Heat pump size advice – is 16kW overkill for this property?
@iancalderbank Thanks Ian, I didnt spot the link, the colour is quite subtle on my monitor.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
So the latest in this saga, is that the neighbour still hasnt been given control of her heat pump via a local network and the company are unable to give her access via their internet portal because of poor broadband coverage.
I am trying to get them to guarantee the large heat pumps performance, in terms of the maximum number of cycles allowed per hour in mild weather. I suggested 3 per hour, they stated that the industry standard is 4. Does anyone know if this figure is correct?
I also found this quote in the MCS best practice guide which exactly mirrors her situation!
Key point:
Many installers use just one preferred
manufacturer for supply of heat pumps.
Whilst this has advantages with familiarity,
associated design, installation and
commissioning requirements, it could mean
that the heat pump becomes significantly
under or oversized if the nearest available
size is utilised. In such a situation it
may be advisable to seek an alternative
manufacturer’s product which is more closely
matched to the design load, or consult
the manufacturer and seek guidance (e.g.
increased water volume/install a buffer).
The Contractor responsible must weigh up
the pros and cons of their actions.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody I'm not sure that there is a single, universally accepted "industry standard" for heat pump cycles per hour. I suspect different manufacturers might have their own internal guidelines and "interpretations", and some may recommend 3 cycles/hour while others might suggest 4.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor I'll defer to Brendon/Heatcol's encylopedic knowledge here when and if he responds in terms of how many compressor starts per hr is too many.... but....lets think about reducing them from a theoretical point of view:
This is why sizing becomes absolutely vital. There's already oversizing "calculated in" to many systems because currently under MCS base temperature isn't accounted for because they refer to BS12831 for calculating the peak heat load and 12831 doesn't account for base temp. So for instance you house may only need heating once the outside temp drops to 15º, and the outdoor design temp (ie "really cold") might be -3º, giving a temp difference of 18. However the calc can mean, depending on the types of rooms in the house, that the starting temperature used for the calculation is 21º = temp difference of 24 - so that's already 33% oversized (not accounting for headroom for intermittent heating of course - ie heating up from cold).
You can work out base temperature from monthly bills via a regression calc on the degreedays website, or you can just record the outside temp every time it feels like you shoudl turn the heating on.
Many manufactures will state that their heat pump is blah-kW. I guess this allows for comparison between makes, but an air source heat pump's output generally varies according to the flow temp required, and according to the outside air temp. So you need to know the designed flow temperature of your system and the external design temperature where you live. You then look up the output in the table which you should find in a tech manual. So we happen to supply Clivet heat pumps to engineers and here's the output table for the Evo I 41 unit. I've highlighted the max output at 45 flow temp, -2/3 outside as an example.
The types of system that Brendon teaches engineers to design will also reduce cycling. Not using weather compensation (ie delivering water that is too hot for the house), using TRVs, room stats and zones all increase cycling, whereas weather comp, open circuit, or open zone, flow balanced systems will tend to do the opposite. Engineers should be encourage to attend this type of training.
I also think that loading up extra heat into the house and hot water when electricity prices are low is a potential way to reduce cycling, as is the use of a volumiser - both are acting as a type of thermal storage.
The only reference I can find in the MCS guide is how to reduce starts to no more than 6 starts per hr... there may be updates in the pipeline of course. Min Utilisation factors are being updated in the biomass standards for instance, which may have a relationship to the number of ignitions, which is the equivalent of compressor starts in heat pumps.
I realise I've not directly answered the question, hopefully Brendon will step in with his vast array of practical and technical knowledge!
Sustainable Groups - Renewable Heating - Director of Firepower. Book a one-to-one consultation to discuss your heating and sustainability here.
@bontwoody how did your neighbour’s saga finally conclude? Are they happy?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Hi Mars, unfortunately I never got to find out. Despite my best efforts the neighbour could not get her head around how to set up weather compensation on her unit and started I think to blame me. I was rather busy at the time with my extension and couldn't keep popping around to try and sort out her latest experiment.
IMO the heat pump was oversized, but I think it could have been made to work moderately well with the right setup, unfortunately because the neighbour couldn't get broadband at her property, the company could not log in to remotely help her.
While I think the company's response was poor, I also don't think the lady helped herself either and was fixated on taking them through the available legal options to get some redress.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Weather comp is straightforward when in "ACONDTHERM" mode it has full weather comp, this mode uses high heat to reach desired room temp then backs off to try and keep temp .3˚C above or below set temp. The other option is EQUITHERM which uses weather comp, but you can also set your own curve (kinda like am aertotherm) which would probably be the best option, but requires time and a bit of tweaking. EG
though it sounds like it, it's probably not worth the effort.
@bontwoody I guess you never got the admin login details for the Acond unit ?
@deano Hi Dean, yes I did get the local interface working (Thanks for all your help).
I went through it with the owner and the concepts of weather compensation several times over multiple visits even writing help sheets. In the end my wife thought I was having an affair!
I explained the importance of changing one thing at a time and seeing the effect, but she just didnt seem to listen.
Things came to a head after her last experiment set the return flow temperature to 22C at all OATs. I tried to explain that the radiators would feel cold and that I thought she was mixing up flow temperature and room temperature. In response she said she had an IQ the size of a small planet and didnt need my help anymore, so I left it there. 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoody...
In response she said she had an IQ the size of a small planet and didnt need my help anymore, so I left it there.
...
I take it you didn't reply that "in that case, you're talking out of Uranus"....
Taxi!
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 22 Forums
- 2,057 Topics
- 44.9 K Posts
- 43 Online
- 3,299 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
There are various ways to look at things related to CoP...
By Johnmo , 4 hours ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
@abbote thanks for that advice.There was a bit of air i...
By tdudgeon , 4 hours ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
One manufacturer Viessmann has to have their buffer, as...
By Johnmo , 7 hours ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 1 day ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 1 day ago
-
RE: Is your heat pump insured?
@johnmo sorry it comes across like that. The post is au...
By KevinPotts , 1 day ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@johnmo Perhaps a little detail might explain my reason...
By Toodles , 1 day ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 2 days ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 2 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 2 days ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Hopefully iv done the right thing today by signing up t...
By Westkent , 2 days ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 2 days ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 3 days ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
The useful bit is the bit that specifies the heat loss ...
By JamesPa , 3 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 3 days ago
-
@editor thanks Mars that’s the same table I found in th...
By Gary , 3 days ago
-
RE: Tariff and charging strategy advice please
They haven't asked me to prove that I have an EV (I do)...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Took a while to find on the OFGEN site: ”The FIT sche...
By AgentGeorge , 3 days ago
-
RE: why solar diverters for HW instead of the heat pump?
For me there are few factors why you may want to heat w...
By Johnmo , 3 days ago