Ecodan 14kW flow rates too low?
We have an Ecodan 14kW. It was installed about 12m from the tank (due to aesthetics and an existing oil tank concrete base).
The installer used preinsulated pipe which was buried. But it was 28mm which I’m now picking up isn’t big enough.
We have an 80L buffer. Two pumps, one on the flow and one on the return from the heat pump to the buffer, which seems to be standard for Mitsi according to their manuals.
40-70 pumps on full.
Our flow rate is 29-30. It’s not affected by radiators etc as the buffer separates the internal circuits off.
I’ve been told the flow should be closer to 40. So I guess the only way is to replace the preinsulated pipe?
Just gathering opinions really. We will probably see out this winter and see what COP we get (was installed 3 years ago but have just tuned the WC curve etc)
Installer says flow rate is fine!
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
I can only speak from our own experience and the optimal flow rate for the Global Energy Systems ASHP is over 30 litre and it doesn't trigger alarms. 40 litre seems high, but I'm not an expert. Will be interesting to see what others say.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
28mm pipe can carry 16.8kW of power if the difference in temperature between flow and return is 5C, which it probably is. This means that assuming the pipe is not kinked or set up like a rollercoaster, it is not the pipe limiting the flow to 30L/m by itself.
My best guess is that your unit is modulating its power downwards because your house doesn't need 14kW right now. I actually emailed Mitsubishi to ask what their minimum output is yesterday, so I can update with what they say if they get back to me.
Have you been cold the previous three winters? If not, I would just wait to see what happens and not worry about it. Assuming the flow rate was limited by something - be it a pipe or a connection or a pump or anything else - it's still able to provide almost 11kW. It's possible that the length of the pipe run is having a limiting factor, but I don't know how to work that out. Again, I'd wait and see what happens when it's actually cold.
Posted by: @bensebA question for those of you in the know
We have an Ecodan 14kW. It was installed about 12m from the tank (due to aesthetics and an existing oil tank concrete base).The installer used preinsulated pipe which was buried. But it was 28mm which I’m now picking up isn’t big enough.
We have an 80L buffer. Two pumps, one on the flow and one on the return from the heat pump to the buffer, which seems to be standard for Mitsi according to their manuals.
40-70 pumps on full.
Our flow rate is 29-30. It’s not affected by radiators etc as the buffer separates the internal circuits off.
I’ve been told the flow should be closer to 40. So I guess the only way is to replace the preinsulated pipe?
Just gathering opinions really. We will probably see out this winter and see what COP we get (was installed 3 years ago but have just tuned the WC curve etc)
Installer says flow rate is fine!
Our 14kW Ecodan also uses 28mm pipe. We have no buffer. The minimum output of your Ecodan is on p 69 of the link below. The 14kW Ecodan needs 40l/min at its nominal speed.
Hopefully you won't need anything like 14kW most of the time so a lower flow won't matter.
https://library.mitsubishielectric.co.uk/pdf/book/ATW_Databook_R32_2020#page-68-69
That’s a good point about output. I’ve been checking when it’s just ticking over at 25-30c flow temp.
I’ll check again when it gets cold.
it was fine last year aside from one day when it was about -6c outside and I got a flow fault. But that’s below design temp anyway. We have an immersion in the buffer tank that we can use with excess solar so switched that on when it was ultra cold.
let’s see what this winter brings!
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
Posted by: @bensebA question for those of you in the know
We have an Ecodan 14kW. It was installed about 12m from the tank (due to aesthetics and an existing oil tank concrete base).The installer used preinsulated pipe which was buried. But it was 28mm which I’m now picking up isn’t big enough.
We have an 80L buffer. Two pumps, one on the flow and one on the return from the heat pump to the buffer, which seems to be standard for Mitsi according to their manuals.
40-70 pumps on full.
Our flow rate is 29-30. It’s not affected by radiators etc as the buffer separates the internal circuits off.
I’ve been told the flow should be closer to 40. So I guess the only way is to replace the preinsulated pipe?
Just gathering opinions really. We will probably see out this winter and see what COP we get (was installed 3 years ago but have just tuned the WC curve etc)
Installer says flow rate is fine!
Hi Benseb,
The fact that it has been operating correctly for three years should provide you with the answer.
Setting weather compensation should not have a detrimental effect on operation, and should improve overall efficiency. Remember the old adage 'if it's not broken, don't fix it'. 😎
Posted by: @kev-mOur 14kW Ecodan also uses 28mm pipe. We have no buffer. The minimum output of your Ecodan is on p 69 of the link below. The 14kW Ecodan needs 40l/min at its nominal speed.
Why be like that and not also say the minimum output of an Ecodan is generally 3-4kW in above-zero ambient temperatures.
Although are you sure this isn't about a monobloc unit on page A-58? That has a wider 2-7kW minimum range depending on ambient and flow temperatures. I think if you bump into the 6+kW minimum often, that can be problematic and may mean the heat pump is oversize.
Be like what? I was trying to be helpful and show the questioner the whole picture rather than just quoting one number. That link has lots of other information too. I always like to see a link rather than just an opinion.
And yes I quoted the wrong page so thank you for pointing that out; the monobloc 14kW Ecodan is on p 58.
Posted by: @kev-mI always like to see a link rather than just an opinion.
I like to see both. I admit it irritates me a little when only a link is mentioned because before getting our heat pump, I read lots of forum posts where no answer was given, only a link, and that link has broken: maybe the linked site moved the file, or maybe the link was incorrect all along. So please, think of future people reading these discussions ☺
- 21 Forums
- 1,964 Topics
- 42.6 K Posts
- 48 Online
- 2,278 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Towel rails. An unexpected final hurdle
I had a similar issue but convinced the installer to le...
By Pie_Eater , 26 seconds ago
-
Cliff, welcome to the forum. You’re running into one ...
By Mars , 8 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
This whole discussion highlights just how much of a mes...
By Mars , 19 minutes ago
-
RE: NIBE F2040 12 kW heat pump and 100 liter buffer tank
@cheshirejohn thanks for the update and for sharing. I’...
By Mars , 42 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@jamespa @bontwoodyHeat loss calculations found and att...
By BAMi , 2 hours ago
-
RE: Setback savings - fact or fiction?
Here's the same plot, less the R squared values, done q...
By cathodeRay , 3 hours ago
-
RE: SolarPV tables / online calculator
We've only had our solar since last June, but so far fo...
By Old_Scientist , 3 hours ago
-
@robs useful thread! Thanks for sharing - Octopus are c...
By big_si , 4 hours ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 6 hours ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 6 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 7 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 11 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 1 day ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 1 day ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 2 days ago
Latest Topics
-
By cliffhanger 21 minutes ago
-
Heat Pump Sizing & Installation Costs
By Mars 13 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 14 hours ago
-
SolarPV tables / online calculator
By MichelleC 21 hours ago