Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan Zones/Wireless controller
Hi, I've recently moved into a new build which has an Ecodan PUZ-WM60VAA set up with DHW, Zone 1 > UFH, Zone 2 > rads.
There's one Heatmiser stat for the rads upstairs. UFH has stats in each room.
This is obviously setup like an old-school boiler, inefficient for a heat pump and leads to short cycling.
I purchased a couple of the wireless Mitsubishi stats and set them up, put the system into room temp mode (auto adapt?). However, I soon learned that the Heatmiser stats do actually call for heat and the system will not stop heating until it hits their limit, even when the wireless stats are showing a temp higher than the target.
I disabled 2 dip switches (SW2-1 & SW3-1) which prevents the stats controlling the heat and just act as pump control. This seems to work for the UFH however, Z2 will not heat independent of Z1 and with Z2's pump running will not put any heat into the radiators even while Z1 is flowing at 40c.
It seems the solution to this is: "For 2-zone temperature control, check DIP SW2-7 is set to ON (2-zone temperature control) and DIP SW2-6 is set to ON (With Mixing Tank)"
These are both off, I'm assuming I don't have a mixing tank and cannot just enable these?
I'm looking for a solution, maybe I need to hound the developer?
Tank image:

There’s quite a lot going on here, so we'll try to break it down with some unofficial insights from Mitsubishi. It sounds like your system is set up with two zones at the same design temperature rather than two zones with different temperatures. If that’s the case, SW2-6 & SW2-7 (which are for systems with a mixing tank) wouldn’t apply here. Instead, it seems SW3-6 is managing the two zones with the same temperature settings, and that’s correct for your system as it stands.
When it comes to third-party stats like Heatmiser, they usually work best when the Ecodan’s weather compensation is set up properly. The stats can then manage room temperatures and schedules. One potential tweak might be to check if the Heatmiser stats allow you to adjust the hysteresis (basically the delay between on/off signals). Widening this could help reduce short cycling. Another workaround some people use is combining zones or removing actuator heads to simplify the system and move towards an open-loop design, which can also reduce cycling.
For the Mitsubishi stats, Zone 1 should be fine in Auto Adaptive mode, but Zone 2 has to either follow the weather compensation curve or run in fixed flow mode. To get Zone 2 heating independently, you’ll probably need to look at what’s controlling its pump. It might require adjusting the signal cables or wiring, but it’s hard to say without seeing the full setup.
At this stage, it might be worth getting a heating engineer to take a closer look – they’ll be able to advise on pump controls, wiring changes or any other tweaks to get everything working smoothly. Mitsubishi’s Homeowner Helpline (0161 866 6064) could also be helpful for further advice.
Also, this video might help:
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
- 27 Forums
- 2,765 Topics
- 65.1 K Posts
- 1,701 Online
- 7,169 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Daikin ESPAltherma and Home Assistant installation
It’s well enough organised for what it’s designed to do...
By Majordennisbloodnok , 43 minutes ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
R (The R Project for Statistical Computing, I use it wi...
By cathodeRay , 1 hour ago
-
RE: Vaillant Arotherm Plus 7KW need a service on it
booked it with Vaillant. will use them until i can find...
By AdamK , 2 hours ago
-
We have electric underfloor heating in our reasonably l...
By Bash , 5 hours ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
@jamespa This was exactly what I did in the...
By Bash , 6 hours ago
-
RE: Adventures in heat loss calculations
I have seen it stated that the declared calorific value...
By JamesPa , 7 hours ago
-
RE: Siting of the external sensor on a heatpump
Here's my heat pump running with a steady mildish 'OAT'...
By cathodeRay , 8 hours ago
-
RE: Two heating zones to one zone
@transparent Many thanks. The garage is fairly well ...
By Profzarkov , 1 day ago
-
RE: Vaillant Aurotherm - Heater Wire Position
Ah, good point. I need to check if this was installed i...
By Batpred , 1 day ago
-
@batpred thanks for getting a copy. Appreciate the supp...
By Mars , 2 days ago
-
RE: Tell us about your Solar (PV) setup
We have a 6.56kW solar PV system (16x 410W panels) inst...
By Rob of York , 2 days ago
-
RE: Where heat loss surveys seem to go against practical reality
@cathoderay @jamespa I've managed to get some nice re...
By Rob of York , 3 days ago
-
RE: 7kW EV Charger Options Advice
Doh, not sure that I was thinking straight there, less ...
By Rusty , 3 days ago
-
Thank you @trebor12345
By rgabor , 3 days ago