Ecodan high pressure at 3 bar
We have a Mitsubishi Ecodan with UFH downstairs and radiators upstairs. The pressure at the water tank is 3 bar.
I have lowered this by bleeding water from the radiators to 2 bar as indicated by the fixed red marker on the pressure gauge.
This has gone back up to 3 bar and there is water coming from all the radiator bleed valves when opened so no air in them it seems.
We have had 2 new towel rails replacing cheap old ones. Not sure if this has anything to do with it.
Any advice on how I can resolve this issue and what might be causing it?
Andy
Something similar happened to me once with a gas system boiler. The filling loop hadn't been closed properly and it was pushing up the pressure over time. You might want to check that.
Posted by: @dorkyparkThe filling loop hadn't been closed properly and it was pushing up the pressure over time. You might want to check that.
That's a good reason to disconnect the filling loop when not in use, in the way that it is designed for!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hi thanks for that, I'm not sure if I'm correct but I seem to remember having to open a valve to add pressure to the system. Would this be the valve that you mean? It was fully open and I've now closed it.
Yes, you would need to reduce the pressure to the correct value for your system (usually 1 to 1.5 bar when cold).
And as @jamespa says, disconnecting the filling loop when not used is the correct thing to do.
@sand I far as I am aware, all systems have two of these valves (one on each side of the mains feed to the red tank; these should both be shut off after any adjustment to pressure. (I may be wrong but all systems I have come across have the two valves and plumbers have told me they should both be shut after adjustments are complete.) Nervously, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @toodles@sand I far as I am aware, all systems have two of these valves (one on each side of the mains feed to the red tank; these should both be shut off after any adjustment to pressure. (I may be wrong but all systems I have come across have the two valves and plumbers have told me they should both be shut after adjustments are complete.) Nervously, Toodles.
You are correct, but they also come with thumb-turn fittings so they can be disconnected easily. On mine at least its necessary to do this to be sure that the shut off valve is truly shut off.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 16 Online
- 5,662 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Sanity check please. Battery storage and inverter sizing.
@old_scientist yes already have a 4kwp array on a vener...
By AdamK , 4 hours ago
-
RE: Rodents! A word of warning for heat pump owners
Thanks for this. My pipe insulation in my garage has...
By JamesPa , 5 hours ago
-
RE: Why so many sigenergi installer recommendations?
I've noticed lots of love for them on YouTube too - I w...
By Old_Scientist , 7 hours ago
-
@editor Something changed in this last 12 months, they ...
By ASHP-BOBBA , 9 hours ago
-
RE: Ecodan & MelCloud scheduling
I put the above question to Mitsu UK at the sme time as...
By DavidAlgarve , 17 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: EGP01 Manufacturer: Samsung Model: 8K...
By EGP01 , 2 days ago
-
Thanks for the heat geek info. I've fitted my own heat ...
By bontwoody , 2 days ago
-
RE: Does anyone have experience of a smart water meter?
Just to give a sense of scale, I've used the CCW water ...
By Majordennisbloodnok , 2 days ago
-
RE: Powerwall 3 or Myenergi or something else?
We have a Tesla Powerwall 3, recently installed, so I m...
By Old_Scientist , 2 days ago
-
RE: Mitsubishi PAR-WT60R-E Wireless Controller installation
@morgan They have been paired once but it was thought b...
By DavidAlgarve , 3 days ago
-
RE: Isolating the system for a planned power cut
A great many ground-mounted local substation transforme...
By Transparent , 3 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 4 days ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 5 days ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 5 days ago
-
RE: Mitsu Wireless Controller and MelCloud
Well it has now become obvious that the installation of...
By DavidAlgarve , 6 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 6 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 1 week ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 1 week ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 1 week ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 1 week ago