Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@kev-m Thanks kev-m, but I'm still not sure if my setup is correct. What I really want to know is - do your house thermostats stop your HP (and it's pumps) when they all stop calling for heat? If so, then your thermostat/ Heatmiser signal cables are still connected to your FTC, which mine aren't. I could just reconnect mine, and see if AA is still operating, but it might be difficult to know if it is, or if it is just running dumbly to the RC target. How can you tell if AA is actually operating?
You have your thermostats up high, so your manifold pumps must be running all the time? I know they don't use much power but it's still a waste. I am trying to program my Salus RT500 thermostats (£19 in B&Q if available), so as not to be all on all the time, if I can do it so the AA is not affected.
Another question, I think you said previously that you can program a night setback into the mitsubishi wireless controller. I haven't got one yet or seen that stated anywhere, so do you just mean - turn it down a few degrees at night and back up in the morning?
Regards S
Sliderule: Just to be sure what are we talking about here:
- Mitsubishi wireless controller gives HP info about room(zone) temperature and it is used when HP is in AA mode.
- ordinary thermostat which is connected to FTC directly (don't know which input) is just saying ON / OFF - and HP can't be smart about it I believe
Posted by: @sliderule@kev-m Thanks kev-m, but I'm still not sure if my setup is correct. What I really want to know is - do your house thermostats stop your HP (and it's pumps) when they all stop calling for heat? If so, then your thermostat/ Heatmiser signal cables are still connected to your FTC, which mine aren't. I could just reconnect mine, and see if AA is still operating, but it might be difficult to know if it is, or if it is just running dumbly to the RC target. How can you tell if AA is actually operating?
You have your thermostats up high, so your manifold pumps must be running all the time? I know they don't use much power but it's still a waste. I am trying to program my Salus RT500 thermostats (£19 in B&Q if available), so as not to be all on all the time, if I can do it so the AA is not affected.
Another question, I think you said previously that you can program a night setback into the mitsubishi wireless controller. I haven't got one yet or seen that stated anywhere, so do you just mean - turn it down a few degrees at night and back up in the morning?
Regards S
My house thermostats are still connected to the FTC but turned up high and the external pumps definitely don't run all the time.
If you want to know whether AA is working, turn up the set room temp when the radiators are already warm/hot. If AA is working the rads will get noticeably hotter as it attempts to warm the house, if not they won't.
The setback is programmed into the FTC rather than the wireless controller. You can programme in a setback or switch it off and on. The wireless controller just communicates the room temp to the FTC. You can override the set programme by changing the temp on either the wireless controller or the wired one. Sorry if I'm stating the obvious but you can programme in the setback without having the wireless controller.
Good morning Kev. I've searched the forum but haven't found the necessary info. Could you please be kind enough to point me to instructions on how to programme a setback on the FTC? I fancy giving it a go to see if I can save some energy/money overnight. At the moment I'm running my Ecodan 11.2 24/7 on auto adaptation and would like to try a setback of a couple of degrees overnight from say 10 pm to 4 am.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Thanks kev-m, this forum really helps to get my head around these issues, and the penny has finally dropped. On installing the replacement HP, a house wiring issue emerged which meant the living room thermostat had to be disconnected from the FTC or rewired. From another forum I thought that with AA, thermostats were not connected to the FTC, so I wouldn't have to rewire, but from what you say, they normally are. I ran on WC for 35 days with some inconvenience, and got an overall reported COP of 4. I have run for 4 days so far temporarily on AA, and the COP is also 4. I will carry on running AA for a while, with the thermostats disconnected and see how it goes. AA has the advantage of being able to adjust the temperature from my phone, and seems to reduce cycling without noticeably increasing power consumption.
What I meant by "how do we know if AA is actually operating" was in comparison to non intelligent Room Thermostat control. I know that there is a dipswitch to set it on or off, but in my situation of unconnected thermostats, I wondered if it was really working as it should. I will just have to see how it goes.
Yes I was using "setbacks" by programming the FTC timer to off for some hours at night. With AA, I turn down the FTC temperature 2 degrees until morning and then turn it up again.
I am happy using my Salus RT500 programmable thermostats to switch on and off rooms which don't need heat all the time, such as Bedrooms, Bathrooms and hallways, and for setback in the living room. These thermostats are not very sensitive, which is a good thing with our all-UHF house as they aren't continually switching on and off. They are also cheap if you can get them now.
Regards S
Posted by: @morganGood morning Kev. I've searched the forum but haven't found the necessary info. Could you please be kind enough to point me to instructions on how to programme a setback on the FTC? I fancy giving it a go to see if I can save some energy/money overnight. At the moment I'm running my Ecodan 11.2 24/7 on auto adaptation and would like to try a setback of a couple of degrees overnight from say 10 pm to 4 am.
Morgan, try this Mitsubishi video.
It shows how to set a On off schedule and vary temperatures along the time line. Just remember that Auto adapt tends to over heat by 1 degree C so try setting temp at 19 to see what temperature the room stat rises to. Also set the night time set back to 17c. We have found that a rise in small steps of 1c at a time has worked best for us, in preventing fast heat rises which would otherwise use more energy. Once you’re familiar with how your house responds you could try lowering your night time set back temperature a little further.
Kev might have views on what works for him.
Thank you. I only want to vary the overnight temp by a couple of degrees lower rather than having the system off.
I was using the wrong words for searching. 🙄
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
But it is a shame that you can't set temp to 0.5°C (as with wireless remote or via melcloud).
Posted by: @sunandairPosted by: @morganGood morning Kev. I've searched the forum but haven't found the necessary info. Could you please be kind enough to point me to instructions on how to programme a setback on the FTC? I fancy giving it a go to see if I can save some energy/money overnight. At the moment I'm running my Ecodan 11.2 24/7 on auto adaptation and would like to try a setback of a couple of degrees overnight from say 10 pm to 4 am.
Morgan, try this Mitsubishi video.
It shows how to set a On off schedule and vary temperatures along the time line. Just remember that Auto adapt tends to over heat by 1 degree C so try setting temp at 19 to see what temperature the room stat rises to. Also set the night time set back to 17c. We have found that a rise in small steps of 1c at a time has worked best for us, in preventing fast heat rises which would otherwise use more energy. Once you’re familiar with how your house responds you could try lowering your night time set back temperature a little further.
Kev might have views on what works for him.
Yes that's the one. It's bit fiddly but worth persevering with. I agree about AA overheating but now Mrs M has got used to 22 deg I'm not going to get away with the 21 deg I meant to have!
I haven't tried stepping the morning temp rise (I will) but I agree about AA trying to heat the house up quickly. I set mine to 21 deg with a setback to 17 deg 10pm to 6am. I might have to decrease the setback time as it gets colder outside. In practice this is almost an onn/offf setting since the IAT rarely drops below 17 deg.
Posted by: @kev-mPosted by: @sunandairPosted by: @morganGood morning Kev. I've searched the forum but haven't found the necessary info. Could you please be kind enough to point me to instructions on how to programme a setback on the FTC? I fancy giving it a go to see if I can save some energy/money overnight. At the moment I'm running my Ecodan 11.2 24/7 on auto adaptation and would like to try a setback of a couple of degrees overnight from say 10 pm to 4 am.
Morgan, try this Mitsubishi video.
It shows how to set a On off schedule and vary temperatures along the time line. Just remember that Auto adapt tends to over heat by 1 degree C so try setting temp at 19 to see what temperature the room stat rises to. Also set the night time set back to 17c. We have found that a rise in small steps of 1c at a time has worked best for us, in preventing fast heat rises which would otherwise use more energy. Once you’re familiar with how your house responds you could try lowering your night time set back temperature a little further.
Kev might have views on what works for him.
Yes that's the one. It's bit fiddly but worth persevering with. I agree about AA overheating but now Mrs M has got used to 22 deg I'm not going to get away with the 21 deg I meant to have!
I haven't tried stepping the morning temp rise (I will) but I agree about AA trying to heat the house up quickly. I set mine to 21 deg with a setback to 17 deg 10pm to 6am. I might have to decrease the setback time as it gets colder outside. In practice this is almost an onn/offf setting since the IAT rarely drops below 17 deg.
AA mode is designed to keep the IAT constant, so to the controller even 1C setpoint change is a large deviation between desired and actual. This is the reason why the LWT will be ramped up in what is thought to be an aggressive manner. I believe that gradually increasing the setpoint over several hours may produce a more sedate response from the controller.
I don't know how you have it in your country (UK?) but in our country price of electricity is cheapest during the night. And also HP is meant for 24/7 as this enables operation at lowest flow temperatures. So I don't know how much is it possible to save if heating temp is decreased during night as this means that HP must run harder in the morning.
- 27 Forums
- 2,539 Topics
- 59.1 K Posts
- 737 Online
- 6,818 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Balancing is a long process and its possible to mess th...
By JamesPa , 17 minutes ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 1 hour ago
-
Thanks everyone for the help, Havenwise now diasbled. q...
By Boycey , 3 hours ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli Depending on whether you can get an EV tariff, I...
By ChandyKris , 4 hours ago
-
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 6 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@technogeek I think you are correct, but, it didn’t inf...
By Papahuhu , 6 hours ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 7 hours ago
-
@Mars at the time of writing heating oil is £1.28 / ltr...
By TechnoGeek , 7 hours ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 10 hours ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 10 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
The setup for this is a Samsung Modbus card. Connected ...
By antonical , 11 hours ago
-
RE: Forum updates, announcements & issues
@davidalgarve, if the emails are more than roughly a mo...
By Mars , 12 hours ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 12 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Sorry to hear that but I'm not surprised TBH. Stratifi...
By JamesPa , 13 hours ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 1 day ago
-
RE: Setback savings - fact or fiction?
The answer was in two parts in my reply, the second par...
By RobS , 1 day ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 1 day ago
-
Ecodan control return to Melpump from Havenwise trial. settings check
Hi, Just got control back after being on the hav...
By Boycey , 1 day ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
I wonder if heat pump manufacturers will tone these sit...
By JamesPa , 1 day ago
-
RE: Who’s Caved and Switched the Heating On Already?
@editor yesterday we used 12kW of electricity for heat,...
By Judith , 1 day ago
-
RE: Rate the quality of your heat pump design and installation
Loss assessments can be a very serious case of GIGO. I...
By JamesPa , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@jamespa Just bizarre. This is our data. I really don't...
By antonical , 2 days ago
-
RE: Mitsubishi Ecodan 11.2kW review
I think you said its an 11.2kW model and your house is ...
By JamesPa , 2 days ago