Posted by: @richard24738James: Just noticed the timing of the drop: from 21 c at 16:05 to 10c at 16:45.
Useful. When did it go into shade? If not then, what else was happening at the same time?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Sorry not exactly sure about when it went into shade but my feeling is at the same time as the temp drop.
Clutching at straws:
- I did have a Tesco delivery at 16:05 so the front door to the house was open for a while but I can't see how that would influence the outdoor temp.
- my heating timing has a room temp increase from 21c to 22c at 16:00
If it's sunny tomorrow, I'll keep an eye on the temp and if it spikes I'll try to add some shade.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate
@richard24738 if the sun's out, aren't you getting solar gain in the house?. We have the same thing, our HP is on the south side so get sun directly on it, but although it's only a couple of degrees outside we get warmed up a lot for free from the sun. The next day it may be cloudy and so not affect the HP. So it's not really an actual problem for us. Do you find the same? Or am I missing the point?
I think the point is that the sun can be out, but it can still be very cold, so you still need some heating. @richard24738 seems to have a problem that, when the sun is out (?), his outdoor sensor which controls the weather compensation reads 20 degress plus, so the ASHP stops heating altogether. It seems likely that its because its in the sun (it should be in the shade), but this is yet to be proved.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@boycey Heat pump is located at the back of the house and yes I agree, yesterday the sun was out and the rooms at the back of the house had some solar gain.
Mitsubishi were concerned that the outdoor temperature reading would adversly affect the Auto Adapt calculations.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate
@jamespa Many thanks for comment.
I can't recollect any location instructions from Mitsubishi stating that the unit should be in the shade, only physical positioning. Maybe it's an unwritten rule.
I believe other heat pump manufacturers allow the relocation of the outdoor thermostat sensor.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate
Posted by: @richard24738I can't recollect any location instructions from Mitsubishi stating that the unit should be in the shade, only physical positioning. Maybe it's an unwritten rule.
Thats bizarre. It definitely needs to be in the shade! There is a reason small weather stations are inside Stephenson's screens!
Posted by: @richard24738I believe other heat pump manufacturers allow the relocation of the outdoor thermostat sensor.
Vaillants are wireless so they cant really tell. Not sure about Mitsubishi but it obviously needs to be relocated if its in the sun. Suggest you perform the experiment to prove (or disprove) that this is the cause. Temperature sensors are pretty reliable, so its definitely the most likely.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa The mitsubishi outdoor thermostat is attached to the protection frame at the back of the heat pump and connects via a short red cable. There doesn't appear to be any flexibility in positioning.
When the original thermostat was replaced, the engineer positioned it in the same place..
It looks like today is going to be sunny again so will watch things more closely.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate
@richard24738 yes, the R32 its attached to the frame, on the new R290, then can be places away from the unit. This make the weather comp much worse on the R32 units
Posted by: @richard24738@jamespa The mitsubishi outdoor thermostat is attached to the protection frame at the back of the heat pump and connects via a short red cable. There doesn't appear to be any flexibility in positioning.
Thats a bit of a design flaw. Maybe a strategically placed sunshade is required!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@richard24738 have you popped the cover of to see if there's any length tucked inside, if you (we) could position it nearer the bottom of HP I would think that could make a fair difference. Mines on the top right rear corner, looking from the front.
Posted by: @boycey@richard24738 have you popped the cover of to see if there's any length tucked inside, if you (we) could position it nearer the bottom of HP I would think that could make a fair difference. Mines on the top right rear corner, looking from the front.
Good idea.
If you can move it, try to avoid placing it somewhere it gets affected by whether the unit is on or off.
Midea heat pumps (or at least the Midea heat pump owned by @cathoderay) have an air intake sensor which doubles as the outdoor temperature sensor. This appears to be pretty much OK when the heat pump is running, because its constantly drawing fresh air over the sensor, but when its not running the sensor gets warmed by the residual heat in the unit, thus distorting the readings. In practice this probably doesn't matter much unless you are trying to work out whether setback costs money or saves money, which is how the issue came to light.
Temperature sensors are often fairly high resistance thermistors and so can be extended with any ordinary two core cable. My installer did that for my DHW tank sensor. It probably invalidates the warranty though!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 22 Forums
- 2,032 Topics
- 44.3 K Posts
- 37 Online
- 3,237 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
Welcome to the forums. It’s clear that you’ve taken t...
By Mars , 51 seconds ago
-
RE: help sizing rads based on room by room heat loss
By JamesPa , 34 minutes ago
-
Hi Thanks for the reply, the walls are being constru...
By Fingers , 2 hours ago
-
RE: Agile: average import cost vs other tariffs?
@old_scientist I have been imitating a hawk towards the...
By Toodles , 2 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15 I'm no plumber so please don't take this as ...
By dnagre , 3 hours ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 7 hours ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 7 hours ago
-
The Rise and Fall of Europe’s Most Generous Green Subsidy
This story came to my attention thanks to Graham Hendra...
By Mars , 7 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 7 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
From the Full SAP Report: Space heating requirements:...
By trebor12345 , 7 hours ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 12 hours ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Good point. I’ll keep my eye on the manifold temperatur...
By Tomdad , 14 hours ago
-
RE: How hard and expensive would it be to change panel and add battery?
@transparent It is a setting that Octopus make via the ...
By Toodles , 15 hours ago
-
RE: Performance of Heat Pumps in Mild Weather
@heatgeek The flow rate isnt controlled by Mitsub...
By RobS , 17 hours ago
-
RE: Say hello and introduce yourself
I might put a couple of speakers in the ceiling if fund...
By Fingers , 1 day ago
-
RE: Bathroom Radiator replacement
@rob-nezard can you please offer your professional advi...
By Mars , 1 day ago
-
-
RE: Questions on my Hitachi Yutaki SCombi Heat Pump
OK, thats good and low. With low flow temperatures lik...
By JamesPa , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa “They are all equal but, some are more equal t...
By Toodles , 2 days ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
@cliffhanger Mine has a 'space heating off' setting! O...
By JamesPa , 2 days ago