Hi, I've recently moved into a new build which has an Ecodan PUZ-WM60VAA set up with DHW, Zone 1 > UFH, Zone 2 > rads.
There's one Heatmiser stat for the rads upstairs. UFH has stats in each room.
This is obviously setup like an old-school boiler, inefficient for a heat pump and leads to short cycling.
I purchased a couple of the wireless Mitsubishi stats and set them up, put the system into room temp mode (auto adapt?). However, I soon learned that the Heatmiser stats do actually call for heat and the system will not stop heating until it hits their limit, even when the wireless stats are showing a temp higher than the target.
I disabled 2 dip switches (SW2-1 & SW3-1) which prevents the stats controlling the heat and just act as pump control. This seems to work for the UFH however, Z2 will not heat independent of Z1 and with Z2's pump running will not put any heat into the radiators even while Z1 is flowing at 40c.
It seems the solution to this is: "For 2-zone temperature control, check DIP SW2-7 is set to ON (2-zone temperature control) and DIP SW2-6 is set to ON (With Mixing Tank)"
These are both off, I'm assuming I don't have a mixing tank and cannot just enable these?
I'm looking for a solution, maybe I need to hound the developer?
Tank image:

There’s quite a lot going on here, so we'll try to break it down with some unofficial insights from Mitsubishi. It sounds like your system is set up with two zones at the same design temperature rather than two zones with different temperatures. If that’s the case, SW2-6 & SW2-7 (which are for systems with a mixing tank) wouldn’t apply here. Instead, it seems SW3-6 is managing the two zones with the same temperature settings, and that’s correct for your system as it stands.
When it comes to third-party stats like Heatmiser, they usually work best when the Ecodan’s weather compensation is set up properly. The stats can then manage room temperatures and schedules. One potential tweak might be to check if the Heatmiser stats allow you to adjust the hysteresis (basically the delay between on/off signals). Widening this could help reduce short cycling. Another workaround some people use is combining zones or removing actuator heads to simplify the system and move towards an open-loop design, which can also reduce cycling.
For the Mitsubishi stats, Zone 1 should be fine in Auto Adaptive mode, but Zone 2 has to either follow the weather compensation curve or run in fixed flow mode. To get Zone 2 heating independently, you’ll probably need to look at what’s controlling its pump. It might require adjusting the signal cables or wiring, but it’s hard to say without seeing the full setup.
At this stage, it might be worth getting a heating engineer to take a closer look – they’ll be able to advise on pump controls, wiring changes or any other tweaks to get everything working smoothly. Mitsubishi’s Homeowner Helpline (0161 866 6064) could also be helpful for further advice.
Also, this video might help:
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
- 26 Forums
- 2,208 Topics
- 48.7 K Posts
- 62 Online
- 5,868 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Low Flow Rate Error - 8 kW Ideal Logic ASHP - Help!
@wh0am3ye - OK, starting to make sense, but it does mea...
By cathodeRay , 12 minutes ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
My apologies @batpred I overlooked that you'd already I...
By Transparent , 27 minutes ago
-
RE: Heating Turned Off but Radiators Still Warm
Did you ever get an answer to this? I'm experiencing th...
By 9jwr9 , 1 hour ago
-
🏴☠️🔭😂...
By Pirate Rich , 7 hours ago
-
@editor fortunately we have a boiling water tap in the ...
By bontwoody , 10 hours ago
-
RE: Heat Pump Installers: Competence, Illusion and the Hard Truth Homeowners Must Face
@Fiona, I really don’t want to disappoint you, but I ha...
By Mars , 12 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
@dgclimatecontrol, hard to disagree with that. “Zero di...
By Mars , 12 hours ago
-
RE: Daikin 9kW to 8kW Swap Offer from Octopus
@matban I would have to check the CIBSE guide as we hav...
By ASHP-BOBBA , 12 hours ago
-
RE: Ecodan Energy Monitoring Pack
Hi @carpenterstation Did you ever resolve the energ...
By CAMorgan , 14 hours ago
-
RE: is a home battery without an EV worth it?
I would find it difficult to justify a battery without ...
By Batpred , 14 hours ago
-
RE: What is the Heat Geek Guarantee?
Very useful post, one observation: I can see why instal...
By Batpred , 14 hours ago
-
RE: Widespread failure of insulation installation
And there are different kinds I guess. One fri...
By Batpred , 14 hours ago
-
@drei - there is definitely something not right, notwit...
By cathodeRay , 15 hours ago
-
RE: Octopus tariffs - a quick comparison
Great summary, @majordennisbloodnok! I'd take the ho...
By Batpred , 15 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@mike-patrick I'm no expert... but believe your ASHP is...
By Tim441 , 18 hours ago
-
RE: Renewables & Heat Pumps in the News
Good News from NESO released today which d...
By Transparent , 18 hours ago
-
RE: Samsung Heat pump with Yonos Pico circulating pump running all the time
I agree with your last last sentence, but for another r...
By JamesPa , 18 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Just wanted to share my experience with this kit, as I ...
By Batpred , 22 hours ago