
Posted by: @cliffhangerCan't pm you I haven't enough posts.
Keep it out in the open! Others will want to have a look and possibly comment.
The heat loss report estimates the heat loss to be 7.42kW at -5.28°C (blimey, that's cold!), using what appears to be standard calculated methodology (areas U values air changes etc). There is a good chance this figure is too high, especially for an old building check the wall U values, there are also some links to published data on actual (measured) U values buried somewhere on the forum. Let's take 25% off: 5.5kW. The report mentions a Vaillant heat pump, but I thinks your is a Grant, either way, I think it is rated at 9kW. If these numbers (5.5 and 9) are correct, then there is a likely explanation for your heat pumps behaviour staring us in the face.
It is possible to get an empirical (measured) heat loss providing you have historical data of fuel usage (can be any fuel, but is easiest with gas). Basically, if your house is in steady state (steady room temp), then the energy being delivered to the house (energy in adjusted for efficiency) is the heat loss at that OAT. If you have such historical data, we can go through the method in more detail.
Midea 14kW (for now...) ASHP heating both building and DHW
@cliffhanger - thoughts on how to deal with your situation: I would still start with room stat set high and all TRVS etc open and then fine tune the weather compensation curve to as low as can be, but still sufficient to heat your home. It may take a lot of tweaking, all the more so if the heat pump is over-sized. It will struggle to lower output sufficiently (because it can only go down so far), and will end up cycling sooner than a less powerful model. Ignore what the curve numbers appear to be telling you - they are just numbers - and focus instead on the leaving water temp and room temp.
Midea 14kW (for now...) ASHP heating both building and DHW
- 21 Forums
- 1,969 Topics
- 42.7 K Posts
- 68 Online
- 2,295 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Should I make my radiators smaller?
The deviations can be handled by a) the lockshield v...
By JamesPa , 11 minutes ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
Interesting session to be involved with @editor and I s...
By Tim441 , 28 minutes ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
@vsmith1 I have a feeling that some ‘discretionary fact...
By Toodles , 56 minutes ago
-
Noted but (a) constant vs variable flow rate doesn't ma...
By JamesPa , 1 hour ago
-
RE: Transforming a Derbyshire Property into an Energy-Efficient Haven
Incredibly detailed piece @carpenterstation – thanks fo...
By Mars , 2 hours ago
-
RE: Who's your electricity provider and what's your tariff?
I haven't yet bothered optimising the heat pump cycle, ...
By JamesPa , 4 hours ago
-
@lucia thanks for the reply, I think I've now got suffi...
By big_si , 4 hours ago
-
RE: Battery storage to run Heat Pump.
Thanks I presume 3.86kW applies to export (is this co...
By JamesPa , 5 hours ago
-
RE: Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
Would be nice to see some data for Midea units, as thes...
By Old_Scientist , 5 hours ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
@cliffhanger - thoughts on how to deal with your situat...
By cathodeRay , 5 hours ago
-
RE: Setback savings - fact or fiction?
@jamespa - thank you for your ongoing heroic attempts t...
By cathodeRay , 5 hours ago
-
RE: Towel rails. An unexpected final hurdle
@davesoa No, unfortunately. I had to pay the VAT becaus...
By Lucia , 6 hours ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@editor I have been persuaded by the argument that you ...
By SUNandAIR , 7 hours ago
-
RE: SolarPV tables / online calculator
@majordennisbloodnok what degradation per year is typic...
By MichelleC , 7 hours ago
-
RE: Daikin Heat Pump Cycling Frequency?
I think your current method of logging F-gas pipe tempe...
By Mars , 18 hours ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
@cathoderay thank you, I will.
By Cathyem1 , 21 hours ago
-
RE: Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
Sorry, yes, 2105. OOPS! If I recall the unit circulates...
By AllyFish , 23 hours ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
No pressure or obligation, this discussion has moved on...
By JamesPa , 23 hours ago
-
RE: Split system and pipe lengths for air source heat pump installation
@johnmo got it. Thanks.
By nickmorgan , 1 day ago
Latest Topics
-
Should I make my radiators smaller?
By Scalextrix 41 minutes ago
-
Daikin Heat Pump Cycling Frequency?
By Ubert767 20 hours ago
-
Battery storage to run Heat Pump.
By Broadsman 1 day ago
-
Heat Pump Sizing & Installation Costs
By Mars 2 days ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 2 days ago
-
SolarPV tables / online calculator
By MichelleC 3 days ago