Increase floor temps for UFH, Samsung Gen6
We have a new build, well Insulated. 160mm PIR floor, 150mm PIR roof, 125mm full fill walls. Meticulously checked by me throughout installation. Air tightness of 3, likely due to multiple sets of sliding doors.
We are on octopus cosy, and for the last 12 months average about £160 a month, inclusive of Elec cooking, daily dish washer, daily washing machine, twice weekly tumble dryer etc.we go through a lot of hot water. We get away with the cheap heating periods, albeit it for cold snaps we do need to extend the hours noticeably.
We have a Samsung gen6 12kw ASHP, powering two UFH manifolds (one with 13 zones, other 5 zones). No buffer tank. From what I can tell we don't short cycle?
However the bungalow does have an inefficient design... . Very very high ceilings, sprawling a bit, lots of glass. Children's rooms have small floor space, but then a Mezzanine in them to give them two stories under a 4.5m bungalow roof. It's cool, but means they are tricky to heat die to surface area if UFH vs volume of room.
Now everything works well, however during these sub zero the children's rooms struggle to heat behind 18 degrees due to the design.
I am keen to see if I can force increase the UFH temps. Especially as the pays are nicely cheap in my mind, and the cosy periods at 11p mean I want to hammer them vs extending the hours excessively into the 24p tariffs.
My Samsung water law settings are....
Outdoor temp for water law:
15 degrees ........3.0
Water out temp for WL1 Heat (WL1 floor)
36 degrees..... 43degrees high target
Water temp out for WL2 Heat (wl2-fcu)
36 degs....... 43 degrees
However even setting the offset to +5 degrees, after 4 hours of operation the outflow temp is still only 29 degrees, and the rooms are all a couple degrees colder then I would like.
Welcome any recommendations. I know I could run the ASHP for longer... But the 11p vs 24p tariff change means I am keen to loose efficiency to make more usage of it.
Thank you!
Posted by: @andehhHowever even setting the offset to +5 degrees, after 4 hours of operation the outflow temp is still only 29 degrees, and the rooms are all a couple degrees colder then I would like.
4 hours isn't very long, houses have a large heat capacity (ie energy stored in the fabric) and can therefore take a day or more to reach a steady temperature. Is it possible that you have hit the maximum output of the heat pump which, if it were the case, would explain what you are seeing? ASHPs are generally sized on the assumption that they are run full time; if you are only running part time you could quite easily be hitting max output even though 12kW is quite a large ASHP. What was the design loss at what OAT and for how many hours are you running?
If you have in fact reached the max output capacity then there is not much more you can do with the heat pump. At this point its either run it for longer (as intended) or deploy some supplementary heating. Remember its only this cold for a few days of the year so if you hammer your electricity bill for a few days its not so much in the grand scheme of things. You do have to think about any heating, but particularly ASHPs, over a season since load varies quite dramatically.
@andehh, do you have a way of monitoring the power being produced by the ASHP when the UFH is on or, failing that, can you check the Instantaneous Usage shown in the Energy information display?
With your Water Law settings and the +5C set point, the target output temperature should be 48C when the outside air temperature is 3C or lower. If the output temperature is only 29C then I would expect the ASHP to be running up to its 12kW maximum to achieve the target (with regular defrost cycles given the low outside temperature).
With my Samsun 8kW Gen 6 it is very obvious from the noise when it is running at maximum during the DHW cycle. How does your 12kW unit sound during heating and DHW operation?
The reason I am asking about the power output is that my 8kW unit is regularly failing to achieve the Water Law target temperature but it is running well below full power, see this topic.
Highest draw I've seen from it is about 5kw input via the instantaneous power menu , though I don't check it too often. From octopus half hourly it seems to only pull 2 to 2.4kw over a 30min window on average..... Ie 4am to 7am slot. DHW is the same.
I presume this is ok? 2.4kw x my Cop of 3.5 ish comes close to the 12kw which I imagine is the OUTPUT up to?
And yes.... It could be 29 degrees is as hot as it can get if the whole slab is relatively cool from a period of 3-5 hours of a heat off cycle I guess?
I have added an extra 2 hours a day onto the schedule and will monitor, maybe add a couple more each time until 'cold' winter passes and then I'll reduce it back to cosy periods for the shoulder months.
- 21 Forums
- 1,875 Topics
- 40.9 K Posts
- 25 Online
- 2,196 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump? Or already have one but it’s not performing as it should? Rob is here to help!
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
Latest Posts
-
RE: Vaillant Arotherm ASHP gets noisier when it gets colder outside
I didn’t hear any problem with that noise it was less t...
By Judith , 7 hours ago
-
RE: New Project! ASHP, Solar PV + Battery, MVHR!
@editor yes please Mars, that would be fantastic.
By nickmorgan , 8 hours ago
-
Struggling to Find a Top Heat Pump Installer? We Can Connect You With the Best Installers in the UK
We know from homeowner’s posts and emails how stressful...
By Mars , 9 hours ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
@cathoderay Our 01.00 to 06.00 electricity tariff is go...
By Cathyem1 , 9 hours ago
-
-
RE: Recommendation for Consultants in West Yorkshire for 1850's House Installation
Welcome to the forums. I’ll connect you some recommende...
By Mars , 10 hours ago
-
RE: Large ASHP recommendations for listed house
I’ll connect you via email (using the email address you...
By Mars , 10 hours ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
An update - got through to a helpful Octopus employee, ...
By samiebon1 , 11 hours ago
-
There should be no significant change in the load on th...
By JohnR , 12 hours ago
-
RE: Ideal Logic 10kW Heat Pump Pipes Noisy and Very Expensive to Run
@ajbevster If it's fully pushed in yes, better if it...
By JamesPa , 12 hours ago
-
RE: Controversial opinions - pure weather compensation, buffer tank, heat loss, oversized heat pumps
@heatgeek Thank you, yes this is quite a meal and I'...
By Uk_pete_2000 , 13 hours ago
-
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Its the actual flow rate, after you have bypassed the b...
By JamesPa , 16 hours ago
-
RE: The good, the bad and the not that great – my heat pump installation
@lokisam Thank you for reply. I have posted here bef...
By Dwynwen , 19 hours ago
-
RE: Is My Midea Heat Pump Inherently Defective?
Absolutely, I am very aware of that! Moving to a fan co...
By cathodeRay , 20 hours ago
-
-
RE: Noise problems with newly installed Samsung 8kW ASHP
@odynsfee Hi, I only just saw your post. Sorry to hear ...
By Lokisam , 1 day ago
-
RE: Best way to heat and store hot water with ASHP and Solar - am I being stupid?
@nickmorgan you’re absolutely spot on with your thinkin...
By Mars , 1 day ago
-
RE: Grant Aerona3 with Octopus Cosy tariff
Unless I completely misunderstood you (in which case ap...
By JamesPa , 2 days ago
Latest Topics
-
By bretix 15 hours ago
-
Large ASHP recommendations for listed house
By Greenlover75 17 hours ago
-
VisitaHeatPump Participants - Guidance Please
By Toodles 2 days ago
-
By KundK 2 days ago
-
Pipes and cables exposed on roof
By MichelleC 2 days ago
-
By Silverkop 3 days ago
-
Baxi Air Source Heat Pump tips and tricks please
By Cathyem1 3 days ago