I’ve installed MAC-587IF-E on my Ecodan. When I open the Melcloud app, it shows my Room Temperature -39C. Can anyone suggest where this data comes from? I guess I’m missing a room sensor? As I live in an area where it’s often subzero temperatures outside, I was hoping I could monitor my house temperature via Melcloud when I’m away for extended period.
Another disappointment is that Melcloud app seems to only support underfloor heating adjustments when not using “Curve” (weather compensation). When Curve is activated, I still see the slider set at 20C and no matter where I slide it, it doesn’t trigger change to Ecodan. When I change it to Room, the slider works fine and sends the data through.
My system is installed with one zone which heats both floors and rooms are manually adjusted by thermostats. Everything works fine and I’m happy with the efficiency. It’s just the lack of control via app.
Any advice is much appreciated.
Firstly, Melcloud isn't great at controlling the Ecodan.
I don't know where the -39 comes from but you can set where the room temperature is monitored from the initial settings menu on the main FTC control panel.The source of the temperature is the main wired control, a remote thermistor wired into the FTC or the Mitsubishi wireless controller. It will not show the temperature from a third party thermostat.
When curve is activated, you are right it won't respond to a change in room temp because you are not in room temp mode. The only way I've found to control the heating via the app is when you are in room temp mode.
Where is your main FTC controller? Is it in your living space?
As I said, the app isn't that good.
You can change the flow temp and target room temp via the app, but not the WC curve or the offset. A bit frustrating for me as my installer put the FTC in the boiler cupboard, meaning it is useless as a thermostat/temp sensor for Room Temp targetting. My only option therefore if I want to control the indoor temp remotely is to not use WC and instead manually adjust the flow temperature.
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
Thanks for your valuable input regarding WC. That’s unfortunate.
Kev M, thanks for the tip regarding initial settings. I changed sensor to Main RC and now it’s +29C. It’s probably what it is inside the controller panel. Let’s see how useful of a reference number that will be. I guess there’s no way to move that sensor outside?
On another note, I’ve noticed once before and just saw again that the black flash icon was on, meaning the electric heater is activated. I wonder why it does that? It’s +2 outside and DHW is 50 degrees. House heating is on. It is quite windy outside but it looks a bit odd it would use electric heater now and did fine when it was -15 outside a few weeks ago.
Posted by: @marthThanks for your valuable input regarding WC. That’s unfortunate.
Kev M, thanks for the tip regarding initial settings. I changed sensor to Main RC and now it’s +29C. It’s probably what it is inside the controller panel. Let’s see how useful of a reference number that will be. I guess there’s no way to move that sensor outside?
On another note, I’ve noticed once before and just saw again that the black flash icon was on, meaning the electric heater is activated. I wonder why it does that? It’s +2 outside and DHW is 50 degrees. House heating is on. It is quite windy outside but it looks a bit odd it would use electric heater now and did fine when it was -15 outside a few weeks ago.
The temp sensor is inside the main FTC control panel (the one you use to change settings). You can move that panel depending on how long the cable is. Alternatively you can attach a remote thermistor pac-se41ts-e to the main FTC box. It comes with a very long cable. You can get them for about £20 on ebay. That's what I use and it works well. Once it's attached another option appears in the initial settings menus you've already used.
I don't know why the electric heater is on. Maybe a legionella purge?
@scrchngwsl I am on the weather compensation setting but I can’t understand why Melcloud does not give me any flow temperatures. Temperature reports include a flow temperature feature but this I’d greyed out
@dotty9943 tap on the greyed out flow temp. What happens?
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @dotty9943@scrchngwsl I am on the weather compensation setting but I can’t understand why Melcloud does not give me any flow temperatures. Temperature reports include a flow temperature feature but this I’d greyed out
I assume you have tried tapping on the greyed out options? If they are available, doing this un-greys them.
-39C means that the software running the FTC is a buggy version that needs to be updated. There is a firmware check in the MelCloud app, I presume this is the software that needs to be updated (mine was changed during an engineer visit), there's only one way to find out! When you switch to room mode the FTC will be using this incorrect temperature as a gauge of how much energy it needs to put in, this will be massively wrong, which is what might be triggering the back-up heaters to come on . You don't want to be in room mode until you have an accurate temperature showing.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
@kev-m Now that you have solved the problem of temperature readings, this has enabled me to move on to the next stage of my attempts to find out why my heat pump is achieving such poor COP scores (They are about 2.3 when the predicted score is 3.2 and better. We have done the following without much progress
a. On the basis of the Ecodan recommendations following a heat loss study, we have up graded all our radiators
b. We have replaced doors and windows so that all our doors and windows are now double glazed
c. We have put new thicker insulation in our loft
c. We have put throttles in our chimneys
d. Our radiators were rebalanced last week
e. We have set weather compensation so that flow temperature is at the recommended level
f. The heat loss study confirmed that our 14 kw is big enough to heat our. House and compensate for the heat loss
G. The system was serviced in December, when the filters were cleaned.
My web researches don’t suggest any other explanation for poor efficiency so can any one come up with new ideas? Failing that I don’t know what to do short of taking our heat pump out and starting again with an efficient combi boiler
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 66 Online
- 5,673 Members
Podcast Picks
Latest Posts
-
Engineer has been. Prob air locks....undid a few things...
By Profzarkov , 58 minutes ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 2 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 4 hours ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
A bit of a follow up on the progress of the Ecodan pump...
By ThunderMink , 5 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
After our rather lengthy meander off piste, I thought I...
By GrahamF , 6 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - to collect the IAT/OAT data, can I sugges...
By cathodeRay , 7 hours ago
-
RE: Ecodan software update. Real or scam?
@vinz86 Contact Mitsubishi and an engineer attends and ...
By ASHP-BOBBA , 17 hours ago
-
My Samsung Gen6 (probably same controller as yours) onl...
By Old_Scientist , 1 day ago
-
@drei When I was in local government we were of cours...
By JamesPa , 1 day ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 1 day ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Hope they know what they're doing regarding paint types...
By PatrickVito , 2 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 2 days ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 2 days ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 2 days ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 2 days ago
-
@mars That response surely deserves a nomination for Tu...
By JamesPa , 3 days ago
-
Specifying batteries, pv solar etc using ChatGPT
I thought I'd try to use ChatGPT to specify my requirem...
By Tim441 , 3 days ago