The schematic on page 24 is the closest I could find with your system, the difference is you have a buffer tank instead of a 40 litre decoupler but they do similar jobs.
The system design is not straight forward and I would strongly recommend working your way through the components to understand the potential impact of each. I’ve also had issues with laser thermometers on pipes so would recommend some clip on pipe dial pipe thermometers from a plumbers merchant.
Record the temps in order:
1. Hex module (box on wall) right side red and blue are the feed from the heat pump and return. This is the closest to the heating source and will give you a means of comparison to the Vr10 temp probe which is in the top of the buffer tank and should be readable from the VR700 under the configuration screen assuming you have the installer codes.
There are a number of adjustable points in this system, hex module pump, radiator pump, ufh pump, not to mention just balancing the radiators. This added with the fact it looks like you have bypass valves on both the flow to the radiators and the ufh (which could be passing flow in to the return).
All these points can be adjusted but consistently measuring the temps from around the system you will be able to locate if it is system setup or design.
Posted by: @webcmgPosted by: @derek-mHi,
It would appear that your buffer tank has 2 input pipes and 4 output pipes, which is now making more sense. So what temperatures are you getting on the various pipes?
I don't have equipment to measure the temperature accurately (plumber did the last readings), but with an infrared laser thermometer I'm getting
UFH
- 20.3 flow
- 18 return
Radiators
- 21.4 flow
- 19 return
Flow temp on the programmer at the time was 33, target was also 33.
Hi,
I can't remember if you said yours is a newly installed system that has never performed correctly?
I have been working for while with a lady experiencing similar problems to yourself, and after numerous tests I'm coming to the conclusion that the main problem is associated with the water flow around the buffer tank.
If the water flow around the buffer tank is correct, then the temperature of the water flowing out of the buffer tank to your radiators and UFH, should be approximately the same temperature as the water flowing into the buffer tank from the ASHP. In the same manner, the return water from the buffer tank to the ASHP, should be at approximately the same temperature as the return water from the radiators and UFH going into the buffer tank. When the system is functioning correctly there should be a delta T of approximately 5C between flow and return temperatures.
As an example, if the water flow temperature coming from the heat pump is 35C, then the water going to the radiators and UFH should be approximately the same. The return water coming from the radiators and UFH should be in the region of 30C, as should the temperature of the return water to the heat pump. Any large differences would probably be caused by mixing within the buffer tank, which of course will affected the operation and efficiency of your system.
You could try measuring the temperature of the pipework around your system by using your IR temperature gun, but if you do not get meaningful results then purchasing one or two cheap temperature meters may be worthwhile.
Posted by: @webcmgPosted by: @derek-mHi,
It would appear that your buffer tank has 2 input pipes and 4 output pipes, which is now making more sense. So what temperatures are you getting on the various pipes?
I don't have equipment to measure the temperature accurately (plumber did the last readings), but with an infrared laser thermometer I'm getting
UFH
- 20.3 flow
- 18 return
Radiators
- 21.4 flow
- 19 return
Flow temp on the programmer at the time was 33, target was also 33.
Hi,
Did you manage to resolve your problems? Feedback would be welcome.
Posted by: @derek-mPosted by: @webcmgPosted by: @derek-mHi,
It would appear that your buffer tank has 2 input pipes and 4 output pipes, which is now making more sense. So what temperatures are you getting on the various pipes?
I don't have equipment to measure the temperature accurately (plumber did the last readings), but with an infrared laser thermometer I'm getting
UFH
- 20.3 flow
- 18 return
Radiators
- 21.4 flow
- 19 return
Flow temp on the programmer at the time was 33, target was also 33.
Hi,
I can't remember if you said yours is a newly installed system that has never performed correctly?
I have been working for while with a lady experiencing similar problems to yourself, and after numerous tests I'm coming to the conclusion that the main problem is associated with the water flow around the buffer tank.
If the water flow around the buffer tank is correct, then the temperature of the water flowing out of the buffer tank to your radiators and UFH, should be approximately the same temperature as the water flowing into the buffer tank from the ASHP. In the same manner, the return water from the buffer tank to the ASHP, should be at approximately the same temperature as the return water from the radiators and UFH going into the buffer tank. When the system is functioning correctly there should be a delta T of approximately 5C between flow and return temperatures.
As an example, if the water flow temperature coming from the heat pump is 35C, then the water going to the radiators and UFH should be approximately the same. The return water coming from the radiators and UFH should be in the region of 30C, as should the temperature of the return water to the heat pump. Any large differences would probably be caused by mixing within the buffer tank, which of course will affected the operation and efficiency of your system.
You could try measuring the temperature of the pipework around your system by using your IR temperature gun, but if you do not get meaningful results then purchasing one or two cheap temperature meters may be worthwhile.
@Derek-M what was the solution to this issue?
Hi @webcmg
The ladies problem has not yet been fully resolved, to do so may mean alterations to the pipework around the buffer tank.
With your particular system I would suggest that you identify where the pipework around your buffer tank is connected, check for any closed valves and whether or not any pumps are running. Then measure the temperatures of the pipework and to try to ascertain where the water may be flowing.
Posted by: @derek-mPosted by: @webcmgPosted by: @derek-mHi,
It would appear that your buffer tank has 2 input pipes and 4 output pipes, which is now making more sense. So what temperatures are you getting on the various pipes?
I don't have equipment to measure the temperature accurately (plumber did the last readings), but with an infrared laser thermometer I'm getting
UFH
- 20.3 flow
- 18 return
Radiators
- 21.4 flow
- 19 return
Flow temp on the programmer at the time was 33, target was also 33.
Hi,
Did you manage to resolve your problems? Feedback would be welcome.
Hi @derek-m - the plumber popped over today so was able to get some readings which are as follows:
Buffer
Flow 34
Return 31
Radiator circuit
Flow 34
Return 29
Radiator circuit (nearer buffer)
Flow 34
Return 31
UFH circuit without running radiators
Flow 31
Return 27
From ASHP to buffer
36 flow
33 Return
Radiator circuit when also running UFH
30 Flow
28 Return
Underfloor when also running Radiators
32 flow
28 return
All looks pretty normal?
Posted by: @derek-mSo what are the room temperatures?
@derek-m It's hard to tell because it's been warmer outside (10 degrees today) and I had to put the heat curve up to 0.9 in order to get any heat in the rads. It's now been escalated within Vaillant because they've accepted that the system isn't operating as per their design specification (i.e. comfort at the right level of economy).
Posted by: @webcmgPosted by: @derek-mSo what are the room temperatures?
@derek-m It's hard to tell because it's been warmer outside (10 degrees today) and I had to put the heat curve up to 0.9 in order to get any heat in the rads. It's now been escalated within Vaillant because they've accepted that the system isn't operating as per their design specification (i.e. comfort at the right level of economy).
Hi,
What I meant is what is the actual temperature in the various rooms, and are they remaining reasonably constant or are they varying with the outdoor air temperature?
@webcmg why did you want heat in the radiators…the whole point of any heating system is to have warm rooms, NOT hot radiators!
Professional installer
Posted by: @alec-morrow@webcmg why did you want heat in the radiators…the whole point of any heating system is to have warm rooms, NOT hot radiators!
Yes, but if the radiators aren't even warm... Then it's unlikely the room will be warm either. Quick update. Vaillant have been investigating, no real progress, no major changes proposed. Upstairs cold when it's cold outside. Seriously frustrated and disappointed.
-
ASHP install contract and BUS grant money
6 days ago
-
Savings - using Weather Compensation & Time of Use Tariffs
2 weeks ago
-
Heat Pump starting current
1 month ago
-
Running my new Nibe ASHP efficiently
1 month ago
-
Air source heat pump problems - NIBE F 2040 ASHP
2 months ago
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 52 Online
- 2,277 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 2 hours ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 3 hours ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami I think if the heat loss documentation matches a ...
By bontwoody , 3 hours ago
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa I'm afraid that's over my head but if anyon...
By IRMartini , 3 hours ago
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 4 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 4 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 5 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 8 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 10 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 22 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 1 day ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 10 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 11 hours ago
-
SolarPV tables / online calculator
By MichelleC 18 hours ago
-
By Toodles 2 days ago