Ecodan Zones/Wireless controller
Hi, I've recently moved into a new build which has an Ecodan PUZ-WM60VAA set up with DHW, Zone 1 > UFH, Zone 2 > rads.
There's one Heatmiser stat for the rads upstairs. UFH has stats in each room.
This is obviously setup like an old-school boiler, inefficient for a heat pump and leads to short cycling.
I purchased a couple of the wireless Mitsubishi stats and set them up, put the system into room temp mode (auto adapt?). However, I soon learned that the Heatmiser stats do actually call for heat and the system will not stop heating until it hits their limit, even when the wireless stats are showing a temp higher than the target.
I disabled 2 dip switches (SW2-1 & SW3-1) which prevents the stats controlling the heat and just act as pump control. This seems to work for the UFH however, Z2 will not heat independent of Z1 and with Z2's pump running will not put any heat into the radiators even while Z1 is flowing at 40c.
It seems the solution to this is: "For 2-zone temperature control, check DIP SW2-7 is set to ON (2-zone temperature control) and DIP SW2-6 is set to ON (With Mixing Tank)"
These are both off, I'm assuming I don't have a mixing tank and cannot just enable these?
I'm looking for a solution, maybe I need to hound the developer?
Tank image:
There’s quite a lot going on here, so we'll try to break it down with some unofficial insights from Mitsubishi. It sounds like your system is set up with two zones at the same design temperature rather than two zones with different temperatures. If that’s the case, SW2-6 & SW2-7 (which are for systems with a mixing tank) wouldn’t apply here. Instead, it seems SW3-6 is managing the two zones with the same temperature settings, and that’s correct for your system as it stands.
When it comes to third-party stats like Heatmiser, they usually work best when the Ecodan’s weather compensation is set up properly. The stats can then manage room temperatures and schedules. One potential tweak might be to check if the Heatmiser stats allow you to adjust the hysteresis (basically the delay between on/off signals). Widening this could help reduce short cycling. Another workaround some people use is combining zones or removing actuator heads to simplify the system and move towards an open-loop design, which can also reduce cycling.
For the Mitsubishi stats, Zone 1 should be fine in Auto Adaptive mode, but Zone 2 has to either follow the weather compensation curve or run in fixed flow mode. To get Zone 2 heating independently, you’ll probably need to look at what’s controlling its pump. It might require adjusting the signal cables or wiring, but it’s hard to say without seeing the full setup.
At this stage, it might be worth getting a heating engineer to take a closer look – they’ll be able to advise on pump controls, wiring changes or any other tweaks to get everything working smoothly. Mitsubishi’s Homeowner Helpline (0161 866 6064) could also be helpful for further advice.
Also, this video might help:
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
- 21 Forums
- 1,741 Topics
- 37.2 K Posts
- 56 Online
- 2,033 Members
Join Us!
Latest Posts
-
RE: Baffled by heat pump size/ choice!
OK lets go with 6, 8 minute showers at 10l/min. So you...
By JamesPa , 11 minutes ago
-
Contacted Samsung support (thanks Mike). Two problems a...
By Raiph , 40 minutes ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
Thanks for this Mars. I've actually found out the issue...
By dnagre , 21 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@transparent it doesn't sound good 🤔
By Andris , 21 hours ago
-
RE: 6 Red Flags to Avoid When Considering a Heat Pump Installation
The ASHP, just like a boiler, can supply water at only ...
By JamesPa , 22 hours ago
-
RE: New Samsung 12KW Heat Pump Help
@dinhp I will try and upload an audio file as it is dif...
By Mike H , 23 hours ago
-
RE: Excessive performance/system issues with GSHP
Is the buffer tank in the house? If so, any heat loss s...
By JohnR , 23 hours ago
-
RE: Should We Rethink the Name “Heat Pump” for Homeowners?
@marzipan71 How about ‘Coldtohotbox”?
By Toodles , 24 hours ago
-
RE: The good, the bad and the not that great – my heat pump installation
@transparent - here's the page with more details and im...
By cathodeRay , 1 day ago
-
RE: Vaillant ASHP Weather Compensation with Octopus Cosy
In the Vaillant app go to Settings (the cog wheel icon)...
By JohnR , 2 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Thanks for your reply. I love Octopus Energy and are a ...
By Trevor , 2 days ago
-
RE: Watch Where Your Installer Fits Motorised Valves
The 2000W Karcher will be out shortly!
By Mars , 2 days ago
-
We had a Daikin 8kW ASHP installed two weeks ago. We h...
By R0y124 , 2 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
I did not have the time to check the thermistors Yester...
By ThunderMink , 3 days ago
-
Evening all. Thanks for the replies. Great info....
By TheHolyHeatPump , 3 days ago
-
RE: Incorrect Billing of Customers with a Smart Meter
It would be nice if there being lower existing demand o...
By Transparent , 3 days ago
-
RE: Mitsubishi Ecodon stuck on immersion symbol
This how my system is running : Top graph is the am...
By ak2024 , 3 days ago
-
RE: Ecodan help - flow temperature spikes when operating in weather compensation mode
@eleusis it can do it but not in 4 hours, you will need...
By Gary , 3 days ago
-
RE: Most treasured kitchen gadget.
@toodles With the machine its as many as I want or s...
By IRMartini , 3 days ago
-
RE: Mitsubishi Ecodan ASHP general set-up and efficiency
@gary The heating bill often looks like we live in a ma...
By ngillam , 3 days ago
Latest Topics
-
Baffled by heat pump size/ choice!
By zuluwarrior 1 day ago
-
Vaillant ASHP Weather Compensation with Octopus Cosy
By tom58l 2 days ago
-
By R0y124 2 days ago
-
Mitsubishi Ecodan 11kw Defrosting Issue.
By ThunderMink 3 days ago
-
By TheHolyHeatPump 4 days ago
-
Flow temperature- At what point?
By Westkent 4 days ago
-
Excessive performance/system issues with GSHP
By didjerama_uk 4 days ago
-
Thermostat setting...still learning
By Profzarkov 4 days ago
-
Watch Where Your Installer Fits Motorised Valves
By Mars 5 days ago
-
Mitsubishi EcoDan ASHP Settings not saving.
By Fez96 5 days ago