Ecodan Auto Adapt Questions

41 Posts
6 Users
3 Reactions
2,060 Views
(@richard24738)
Estimable Member Member
1113 kWhs
Joined: 1 year ago
Posts: 79
Topic starter  

@boycey If I remember correctly, when the engineer fitted the replacement thermostat, the cable wasn't very long.

Yes, my thermostat is in the same position as yours; on the back, top right from the front.

As Mitsubishi are going to send an engineer, I don't think I should try repositioning at this stage.

Thinking about this a bit more, the excess reading is when it's sunny but the thermostat, being behind the pump, is not necessarily in the sun. It is for a while though when the sun is low at this time of year.

My original thought was that it was reflected heat from the house brickwork behind the pump. You can really feel the heat from the brickwork in the summer.

It's currently 39cm from the back wall so well within the 30cm that mitsubishi specify.

Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate


   
ReplyQuote
(@jamespa)
Famed Member Moderator
11242 kWhs
Veteran
Joined: 2 years ago
Posts: 2127
 

Posted by: @richard24738

As Mitsubishi are going to send an engineer, I don't think I should try repositioning at this stage.

Thats good news

Posted by: @richard24738

My original thought was that it was reflected heat from the house brickwork behind the pump. You can really feel the heat from the brickwork in the summer.

It's currently 39cm from the back wall so well within the 30cm that mitsubishi specify.

Hopefully your obs today will clarify whats going on so you can tell the Mitsi engineer! 

The reflected heat from my south facing white wall has definitely not subsided 30cm from the wall.  

Silly design, which obviously they know as they modified it for the R290

 

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@richard24738)
Estimable Member Member
1113 kWhs
Joined: 1 year ago
Posts: 79
Topic starter  

@jamespa Extending the cable is not something I would like to attempt especially as Mitsi have agreed to send an engineer. Perhaps he will do it.

It's quite sunny now but cold. If the temperature rises, I'll try shading the unit.

 

Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate


   
👍
1
ReplyQuote
(@richard24738)
Estimable Member Member
1113 kWhs
Joined: 1 year ago
Posts: 79
Topic starter  

13:51 - Pump is "idle"

Temperature in the shade at the side of the house 14c.

Outdoor temperature reading of the heat pump 21c.

The top of the pump is shaded with an umbrella.

I have placed a normal thermometer on the back of the heat pump at the top and it reads 21c so that means the Mitsi outdoor thermostat is reading correctly.

Placing my thermostat near the bottom of the heat pump close to the cooler side of the house reads 18c.

Unfortunately, it looks like a sun and shade issue.

@jamespa: you mention a change on the R290. I can't find any documentation. Do they now do wifi remote or is it simply a positional change?

 

Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate


   
ReplyQuote
(@jamespa)
Famed Member Moderator
11242 kWhs
Veteran
Joined: 2 years ago
Posts: 2127
 

Posted by: @richard24738

@jamespa: you mention a change on the R290. I can't find any documentation. Do they now do wifi remote or is it simply a positional change?

It wasnt me that mentioned this, was someone else, I was only repeating what appeared to be a very plausible statement.

 

Posted by: @richard24738

Unfortunately, it looks like a sun and shade issue.

Yup.  Well at least you can tell the Mitsubishi engineer what problem he has to fix.  He may of course simply turn up with a sensor on a longer wire.

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
Page 4 / 4



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security