Posted by: @adamkAlso I’m not entirely convinced the heat loss the last company did is that accurate
I apologise if this has been covered already but have you got any way to sense check loss calculations eg from past usage. The two, three hour full professional surveys I had done on my house both said 16kW, the actual loss is 7kW. This may be extreme but illustrates how far out surveys can be
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I’ve had a few done most come out around 7kw so that’s probably about right, but the loss per room I’ve only got one and it’s been corrected a few times but one bedroom is still listed 2m2 smaller than it is.
@jamespa to be that far out the assessor has got the insulation thickness of the floor, walls and ceiling too thin.
i have 150mm thickness but its celotex not rockwool, took ages to explain that to the assessor who could only input thickness and not the true R rating.
@adamk Sounds encouraging, what about any independent measure of total loss eg from current gas/oil consumption.
Rooms share heat to a fair extent so it's debatable how much precise room by room losses matter, so long as they are roughly right. If in doubt oversize emitters and turn down the lsv (or flow temp if they are all oversized). Much more important to get the total right so your heat pump is right-sized.
Posted by: @agentgeorgeto be that far out (16 kW Vs 7kW actual) the assessor has got the insulation thickness of the floor, walls and ceiling too thin.
I got the calculation details for one of the two surveys, they ignored any fabric upgrades they couldn't see (principally insulation for the solid walls) even though I made a big point of telling the surveyor about them, double counted room to room losses and overestimated ventilation loss. I presume the other surveyor must have done similar. GIGO
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa what I didn’t want to do was oversize too much then end up having the HP cycling. What I have noticed is most companies I’ve contacted want to fit a 45L Vaillant buffer/volumizer? Yet after watching this weeks QA vid a guy on there said no buffers.
Posted by: @adamk@jamespa what I didn’t want to do was oversize too much then end up having the HP cycling. What I have noticed is most companies I’ve contacted want to fit a 45L Vaillant buffer/volumizer? Yet after watching this weeks QA vid a guy on there said no buffers.
The guy was right as regards buffer tanks, avoid. However a 2 port volumiser is ok. Unfortunately terminology isn't quite consistent.
Check that it's got 2 ports only. 2 ports good, 3 or 4 ports bad.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
just trying to roughly get an idea what price an install should be if the following has already been done.
1) upgraded some 15mm copper runs to 22mm. 15mm for the last 3m worst case.
2) the above mentioned 22mm and about half the rads (15mm feeds) fed from 28mm flow and return.
3) 28mm primaries run from plant room and lagged and core drilled through back wall.
4) plant room 1300w x 900d x 2300h
5) new meter box on same side of house as plant room and heat pump, so easy run along wall for cabling.
6) no rad changes as part of the quote.
i would think the only work needed is heat pump base, heat pump mount, 28mm primaries up back wall in primary pro lagging, pipe work for HW tank and rad circuits in plant room, electrical work for plant room and heat pump, smart controls, commissioning.
@adamk, in terms of ballpark pricing, if we assume a straightforward install of a mid-size unit (say 8–12kW), with a standard heat pump ready HW cylinder and proper controls/commissioning, you’d expect to be in the region of £9,000–£12,000 (pre-BUS grant).
That assumes you’re going with a reputable installer using quality kit and doing things by the book: no cut corners, proper lagging, flow setting and performance commissioning. Some might come in a bit lower, but I’d be cautious if it drops below £9,000, because at that point they’re likely clawing it back somewhere else (labour, electrical spec, shortcuts, etc.). The caveat there will be the size and brand of ASHP.
Estimated time of completion is another benchmark. If they say it’ll be installed and commissioned in a couple of days, run.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @adamkjust trying to roughly get an idea what price an install should be if the following has already been done.
1) upgraded some 15mm copper runs to 22mm. 15mm for the last 3m worst case.
2) the above mentioned 22mm and about half the rads (15mm feeds) fed from 28mm flow and return.
3) 28mm primaries run from plant room and lagged and core drilled through back wall.
4) plant room 1300w x 900d x 2300h
5) new meter box on same side of house as plant room and heat pump, so easy run along wall for cabling.
6) no rad changes as part of the quote.
i would think the only work needed is heat pump base, heat pump mount, 28mm primaries up back wall in primary pro lagging, pipe work for HW tank and rad circuits in plant room, electrical work for plant room and heat pump, smart controls, commissioning.
I agree with @mars.
My install was not dissimilar. I got a 7kW Vaillant, 200l cylinder and 4 rads (including one fancoil) for 12.5K les grant. Im in the south east of england, prices may differ elsewhere. In my case the 16A feed for the ASHP was already in place (my friendly electrician did that for £180 - I ran the cable he connected it up), but the pipework run from the ASHP to the point where all the existing pipework converged was a bit of a nasty and took a whole day, even though I had done most of the 'building' work to expose the voids where I wanted it hidden and then made good afterwards.
The whole install was six long days with one person doing the whole thing roughly split as follows
- Receive & check deliveries, site ashp, base on top of existing paving, run primaries to location of existing boiler - 2 days total
- Fit DHW tank & vent pipe - 1 day (8am-9pm without a break!)
- Radiators - 1 day
- Wiring, flush, connect up, debug, commission - 1 day
- Remove old cold water tank, insulate, tidy up generally, commission internet gateway - 1 day
I watched the guy more or less throughout and he worked very hard, so I dont think it could reasonably have been done in fewer man-days.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@editor guess the reason im asking is cause ive looked at the break down on heat geeks quote system and then stripped out what ive already done and im getting around £2800 after BUS for 7KW Vaillant with 250L HW tank and me doing the base. but so far cheapest is £3800, maybe there doing the base like the HG quote suggests?
- 26 Forums
- 2,104 Topics
- 46.3 K Posts
- 69 Online
- 3,393 Members
Join Us!
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist Another point I might have made a little...
By Toodles , 6 minutes ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
It does indeed look like that, @skyefarmer. There is ...
By Majordennisbloodnok , 4 hours ago
-
RE: Plug and play solar. Thoughts?
Have a read of my previous posts on so-called Balcony S...
By Lucia , 22 hours ago
-
@editor @bart Hi, I can see a few problems with your in...
By Brendon Uys , 1 day ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 1 day ago
-
RE: Location of hot water isolation valve on cylinder
@rossowheels if you isolate the water supply in it will...
By ASHP-BOBBA , 2 days ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 2 days ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 2 days ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 3 days ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 3 days ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 3 days ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 3 days ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 4 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 4 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 4 days ago