Posted by: @mjrSo, I wonder whether the settings influence AA mode as well as room temp mode
I just want to check I'm not miss-understanding something. I thought Room Temp Mode, and Auto-Adaptive Mode were the same thing, the two names just get used interchangeably?
@sunandair looks like its a Salus MP200A. adjusting the pump speed via the FTC panel. when changing between 1 & 5 I hear nor feel any change from the pump (I presume this is the pump I am adjusting!)
Posted by: @sunandairis it true that you don’t get cycling when doing the DHW re-heat and this is generally at a higher set temperature?
You will not get cycling in DHW mode because the heat pump is working harder, so is operating within its specified control envelope. Cycling occurs when the heat energy demand is lower than the minimum heat energy output, so the heat pump must periodically stop to prevent overheating the building.
Posted by: @gotaashpPosted by: @mjrSo, I wonder whether the settings influence AA mode as well as room temp mode
I just want to check I'm not miss-understanding something. I thought Room Temp Mode, and Auto-Adaptive Mode were the same thing, the two names just get used interchangeably?
You little devil, you've been reading the instructions again. Shame on you. 😋
@gotaashp in post #2 of this thread, MJR states:
Now, a possible saving grace: you have an ecodan so you might not need to figure out the curve for yourself. If the right switches are set in the unit (and they are by default), the "room temperature" mode is replaced by an "auto adapting" mode where the controller is supposed to learn for itself what temperature is needed given the current indoor and outdoor temperatures.
which also made me wonder if my system is configured from Room Temp or AA. I don't know if there is anyway of telling?
Posted by: @si-fillo@gotaashp in post #2 of this thread, MJR states:
Now, a possible saving grace: you have an ecodan so you might not need to figure out the curve for yourself. If the right switches are set in the unit (and they are by default), the "room temperature" mode is replaced by an "auto adapting" mode where the controller is supposed to learn for itself what temperature is needed given the current indoor and outdoor temperatures.
which also made me wonder if my system is configured from Room Temp or AA. I don't know if there is anyway of telling?
Room Temperature and Auto Adaptation are indeed the same animal. 😎
There are 3 heating modes
• Heating room temp. (Auto adaptation)
• Heating flow temp.
• Heating compensation curve.
Posted by: @derek-mYou little devil, you've been reading the instructions again. Shame on you.
![]()
lol. Assuming I've not missed anything, I do wish they would standardise the naming. I'm guessing they re-branded it at some point.
Posted by: @gotaashpPosted by: @derek-mYou little devil, you've been reading the instructions again. Shame on you.
![]()
lol. Assuming I've not missed anything, I do wish they would standardise the naming. I'm guessing they re-branded it at some point.
It's just good business. Confuse the customer with 'smoke and mirrors', so they have to pay for a visit from the expensive Service Engineer. Simples. 😎
after doing some googling on the pump (Salus MP200A), I read...
This pump is equipped with a control panel on the front for easy operation by users.
...which I guess might enable me to adjust flow speed. The problem being, the said control panel's face is hard against the floor and little/no chance of reading the display. I guess I'll have to live with the flow rate (17/18l/m (range 10-25)) but was hoping that a slower flow would help improve DT (currently at 2)
@si-fillo it’s possible you have a bespoke installation where the pumps may be off the shelf and don’t respond to the ftc controls.
We have 2 independent pumps with 5 speed settings controlled from the pump itself. Push button with neon speed indicators. The system still reads the flow rate.
Perhaps your installer can tell you how to adjust the pump speed and if you have more than one pump you will possibly need to adjust all pumps to get a reduction in flow rate. Without knowing more about your system it’s difficult to be more specific than this at this moment.
Posted by: @derek-mPosted by: @si-fillo@gotaashp in post #2 of this thread, MJR states:
Now, a possible saving grace: you have an ecodan so you might not need to figure out the curve for yourself. If the right switches are set in the unit (and they are by default), the "room temperature" mode is replaced by an "auto adapting" mode where the controller is supposed to learn for itself what temperature is needed given the current indoor and outdoor temperatures.
which also made me wonder if my system is configured from Room Temp or AA. I don't know if there is anyway of telling?
Room Temperature and Auto Adaptation are indeed the same animal. 😎
There are 3 heating modes
• Heating room temp. (Auto adaptation)
• Heating flow temp.
• Heating compensation curve.
What happens if you run room temp mode with the Auto Adapt dip switch 5-2 set to inactive? I haven't tried it nor do I know if it's even possible.
- 26 Forums
- 2,104 Topics
- 46.3 K Posts
- 104 Online
- 3,393 Members
Join Us!
Latest Posts
-
RE: Crystal Ball Time: Communal or even Area Energy Storage?
I am invested in a couple of listed energy storage fund...
By Old_Scientist , 2 hours ago
-
This might be useful for @bart From/p> "Warning: It...
By RobS , 2 hours ago
-
-
RE: Who's your electricity provider and what's your tariff?
That would be my biggest commitment -time to gain great...
By SUNandAIR , 10 hours ago
-
RE: Who has a V2G EV installation
As has been discussed on other threads, trying to justi...
By Majordennisbloodnok , 1 day ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Thanks @mikeh. Then I will also go back to non smart ta...
By ChandyKris , 1 day ago
-
RE: Location of hot water isolation valve on cylinder
@transparent Thank you so much and very helpful. Earlie...
By rossowheels , 2 days ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
It does indeed look like that, @skyefarmer. There is ...
By Majordennisbloodnok , 2 days ago
-
RE: Plug and play solar. Thoughts?
Have a read of my previous posts on so-called Balcony S...
By Lucia , 3 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 3 days ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 4 days ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 4 days ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 5 days ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 5 days ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 5 days ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 6 days ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 6 days ago