Ecodan 14kW flow rates too low?
We have an Ecodan 14kW. It was installed about 12m from the tank (due to aesthetics and an existing oil tank concrete base).
The installer used preinsulated pipe which was buried. But it was 28mm which I’m now picking up isn’t big enough.
We have an 80L buffer. Two pumps, one on the flow and one on the return from the heat pump to the buffer, which seems to be standard for Mitsi according to their manuals.
40-70 pumps on full.
Our flow rate is 29-30. It’s not affected by radiators etc as the buffer separates the internal circuits off.
I’ve been told the flow should be closer to 40. So I guess the only way is to replace the preinsulated pipe?
Just gathering opinions really. We will probably see out this winter and see what COP we get (was installed 3 years ago but have just tuned the WC curve etc)
Installer says flow rate is fine!
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
I can only speak from our own experience and the optimal flow rate for the Global Energy Systems ASHP is over 30 litre and it doesn't trigger alarms. 40 litre seems high, but I'm not an expert. Will be interesting to see what others say.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
28mm pipe can carry 16.8kW of power if the difference in temperature between flow and return is 5C, which it probably is. This means that assuming the pipe is not kinked or set up like a rollercoaster, it is not the pipe limiting the flow to 30L/m by itself.
My best guess is that your unit is modulating its power downwards because your house doesn't need 14kW right now. I actually emailed Mitsubishi to ask what their minimum output is yesterday, so I can update with what they say if they get back to me.
Have you been cold the previous three winters? If not, I would just wait to see what happens and not worry about it. Assuming the flow rate was limited by something - be it a pipe or a connection or a pump or anything else - it's still able to provide almost 11kW. It's possible that the length of the pipe run is having a limiting factor, but I don't know how to work that out. Again, I'd wait and see what happens when it's actually cold.
Posted by: @bensebA question for those of you in the know
We have an Ecodan 14kW. It was installed about 12m from the tank (due to aesthetics and an existing oil tank concrete base).The installer used preinsulated pipe which was buried. But it was 28mm which I’m now picking up isn’t big enough.
We have an 80L buffer. Two pumps, one on the flow and one on the return from the heat pump to the buffer, which seems to be standard for Mitsi according to their manuals.
40-70 pumps on full.
Our flow rate is 29-30. It’s not affected by radiators etc as the buffer separates the internal circuits off.
I’ve been told the flow should be closer to 40. So I guess the only way is to replace the preinsulated pipe?
Just gathering opinions really. We will probably see out this winter and see what COP we get (was installed 3 years ago but have just tuned the WC curve etc)
Installer says flow rate is fine!
Our 14kW Ecodan also uses 28mm pipe. We have no buffer. The minimum output of your Ecodan is on p 69 of the link below. The 14kW Ecodan needs 40l/min at its nominal speed.
Hopefully you won't need anything like 14kW most of the time so a lower flow won't matter.
https://library.mitsubishielectric.co.uk/pdf/book/ATW_Databook_R32_2020#page-68-69
That’s a good point about output. I’ve been checking when it’s just ticking over at 25-30c flow temp.
I’ll check again when it gets cold.
it was fine last year aside from one day when it was about -6c outside and I got a flow fault. But that’s below design temp anyway. We have an immersion in the buffer tank that we can use with excess solar so switched that on when it was ultra cold.
let’s see what this winter brings!
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
Posted by: @bensebA question for those of you in the know
We have an Ecodan 14kW. It was installed about 12m from the tank (due to aesthetics and an existing oil tank concrete base).The installer used preinsulated pipe which was buried. But it was 28mm which I’m now picking up isn’t big enough.
We have an 80L buffer. Two pumps, one on the flow and one on the return from the heat pump to the buffer, which seems to be standard for Mitsi according to their manuals.
40-70 pumps on full.
Our flow rate is 29-30. It’s not affected by radiators etc as the buffer separates the internal circuits off.
I’ve been told the flow should be closer to 40. So I guess the only way is to replace the preinsulated pipe?
Just gathering opinions really. We will probably see out this winter and see what COP we get (was installed 3 years ago but have just tuned the WC curve etc)
Installer says flow rate is fine!
Hi Benseb,
The fact that it has been operating correctly for three years should provide you with the answer.
Setting weather compensation should not have a detrimental effect on operation, and should improve overall efficiency. Remember the old adage 'if it's not broken, don't fix it'. 😎
Posted by: @kev-mOur 14kW Ecodan also uses 28mm pipe. We have no buffer. The minimum output of your Ecodan is on p 69 of the link below. The 14kW Ecodan needs 40l/min at its nominal speed.
Why be like that and not also say the minimum output of an Ecodan is generally 3-4kW in above-zero ambient temperatures.
Although are you sure this isn't about a monobloc unit on page A-58? That has a wider 2-7kW minimum range depending on ambient and flow temperatures. I think if you bump into the 6+kW minimum often, that can be problematic and may mean the heat pump is oversize.
Be like what? I was trying to be helpful and show the questioner the whole picture rather than just quoting one number. That link has lots of other information too. I always like to see a link rather than just an opinion.
And yes I quoted the wrong page so thank you for pointing that out; the monobloc 14kW Ecodan is on p 58.
Posted by: @kev-mI always like to see a link rather than just an opinion.
I like to see both. I admit it irritates me a little when only a link is mentioned because before getting our heat pump, I read lots of forum posts where no answer was given, only a link, and that link has broken: maybe the linked site moved the file, or maybe the link was incorrect all along. So please, think of future people reading these discussions ☺
- 26 Forums
- 2,255 Topics
- 50.3 K Posts
- 607 Online
- 5,918 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: PV Panels on roof in Conservation Area
@majordennisbloodnok Fnaargh, I was thinking about try...
By colinc , 28 minutes ago
-
RE: Electricity price predictions
@jamespa Ah, you mean MPs that have not pro...
By Batpred , 1 hour ago
-
-
RE: Buying large amp bidirectional RCD and RCBO
Exactly @transparent , this type of RCBOs are not easil...
By Batpred , 2 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - though I realise I am a Canute, I have an...
By cathodeRay , 2 hours ago
-
RE: Mitsubishi Ecodan R290 10kW performance
I don't have any obvious issues with the MELCloud data ...
By Sheriff Fatman , 2 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
@jamespa Yup! 😉 Toodles.
By Toodles , 4 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
And just when I think great they’re coming next week to...
By Crimson , 4 hours ago
-
RE: Very Much Awake – Renewing the Heating Industry One Step at a Time
I feel that that attitude shared by Aadil from Heat Gee...
By Toodles , 5 hours ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
I have recently gone through the whole process. I got q...
By debT , 8 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
and we have some of the strongest tidal flows anywhere ...
By Old_Scientist , 8 hours ago
-
RE: Radiator Sizing Dilemma: Vertical vs Type 33 for Low-Temperature Heat Pump Systems
This looks OK. Overall you have roughly the right amoun...
By Old_Scientist , 8 hours ago
-
RE: How can I programme a setback for my Samsung Gen6 8kW heat pump?
I'm not familiar with Hive thermostats/controllers, but...
By Old_Scientist , 9 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Thanks @grantmethestrength and @cathoderay . The reas...
By benson , 22 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa mine seems changing albeit not by much, 3.21, ...
By AdamK , 1 day ago
-
@majordennisbloodnok The migration hasn't started in th...
By HCas , 1 day ago
-
RE: One room is colder than the rest of the house
@jamespa thanks for all the advice. Just so you know, ...
By AndrewJ , 1 day ago
-
RE: Daikin Octopus installation update - I saw my first defrost. 😍😂
My MMI is in the loft but I checked the pump flow rate ...
By RadWhisperer , 1 day ago
-
RE: Grant Aerona 3 and Drayton system questions
Good man/woman that plumber! Very likely....
By JamesPa , 1 day ago