Ecodan 14kW flow rates too low?
We have an Ecodan 14kW. It was installed about 12m from the tank (due to aesthetics and an existing oil tank concrete base).
The installer used preinsulated pipe which was buried. But it was 28mm which I’m now picking up isn’t big enough.
We have an 80L buffer. Two pumps, one on the flow and one on the return from the heat pump to the buffer, which seems to be standard for Mitsi according to their manuals.
40-70 pumps on full.
Our flow rate is 29-30. It’s not affected by radiators etc as the buffer separates the internal circuits off.
I’ve been told the flow should be closer to 40. So I guess the only way is to replace the preinsulated pipe?
Just gathering opinions really. We will probably see out this winter and see what COP we get (was installed 3 years ago but have just tuned the WC curve etc)
Installer says flow rate is fine!
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
I can only speak from our own experience and the optimal flow rate for the Global Energy Systems ASHP is over 30 litre and it doesn't trigger alarms. 40 litre seems high, but I'm not an expert. Will be interesting to see what others say.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
28mm pipe can carry 16.8kW of power if the difference in temperature between flow and return is 5C, which it probably is. This means that assuming the pipe is not kinked or set up like a rollercoaster, it is not the pipe limiting the flow to 30L/m by itself.
My best guess is that your unit is modulating its power downwards because your house doesn't need 14kW right now. I actually emailed Mitsubishi to ask what their minimum output is yesterday, so I can update with what they say if they get back to me.
Have you been cold the previous three winters? If not, I would just wait to see what happens and not worry about it. Assuming the flow rate was limited by something - be it a pipe or a connection or a pump or anything else - it's still able to provide almost 11kW. It's possible that the length of the pipe run is having a limiting factor, but I don't know how to work that out. Again, I'd wait and see what happens when it's actually cold.
Posted by: @bensebA question for those of you in the know
We have an Ecodan 14kW. It was installed about 12m from the tank (due to aesthetics and an existing oil tank concrete base).The installer used preinsulated pipe which was buried. But it was 28mm which I’m now picking up isn’t big enough.
We have an 80L buffer. Two pumps, one on the flow and one on the return from the heat pump to the buffer, which seems to be standard for Mitsi according to their manuals.
40-70 pumps on full.
Our flow rate is 29-30. It’s not affected by radiators etc as the buffer separates the internal circuits off.
I’ve been told the flow should be closer to 40. So I guess the only way is to replace the preinsulated pipe?
Just gathering opinions really. We will probably see out this winter and see what COP we get (was installed 3 years ago but have just tuned the WC curve etc)
Installer says flow rate is fine!
Our 14kW Ecodan also uses 28mm pipe. We have no buffer. The minimum output of your Ecodan is on p 69 of the link below. The 14kW Ecodan needs 40l/min at its nominal speed.
Hopefully you won't need anything like 14kW most of the time so a lower flow won't matter.
https://library.mitsubishielectric.co.uk/pdf/book/ATW_Databook_R32_2020#page-68-69
That’s a good point about output. I’ve been checking when it’s just ticking over at 25-30c flow temp.
I’ll check again when it gets cold.
it was fine last year aside from one day when it was about -6c outside and I got a flow fault. But that’s below design temp anyway. We have an immersion in the buffer tank that we can use with excess solar so switched that on when it was ultra cold.
let’s see what this winter brings!
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
Posted by: @bensebA question for those of you in the know
We have an Ecodan 14kW. It was installed about 12m from the tank (due to aesthetics and an existing oil tank concrete base).The installer used preinsulated pipe which was buried. But it was 28mm which I’m now picking up isn’t big enough.
We have an 80L buffer. Two pumps, one on the flow and one on the return from the heat pump to the buffer, which seems to be standard for Mitsi according to their manuals.
40-70 pumps on full.
Our flow rate is 29-30. It’s not affected by radiators etc as the buffer separates the internal circuits off.
I’ve been told the flow should be closer to 40. So I guess the only way is to replace the preinsulated pipe?
Just gathering opinions really. We will probably see out this winter and see what COP we get (was installed 3 years ago but have just tuned the WC curve etc)
Installer says flow rate is fine!
Hi Benseb,
The fact that it has been operating correctly for three years should provide you with the answer.
Setting weather compensation should not have a detrimental effect on operation, and should improve overall efficiency. Remember the old adage 'if it's not broken, don't fix it'. 😎
Posted by: @kev-mOur 14kW Ecodan also uses 28mm pipe. We have no buffer. The minimum output of your Ecodan is on p 69 of the link below. The 14kW Ecodan needs 40l/min at its nominal speed.
Why be like that and not also say the minimum output of an Ecodan is generally 3-4kW in above-zero ambient temperatures.
Although are you sure this isn't about a monobloc unit on page A-58? That has a wider 2-7kW minimum range depending on ambient and flow temperatures. I think if you bump into the 6+kW minimum often, that can be problematic and may mean the heat pump is oversize.
Be like what? I was trying to be helpful and show the questioner the whole picture rather than just quoting one number. That link has lots of other information too. I always like to see a link rather than just an opinion.
And yes I quoted the wrong page so thank you for pointing that out; the monobloc 14kW Ecodan is on p 58.
Posted by: @kev-mI always like to see a link rather than just an opinion.
I like to see both. I admit it irritates me a little when only a link is mentioned because before getting our heat pump, I read lots of forum posts where no answer was given, only a link, and that link has broken: maybe the linked site moved the file, or maybe the link was incorrect all along. So please, think of future people reading these discussions ☺
- 26 Forums
- 2,300 Topics
- 51.6 K Posts
- 207 Online
- 5,965 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Firstly you are getting your units mixed up. kW is pow...
By JamesPa , 2 minutes ago
-
RE: Electricity price predictions
Until people understanding the problem with electricity...
By Diverted.Energy , 2 minutes ago
-
RE: Buffer tank bypass on EDF Ideal heat pump installation
I would bypass the buffer tank in one of flow or return...
By JamesPa , 16 minutes ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira
I agree with all of that. 220 pages is perhaps 210-215...
By JamesPa , 26 minutes ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
One of those brilliant ideas that is obvious with hinds...
By Lenny , 28 minutes ago
-
RE: Don’t Install a Heat Pump Until You Read This
@davidnolan22 Perhaps you could post some more info a...
By JamesPa , 33 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
OK. I have 2.8 for DHW and 3.4 for space heating runni...
By JamesPa , 39 minutes ago
-
RE: 10kw heat pump run in 24*7 data?
Some observations: 1. I for one don't know the Vailla...
By cathodeRay , 1 hour ago
-
Heat Pump on Flat Roof Low Frequency Noise from Detached Neighbor
Hi, I have been noticing a steady 120Hz noise inside ...
By People_Noise , 8 hours ago
-
RE: Commencing on an ASHP Installation Process
Given that this thread ultimately turned out to be a di...
By Sheriff Fatman , 11 hours ago
-
Ecodan - Flow temperature spiking causing shutdown
Hi everyone, looking for some help. I am in a new bu...
By Gl3484 , 11 hours ago
-
Solis AI is on the right track to leverage the battery:...
By Batpred , 13 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Thanks James, its honestly hard to keep it tog...
By Crimson , 14 hours ago
-
RE: Extend the colder range of the weather compensation curve?
Thanks for replies. That's good to hear and wanted to ...
By TheBinMan , 14 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: KevB Manufacturer: Ideal Model: 5kW ...
By KevB , 16 hours ago
-
RE: DHW heat loss through pumps.
Hi @ngillam I don't have anything as sophisticated for ...
By Marzipan71 , 18 hours ago
-
RE: Has anyone seen this problem before? Huge anticycling times
For the information of others. Vaillent came today, che...
By jamesh , 19 hours ago
-
RE: Here is my heat pump installation with questionable COP in Italy
Hi, and welcome to the forum. I cant quite u...
By JamesPa , 24 hours ago
-
I signed up to Havenwise control on the day after the h...
By Sheriff Fatman , 1 day ago
-
That's not always the case.Let's see what they say once...
By Transparent , 2 days ago