Ecodan 14kW flow rates too low?
We have an Ecodan 14kW. It was installed about 12m from the tank (due to aesthetics and an existing oil tank concrete base).
The installer used preinsulated pipe which was buried. But it was 28mm which I’m now picking up isn’t big enough.
We have an 80L buffer. Two pumps, one on the flow and one on the return from the heat pump to the buffer, which seems to be standard for Mitsi according to their manuals.
40-70 pumps on full.
Our flow rate is 29-30. It’s not affected by radiators etc as the buffer separates the internal circuits off.
I’ve been told the flow should be closer to 40. So I guess the only way is to replace the preinsulated pipe?
Just gathering opinions really. We will probably see out this winter and see what COP we get (was installed 3 years ago but have just tuned the WC curve etc)
Installer says flow rate is fine!
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
I can only speak from our own experience and the optimal flow rate for the Global Energy Systems ASHP is over 30 litre and it doesn't trigger alarms. 40 litre seems high, but I'm not an expert. Will be interesting to see what others say.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
28mm pipe can carry 16.8kW of power if the difference in temperature between flow and return is 5C, which it probably is. This means that assuming the pipe is not kinked or set up like a rollercoaster, it is not the pipe limiting the flow to 30L/m by itself.
My best guess is that your unit is modulating its power downwards because your house doesn't need 14kW right now. I actually emailed Mitsubishi to ask what their minimum output is yesterday, so I can update with what they say if they get back to me.
Have you been cold the previous three winters? If not, I would just wait to see what happens and not worry about it. Assuming the flow rate was limited by something - be it a pipe or a connection or a pump or anything else - it's still able to provide almost 11kW. It's possible that the length of the pipe run is having a limiting factor, but I don't know how to work that out. Again, I'd wait and see what happens when it's actually cold.
Posted by: @bensebA question for those of you in the know
We have an Ecodan 14kW. It was installed about 12m from the tank (due to aesthetics and an existing oil tank concrete base).The installer used preinsulated pipe which was buried. But it was 28mm which I’m now picking up isn’t big enough.
We have an 80L buffer. Two pumps, one on the flow and one on the return from the heat pump to the buffer, which seems to be standard for Mitsi according to their manuals.
40-70 pumps on full.
Our flow rate is 29-30. It’s not affected by radiators etc as the buffer separates the internal circuits off.
I’ve been told the flow should be closer to 40. So I guess the only way is to replace the preinsulated pipe?
Just gathering opinions really. We will probably see out this winter and see what COP we get (was installed 3 years ago but have just tuned the WC curve etc)
Installer says flow rate is fine!
Our 14kW Ecodan also uses 28mm pipe. We have no buffer. The minimum output of your Ecodan is on p 69 of the link below. The 14kW Ecodan needs 40l/min at its nominal speed.
Hopefully you won't need anything like 14kW most of the time so a lower flow won't matter.
https://library.mitsubishielectric.co.uk/pdf/book/ATW_Databook_R32_2020#page-68-69
That’s a good point about output. I’ve been checking when it’s just ticking over at 25-30c flow temp.
I’ll check again when it gets cold.
it was fine last year aside from one day when it was about -6c outside and I got a flow fault. But that’s below design temp anyway. We have an immersion in the buffer tank that we can use with excess solar so switched that on when it was ultra cold.
let’s see what this winter brings!
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
Posted by: @bensebA question for those of you in the know
We have an Ecodan 14kW. It was installed about 12m from the tank (due to aesthetics and an existing oil tank concrete base).The installer used preinsulated pipe which was buried. But it was 28mm which I’m now picking up isn’t big enough.
We have an 80L buffer. Two pumps, one on the flow and one on the return from the heat pump to the buffer, which seems to be standard for Mitsi according to their manuals.
40-70 pumps on full.
Our flow rate is 29-30. It’s not affected by radiators etc as the buffer separates the internal circuits off.
I’ve been told the flow should be closer to 40. So I guess the only way is to replace the preinsulated pipe?
Just gathering opinions really. We will probably see out this winter and see what COP we get (was installed 3 years ago but have just tuned the WC curve etc)
Installer says flow rate is fine!
Hi Benseb,
The fact that it has been operating correctly for three years should provide you with the answer.
Setting weather compensation should not have a detrimental effect on operation, and should improve overall efficiency. Remember the old adage 'if it's not broken, don't fix it'. 😎
Posted by: @kev-mOur 14kW Ecodan also uses 28mm pipe. We have no buffer. The minimum output of your Ecodan is on p 69 of the link below. The 14kW Ecodan needs 40l/min at its nominal speed.
Why be like that and not also say the minimum output of an Ecodan is generally 3-4kW in above-zero ambient temperatures.
Although are you sure this isn't about a monobloc unit on page A-58? That has a wider 2-7kW minimum range depending on ambient and flow temperatures. I think if you bump into the 6+kW minimum often, that can be problematic and may mean the heat pump is oversize.
Be like what? I was trying to be helpful and show the questioner the whole picture rather than just quoting one number. That link has lots of other information too. I always like to see a link rather than just an opinion.
And yes I quoted the wrong page so thank you for pointing that out; the monobloc 14kW Ecodan is on p 58.
Posted by: @kev-mI always like to see a link rather than just an opinion.
I like to see both. I admit it irritates me a little when only a link is mentioned because before getting our heat pump, I read lots of forum posts where no answer was given, only a link, and that link has broken: maybe the linked site moved the file, or maybe the link was incorrect all along. So please, think of future people reading these discussions ☺
- 22 Forums
- 2,058 Topics
- 44.9 K Posts
- 33 Online
- 3,312 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: IVT Greenline high pressure switch and electrical cassette errors
Your system seems to be more modern than mine, mine was...
By abbote , 46 minutes ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
The 16kw will only give you 12kw around 0° so be carefu...
By Damon Blakemore , 1 hour ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
Braver person than me. No way I would go down that rout...
By Johnmo , 13 hours ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Well my switch from eon is tomorrow/Monday so I’ll soon...
By Westkent , 17 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@arundalep yes I have no issue with this. The observati...
By benson , 20 hours ago
-
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@johnmo I have been looking at the daily Agile rates fo...
By Toodles , 23 hours ago
-
RE: Rate the quality of your heat pump design and installation
So your Halo lite should really do nothing, when connec...
By Johnmo , 24 hours ago
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
This is indeed welcome news. In addition the new legi...
By JamesPa , 1 day ago
-
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
@johnmo I think we’ve been trudging through the same...
By SUNandAIR , 3 days ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 4 days ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 4 days ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 4 days ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 5 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 5 days ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 5 days ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 5 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 5 days ago