The schematic on page 24 is the closest I could find with your system, the difference is you have a buffer tank instead of a 40 litre decoupler but they do similar jobs.
The system design is not straight forward and I would strongly recommend working your way through the components to understand the potential impact of each. I’ve also had issues with laser thermometers on pipes so would recommend some clip on pipe dial pipe thermometers from a plumbers merchant.
Record the temps in order:
1. Hex module (box on wall) right side red and blue are the feed from the heat pump and return. This is the closest to the heating source and will give you a means of comparison to the Vr10 temp probe which is in the top of the buffer tank and should be readable from the VR700 under the configuration screen assuming you have the installer codes.
There are a number of adjustable points in this system, hex module pump, radiator pump, ufh pump, not to mention just balancing the radiators. This added with the fact it looks like you have bypass valves on both the flow to the radiators and the ufh (which could be passing flow in to the return).
All these points can be adjusted but consistently measuring the temps from around the system you will be able to locate if it is system setup or design.
Posted by: @webcmgPosted by: @derek-mHi,
It would appear that your buffer tank has 2 input pipes and 4 output pipes, which is now making more sense. So what temperatures are you getting on the various pipes?
I don't have equipment to measure the temperature accurately (plumber did the last readings), but with an infrared laser thermometer I'm getting
UFH
- 20.3 flow
- 18 return
Radiators
- 21.4 flow
- 19 return
Flow temp on the programmer at the time was 33, target was also 33.
Hi,
I can't remember if you said yours is a newly installed system that has never performed correctly?
I have been working for while with a lady experiencing similar problems to yourself, and after numerous tests I'm coming to the conclusion that the main problem is associated with the water flow around the buffer tank.
If the water flow around the buffer tank is correct, then the temperature of the water flowing out of the buffer tank to your radiators and UFH, should be approximately the same temperature as the water flowing into the buffer tank from the ASHP. In the same manner, the return water from the buffer tank to the ASHP, should be at approximately the same temperature as the return water from the radiators and UFH going into the buffer tank. When the system is functioning correctly there should be a delta T of approximately 5C between flow and return temperatures.
As an example, if the water flow temperature coming from the heat pump is 35C, then the water going to the radiators and UFH should be approximately the same. The return water coming from the radiators and UFH should be in the region of 30C, as should the temperature of the return water to the heat pump. Any large differences would probably be caused by mixing within the buffer tank, which of course will affected the operation and efficiency of your system.
You could try measuring the temperature of the pipework around your system by using your IR temperature gun, but if you do not get meaningful results then purchasing one or two cheap temperature meters may be worthwhile.
Posted by: @webcmgPosted by: @derek-mHi,
It would appear that your buffer tank has 2 input pipes and 4 output pipes, which is now making more sense. So what temperatures are you getting on the various pipes?
I don't have equipment to measure the temperature accurately (plumber did the last readings), but with an infrared laser thermometer I'm getting
UFH
- 20.3 flow
- 18 return
Radiators
- 21.4 flow
- 19 return
Flow temp on the programmer at the time was 33, target was also 33.
Hi,
Did you manage to resolve your problems? Feedback would be welcome.
Posted by: @derek-mPosted by: @webcmgPosted by: @derek-mHi,
It would appear that your buffer tank has 2 input pipes and 4 output pipes, which is now making more sense. So what temperatures are you getting on the various pipes?
I don't have equipment to measure the temperature accurately (plumber did the last readings), but with an infrared laser thermometer I'm getting
UFH
- 20.3 flow
- 18 return
Radiators
- 21.4 flow
- 19 return
Flow temp on the programmer at the time was 33, target was also 33.
Hi,
I can't remember if you said yours is a newly installed system that has never performed correctly?
I have been working for while with a lady experiencing similar problems to yourself, and after numerous tests I'm coming to the conclusion that the main problem is associated with the water flow around the buffer tank.
If the water flow around the buffer tank is correct, then the temperature of the water flowing out of the buffer tank to your radiators and UFH, should be approximately the same temperature as the water flowing into the buffer tank from the ASHP. In the same manner, the return water from the buffer tank to the ASHP, should be at approximately the same temperature as the return water from the radiators and UFH going into the buffer tank. When the system is functioning correctly there should be a delta T of approximately 5C between flow and return temperatures.
As an example, if the water flow temperature coming from the heat pump is 35C, then the water going to the radiators and UFH should be approximately the same. The return water coming from the radiators and UFH should be in the region of 30C, as should the temperature of the return water to the heat pump. Any large differences would probably be caused by mixing within the buffer tank, which of course will affected the operation and efficiency of your system.
You could try measuring the temperature of the pipework around your system by using your IR temperature gun, but if you do not get meaningful results then purchasing one or two cheap temperature meters may be worthwhile.
@Derek-M what was the solution to this issue?
Hi @webcmg
The ladies problem has not yet been fully resolved, to do so may mean alterations to the pipework around the buffer tank.
With your particular system I would suggest that you identify where the pipework around your buffer tank is connected, check for any closed valves and whether or not any pumps are running. Then measure the temperatures of the pipework and to try to ascertain where the water may be flowing.
Posted by: @derek-mPosted by: @webcmgPosted by: @derek-mHi,
It would appear that your buffer tank has 2 input pipes and 4 output pipes, which is now making more sense. So what temperatures are you getting on the various pipes?
I don't have equipment to measure the temperature accurately (plumber did the last readings), but with an infrared laser thermometer I'm getting
UFH
- 20.3 flow
- 18 return
Radiators
- 21.4 flow
- 19 return
Flow temp on the programmer at the time was 33, target was also 33.
Hi,
Did you manage to resolve your problems? Feedback would be welcome.
Hi @derek-m - the plumber popped over today so was able to get some readings which are as follows:
Buffer
Flow 34
Return 31
Radiator circuit
Flow 34
Return 29
Radiator circuit (nearer buffer)
Flow 34
Return 31
UFH circuit without running radiators
Flow 31
Return 27
From ASHP to buffer
36 flow
33 Return
Radiator circuit when also running UFH
30 Flow
28 Return
Underfloor when also running Radiators
32 flow
28 return
All looks pretty normal?
Posted by: @derek-mSo what are the room temperatures?
@derek-m It's hard to tell because it's been warmer outside (10 degrees today) and I had to put the heat curve up to 0.9 in order to get any heat in the rads. It's now been escalated within Vaillant because they've accepted that the system isn't operating as per their design specification (i.e. comfort at the right level of economy).
Posted by: @webcmgPosted by: @derek-mSo what are the room temperatures?
@derek-m It's hard to tell because it's been warmer outside (10 degrees today) and I had to put the heat curve up to 0.9 in order to get any heat in the rads. It's now been escalated within Vaillant because they've accepted that the system isn't operating as per their design specification (i.e. comfort at the right level of economy).
Hi,
What I meant is what is the actual temperature in the various rooms, and are they remaining reasonably constant or are they varying with the outdoor air temperature?
@webcmg why did you want heat in the radiators…the whole point of any heating system is to have warm rooms, NOT hot radiators!
Professional installer
Posted by: @alec-morrow@webcmg why did you want heat in the radiators…the whole point of any heating system is to have warm rooms, NOT hot radiators!
Yes, but if the radiators aren't even warm... Then it's unlikely the room will be warm either. Quick update. Vaillant have been investigating, no real progress, no major changes proposed. Upstairs cold when it's cold outside. Seriously frustrated and disappointed.
-
Installing your own ASHP - DIY
3 weeks ago
-
ASHP install contract and BUS grant money
2 months ago
-
Savings - using Weather Compensation & Time of Use Tariffs
3 months ago
-
Heat Pump starting current
3 months ago
-
Running my new Nibe ASHP efficiently
3 months ago
- 22 Forums
- 2,058 Topics
- 45 K Posts
- 53 Online
- 3,314 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Renewables & Heat Pumps in the News
The update above was posted here a few days ago along w...
By Jeff , 40 minutes ago
-
RE: Grant Aerona3 - Home Assistant control via Modbus
And I also did a thing!!!!! In my quest to learn all th...
By Grantmethestrength , 41 minutes ago
-
RE: Commencing on an ASHP Installation Process
I'm not sure expecting consensus from installers is rea...
By JamesPa , 11 hours ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
There is consensus that the current model isn't fit for...
By Jeff , 14 hours ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
Mine has been doing a CoP of -3.18, yes negative, combi...
By Johnmo , 19 hours ago
-
RE: Battery sizing - How low can you go!
The second 6.5 kWh Growatt battery was installed today....
By ChandyKris , 21 hours ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
Thanks for that thoughtful reply. Unfortunately we g...
By JamesPa , 22 hours ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
So… I called them this morning and I’m up and running o...
By Westkent , 22 hours ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
Your system seems to be more modern than mine, mine was...
By abbote , 1 day ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
Braver person than me. No way I would go down that rout...
By Johnmo , 2 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@arundalep yes I have no issue with this. The observati...
By benson , 2 days ago
-
-
RE: Rate the quality of your heat pump design and installation
So your Halo lite should really do nothing, when connec...
By Johnmo , 2 days ago
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
This is indeed welcome news. In addition the new legi...
By JamesPa , 2 days ago
-
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
@johnmo I think we’ve been trudging through the same...
By SUNandAIR , 4 days ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 5 days ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 5 days ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 6 days ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 6 days ago