Figures fluctuated slightly, heating is currently on
Posted by: @jgtukpd0= 31
1 = 60
2 = 52
3 = 5100
4 = 600
5 = -4
6 = 2
7 = 4400
8 = -3
9 = 41
Okay, you have displayed the following information
And it tells me you are using 5kw (#03) at this time. With a flow temp of 41°c (#09) and a return of 31°c (#00)
That's very high, but before anyone makes changes, there are a couple of questions to ask
1/ is the house comfortable, too hot, too cold?
2/ do you just have the one thermostat controlling the system and where it it located ?
3/ do you turn down any rad / ufh when its on ?
The house is slightly chilly for most people, could be warmer.
One thermostat for upstairs and another for downstairs both set to 18 degrees
Only have rads, some turned down (TRV) in smaller rooms but larger rooms feel colder
Thank you for that, I would have expected the system to be running a lot less than that and does imply there may be a problem.
Sorry to ask, but it will help. You say its a Stone house, 5 bed. Are these solid walls, no air gap, and/or little insulation ?
Do you know your house heat loss ?
As the HP has a high flow temp and you had rads changed they should be warm to the touch (ie they are not too hot like gas boiler, but not cold to the touch) ?
I would say they put a buffer in with 4 ports. One side connects to the HP, the other to the CH ? If so, can you feel the two top pipes. I suspect the HP side will be warmer than the CH side (if possible test will thermostat and register the temp)
@jgtukpd yes that looks like it. The size indicates a low loss header.
The left goes to the HP, the right to the CH (?). If correct, then there is the one pump for the CH and two pipes ( right side bottom), come back from the two zones you have.
Feel the two pipes at the top.
Note. Forgot to say, on the controller press the Return key till bleep and the display will go back to normal.
Heat energy being thrown away.
Pipe insulation needs re-doing so that it seals around all open metalwork.
See this article.
Save energy... recycle electrons!
With ch running, hp side (rh top) is reading hotter than ch side (lh top).
Using a cheap led thermometer they’re reading a couple of degrees apart (37.2 degrees and 35.1 degrees)
Posted by: @jgtukpdWith ch running, hp side (rh top) is reading hotter than ch side (lh top).
Using a cheap led thermometer they’re reading a couple of degrees apart (37.2 degrees and 35.1 degrees)
Interesting, the pump on the right (of the photo) is normally inside the HP and another one is not needed inside the house.
Also there is a big drop from the flow out of the HP (#09 @ 41c) to 37.2c, it could be the thermostat itself though.
Okay, from the information we have, though the reading don't quite match it up I suspect the following
The HP and settings have been installed, as Grant send them out. The HP pump is set as high (#07 4400) and I suspect you are running just flow temp and not WC.
This means all your heated water is being sent back to the HP and not into your CH. It does means with some changes, you should see a reduction in cost etc.
As one of the changes is inside the HP unit I'm going to ask you to contact Grant themselves. You need to tell them that you suspect the HP flow pump is set to high and WC is not turned on. Also, if it was a Grant recommended installer, that you have been having problems with them to get it sorted (Spin a yarn etc).
The other point to discuss is @transparent notes about 3ph / single phase and how it may work.
A third thing to look at is insulation on the pipes, if they have done the same outside, these need fixing.
Another thing I would look at is checking all rads have been bleed, new systems / setup should be done more often till they settle down
If you get no joy from Grant let us know
Edit - just to check, the readings from the controller where taken when the HP was in CH mode and not doing DHW ?
Pipe insulation is inexpensive.
It's a very important part of your heat pump installation, and needs doing well.
Here's Class-O Nitrile-rubber pipe insulation from BES.
They offer Kaiflex. Armacell is similar.
You need a wall thickness of at least 13mm.
Use 19mm if space permits.
Lap over any gaps using the 3mm thick tape.
They offer large-diameter lengths of 42mm and 54mm which should work OK for valves.
Join splits and ends together using a standard contact adhesive.
For external pipe insulation, use the products with UV resistance, usually sold for solar thermal arrays.
Ensure that no rain can enter between the insulation and the pipe.
Seal the ends with a smear of waterproof acrylic mastic such as CT1, which you can apply to wet surfaces.
Post a photo here of where the pipework enters the house from the external unit.
This should be insulated right the way through the wall, and have an impact-resisting sleeve around that.
Save energy... recycle electrons!
Brilliant. I have Grant coming to perform a service next month so will address those things then.
My electrician told me that although we have 3 phase, the HP is running on just one of the phases.
Most of the pipework is insulated, the worst is on that photo. All of the exterior is well insulated.
Rads are all bled and seem to have even heat.
I'll update as soon as i see the Grant engineer.
Many thanks for your time today, it's much appreciated.
- 22 Forums
- 2,058 Topics
- 44.9 K Posts
- 17 Online
- 3,308 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@editor yes, alarm bells are ringing for me to. Still,...
By GrahamF , 18 minutes ago
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
This is indeed welcome news. In addition the new legi...
By JamesPa , 6 hours ago
-
RE: Is your heat pump insured?
@benson fairly typical of some insurers.
By KevinPotts , 17 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@majordennisbloodnok I am wearing a glazed expression n...
By Toodles , 18 hours ago
-
RE: Rate the quality of your heat pump design and installation
Yes the HP is running weather compensation and I’ve lef...
By Davesoa , 1 day ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
OK, so when the HP comes on it becomes obvious.It's on ...
By tdudgeon , 2 days ago
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
@johnmo I think we’ve been trudging through the same...
By SUNandAIR , 2 days ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 3 days ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 3 days ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 3 days ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 3 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 4 days ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Hopefully iv done the right thing today by signing up t...
By Westkent , 4 days ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 4 days ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 4 days ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
The useful bit is the bit that specifies the heat loss ...
By JamesPa , 4 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 4 days ago
-
@editor thanks Mars that’s the same table I found in th...
By Gary , 5 days ago
-
RE: Tariff and charging strategy advice please
They haven't asked me to prove that I have an EV (I do)...
By JamesPa , 5 days ago