Posted by: @lfranklin
- @derek-m yes the vessel (buffer I think new one says) was exchanged and is fully pressurised and have checked system fully for any air.
Do you have a suitable thermometer or thermometers that could be used to measure both room temperatures, and could also be taped to radiators and pipework (with suitable insulation) to measure the system temperatures.
Starting from the pipework leaving the heat pump, could you work your way through the system and provide both wide angle and close up photo's of any equipment that you locate, things like valves, pumps, cylinders etc.
Posted by: @william1066Posted by: @derek-mWe can then try to go through your system operation in a logical and systematic manner.
@lfranklin - there is definitely two (or potentially more) components to this, and as Derek said, being systematic will speed things up. From what I can determine in the thread, there are a whole bunch of things that need addressing. My summary is as follows.
- can hear expansion vessel working and its very annoying when trying to sleep
- struggling with system not heating two rads on the system
- added a second pump onto the return side of the system trying to fix problem 2 above and that seemed to help for a few hours when first installed but now not coming back on again
- if i turn the TRV off on others earlier in the system off the last two do get warm but even then not hot
- We had solar installed at the time too (16 x 405w panels) and even that isn't working right at just 1-1.8kwh per day generation at the moment
- wired remote controller showing water pump and some other bits and a very high heat water temp on main front screen even though heating has been off
- heating stopped all together today despite pump running and eating lots of electric!
- DHW not getting up to temp and so not letting the radiators have hot water
1,2,3,4 and 8 could be combined into a single group, which is likely [mostly] plumbing rather than heat pump settings related. (with the caveat that for heat pumps you should be going for warm radiators, not hot radiators)
Item 5 probably needs its own thread on this forum.
6 is likely config/understanding of the Samsung Gen6 system operation
7 probably a mixture of hive, samsung settings, plumbing
I can probably help with 6, the rest, not so much.
To save me having to forage through the Samsung manual, do you know where the control settings for booster or back up heaters are located, and if they can be disabled if necessary?
From what @lfranklin has previously stated, you have correctly identified that there could be a number of issues.
My suggestion would be to initially set the system to operate in fixed LWT mode, and then carry out temperature measurements around the system to try to identify where the heat energy is flowing. Could you therefore explain how to set the system to fixed LWT at say 40C?
@derek-m The easiest way that I found to do this was to set the weather compensation to 40 at minimum and 40 at maximum outside temperatures. That way it’s always going to be 40° C. There is another way, I presume but I haven’t found it!
Posted by: @derek-mTo save me having to forage through the Samsung manual, do you know where the control settings for booster or back up heaters are located, and if they can be disabled if necessary?
The booster heater can be disabled [#3031], but you can also disable it by making sure your hot water is on economical setting, not standard, power or forced. That you can do in the schedul
The benefit of leaving it enabled is to speed things up when needed, by just changing the mode on the remote controller (not so convenient if in the loft)
Posted by: @lfranklinI think that the booster heater is set to come on for last 10 mins of heating if not at temp.
#3032 and #3033 will tell you when and for how long
Posted by: @lfranklinI think that the booster heater is set to come on for last 10 mins of heating if not at temp.
Note: there is an element of "lost in translation" in all the heat pump manuals, but this is what they say.
In Power or Forced mode the booster heater starts without any delay (so ignores) FSV #3032
In Economic mode the DHW heating is via the heat pump only (I think this only applies if your target HW temperature is 55 degC or less. see page 34 of the manual)
- 26 Forums
- 2,364 Topics
- 53.6 K Posts
- 116 Online
- 6,027 Members
Join Us!
Worth Watching
Latest Posts
-
Sadly, no, @agentgeorge. The inverter will handle 5kW t...
By Majordennisbloodnok , 8 hours ago
-
RE: New Fogstar 15.5kWh upright solution
@transparent The readings are 0 for amps, 0 ...
By Batpred , 8 hours ago
-
RE: Say hello and introduce yourself
@velcro welcome to the forums. Please feel free start a...
By Mars , 9 hours ago
-
RE: Speedcomfort radiator fans
I watched the video to see whether they'd potentially b...
By Sheriff Fatman , 9 hours ago
-
RE: Mitsubishi Ecodan R290 10kW performance
@ecoste For what it's worth, this is my equivalent data...
By Sheriff Fatman , 10 hours ago
-
Daikin EDLA11D3V3 DHW Settings
I have a newly installed EDLA11D3V3 which I'm still get...
By Velcro , 10 hours ago
-
RE: Setback savings - fact or fiction?
Will come back to the above points, but for now, I've j...
By cathodeRay , 10 hours ago
-
@jamespa I have found that it comes as a shock when we ...
By Toodles , 12 hours ago
-
RE: My Powerwall 3 Consumes 3-4 kWh/Day in Self-Consumption: Is This Normal?
I suspect a good chunk of the "losses" are power consum...
By Bash , 13 hours ago
-
RE: Need Help Optimising My Rushed ECO4 Install: 12kW Bosch Heat Pump
Hi @mickamills . Welcome to the forum. It sounds like...
By bontwoody , 14 hours ago
-
RE: Midea ASHP – how to set weather compensation
@curlykatie did you get sorted with this?
By MickaMills , 14 hours ago
-
RE: External pipework insulation
@transparent I hope you are not being admonished @trans...
By Toodles , 14 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
The FT levels off at either the set point OR the minimu...
By AndrewJ , 1 day ago
-
RE: MyVaillant Connect Regular Disconnect
Thanks. Yes, if the time is consistently 11pm every nig...
By buckwem , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@transparent Thanks, this helps. Could it be that St...
By Batpred , 2 days ago
-
RE: Clivet ASHPs and weather compensation
Simon did share a lot of very helpful advice. On furthe...
By ambris , 2 days ago
-
-
RE: Advice on internal circulation pump noise
Extend the primary branch and make sure you have more t...
By ASHP-BOBBA , 3 days ago