Ecodan with FTC7 controller DHW schedule
Hi, recently had a Ecodan ASHP fitted with solar panels. Has anyone had much experience with the FTC7 controller when it comes to scheduling the DHW. It asks you to prohibit times which I assume prohibits the use of the heating to allow the DHW to work? I’m looking to set DHW to come on for a couple of hours in the early morning and again early afternoon for about 90mins to take advantage of the solar panels (DHW temp 47 degrees).
Any advice to make sure I set the schedules properly?
Hi Cressie,
Welcome.
My experience with a similar Ecodan and solar setup is that there isn't one solution for summer and winter but it all depends on your solar panel capacity and inverter max output.
In the summer it is a no brainer, use the heat pump to heat the water at the sunniest time of the day plus a half hour top up just before the nighttime cheap rate ends.(It will probably not power up for the full half) Depending on the size of the Ecodan and the available solar and inverter, the big load from the ASHP can be handled and even if it drains the battery, there is time to recharge.
Winter is different because the heat pump demand is far more than the solar and the battery can deliver and so you end up drawing on the mains at the more expensive rate and a near empty battery that doesn't have enough time/ sun to recover and supply the evening/ night requirements.
Consequently I have reverted to 2 sessions of DHW at the off-peak rate.
Hope that helps
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 16kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
Posted by: @cressieHi, recently had a Ecodan ASHP fitted with solar panels. Has anyone had much experience with the FTC7 controller when it comes to scheduling the DHW. It asks you to prohibit times which I assume prohibits the use of the heating to allow the DHW to work? I’m looking to set DHW to come on for a couple of hours in the early morning and again early afternoon for about 90mins to take advantage of the solar panels (DHW temp 47 degrees).
Any advice to make sure I set the schedules properly?
We also have a FTC7 and a newer R290 Mitsubishi heat pump. There are prohibits for heating and DHW, to schedule the DHW you want to prohibit the DHW for times you don't want it to run. DHW takes priority over heating so you don't need to prohibit the heating. The other thing to make sure you have enabled is DHW schedule (the on/off toggle on the DHW screen).
What sized heat pump and DHW tank do you have? You might want to investigate if you can do just one DHW a day. We have solar and are on the Octopus Cosy tarrif (which has a cheap rate period 1-4pm), so do DHW at 1pm - if there's solar then it's powered by the sun or cheap rate electricity if no solar.
@robs Hi Rob, thanks for the reply. We have the R32 heat pump. The tank holds 142L and to be honest we don’t use a great amount of DHW so I was wondering whether I’d only need to heat the tank up once a day and obviously in the afternoon to take advantage of the solar panels.
Im on Octopus’s 15M fixed tariff at the moment but have looked at the cosy which has obviously been designed for ASHP users. Do you think it would be worth switching? Only thing putting me off was the Peak Rate charge.
The default setting is that the DHW is always 'on' but actually runs when the tank temperature drops below the max temp drop value. To force the DHW to run at a time of your choosing you insert a prohibition period, and a DHW run commences when the prohibit ends.
So, to make the most of the solar panels' generation you want a run in the middle of the day, or whenever your production is at its peak - it may vary depending on the orientation of the panels. When In the first few months I had the heap pump I thought I was being clever by manually starting a hot water boost run from the button on the controller or from MelCloud when it was a sunny morning to guarantee a solar powered DHW run. Unfortunately all that was happening was the second scheduled run was still occuring, the heat pump was using energy to get the flow temp up to the maximum temperature required for the HW, but this was not then needed to actually put any heat into the tank.
If you can last a full day with a single DHW run, frequently solar-powered, this will be more energy efficient than having two runs. To make this more likely you could consider raising the temperature you heat the tank to, up into the fifties, so your are simply storing more heat. You'll have to see how much hot water you regularly get through and whether it lasts into the morning - I have a 210l tank and the morning showers are still plenty hot enough.
The other way to avoid programming two runs is to make use of the reheat settings. If you insert a single short prohibit to force a middle-of-the-day run then after that is completed the DHW remains 'on' and a further DHW run is allowed should the tank temperature fall beyond the max temp drop value. The default for this is 10°, which means for you 10° below 47°. You might be surprised how low the measured tank temperature can get before you notice that you are running out of hot water - it depends on where the thermistors are placed in your particular tank. The tank will also lose temperature without any hot water draw of several degrees a day. So to avoid unwanted reheats you might choose to effectively restrict the DHW windows quite narrowly - as you are doing. The alternative is to increase the max drop value a lot so you are closer to being out of hot water before the reheat kicks in. It might be a strategy to allow for high use evenings not having a consequence of tepid water in the morning, without unnecessary non-solar DHW runs.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Posted by: @cressie@robs Hi Rob, thanks for the reply. We have the R32 heat pump. The tank holds 142L and to be honest we don’t use a great amount of DHW so I was wondering whether I’d only need to heat the tank up once a day and obviously in the afternoon to take advantage of the solar panels.
Im on Octopus’s 15M fixed tariff at the moment but have looked at the cosy which has obviously been designed for ASHP users. Do you think it would be worth switching? Only thing putting me off was the Peak Rate charge.
142L is not very big but if you don't use much DHW then it's worth seeing if only one DHW reheat a day works.
Do you have a battery with your solar? As there is a cheap rate period just before the peak rate it is possible to use the battery and avoid the peak rate charges entirely.
@harriup thanks for the advice and information. I’m leaning towards going one run in the afternoon but increasing DHW temp to low 50s as with the amount of water we use we would probably get away with it.
@cressie I have noticed a trend in the last year or so; the attitude seems to be towards having a battery - even in preference to solar PV if the budget won’t run to both. I think it reflects the use of TOU tariffs as much as anything. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @cressie@robs unfortunately I don’t have a battery which is the reason I’m apprehensive about the cosy tariff!
Cosy has the 3 hours of peak rate and the day rate is appropriately 1.5p per hour more - which is appropriately equivalent to another hour and a half of peak rate. With 8 hours of cheap rate, even without a battery it should be cheaper. But not as much as if you had a battery.
I wonder if I am missing something here, regarding heating DHW with the heat pump in the middle of the day.
I found that the heat pump would be be taking 10kW or more for a significant time and my solar can only deliver 4kW. Consequently I am using the remaining power from the grid at the time that it is most expensive.
The heat pump is on weather compensation for the radiators and obviously is consuming far less than that, so could the heat pump be modulated in some way when heating DHW so that it is within the capacity of the inverter?
I have to add that it is a big tank, (500l) and the thermostat is about 2/3 down.
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 16kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
- 26 Forums
- 2,356 Topics
- 53.4 K Posts
- 188 Online
- 6,017 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@andrewj Seeing they deleted both threads with the pict...
By HarrisonC , 9 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@mars I think your commentary is very fair and balanc...
By JamesPa , 10 hours ago
-
RE: External pipework insulation
That's great advice @transparent... thank you. @david...
By Mars , 10 hours ago
-
RE: Advice on internal circulation pump noise
Thanks @mikefl - I'll maybe have a look at the lock-shi...
By jtg , 12 hours ago
-
RE: Heat Pump Heats the House… But It’s Not Cosy. Emitter Changes or System Tweak?
@toodles interesting suggestion, thanks. I will try to...
By GrahamF , 12 hours ago
-
RE: Mitsubishi Ecodan Auto Adaption trial to stop cycling.
The interval you talk of, i think, will be 60min for an...
By F1p , 16 hours ago
-
RE: Electricity price predictions
Does anyone have a current graphic, visual or breakdown...
By Mars , 19 hours ago
-
Agree with @majordennisbloodnok on the setbacks. We hav...
By ChandyKris , 1 day ago
-
RE: New Fogstar 15.5kWh upright solution
It is a matter of luck. 2ith Fogstar "instructions", to...
By Batpred , 1 day ago
-
RE: Speedcomfort radiator fans
@deltona the way the links were added broke the page. A...
By Mars , 1 day ago
-
RE: Setback savings - fact or fiction?
I agree! Even more so if we get an answer! But the chal...
By cathodeRay , 2 days ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
This has been delayed from what I believe to be this ye...
By dgclimatecontrol , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
this is why I provided current flow temperatures in the...
By ksim , 2 days ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
There's many homes that would be quite a disruption for...
By dgclimatecontrol , 2 days ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@rhh2348 ...maybe this option is what you want? Alter...
By benson , 2 days ago
-
RE: Free Ecoheat Heat Pump Install
@old_scientist This does make the unit smaller as the b...
By dgclimatecontrol , 2 days ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
@old_scientist hiya mate, did you ever get to the botto...
By 9jwr9 , 2 days ago
-
RE: Configuring third party dongle for Ecodan local control
@majordennisbloodnok I think the HPDHD diagnosis may be...
By Sheriff Fatman , 3 days ago