Ecodan 11.2 KW Flow Rate
Hi,
I recently had a Mitsubishi Ecodan 11.2 kW ASHP installed and I have a concern regarding the flow rate.
In the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Most of the plumbing to the outdoor unit is 28 mm so I'm surprised it's low. I was wondering if someone who has one of these units can have a look at their flow rate and pump speed settings as a comparison?
Thanks.
Posted by: @elabHi,
I recently had a Mitsubishi Ecodan 11.2 kW ASHP installed and I have a concern regarding the flow rate.
In the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Most of the plumbing to the outdoor unit is 28 mm so I'm surprised it's low. I was wondering if someone who has one of these units can have a look at their flow rate and pump speed settings as a comparison?
Thanks.
The FTC6 manual suggests 14-32 l/min as the acceptable range so 32 would be right at the upper end. My 14kW Ecodan is running at about 24l/min, also well within the acceptable range. The most I have seen it output is 12-13kW so I'm fairly happy and so was the engineer who serviced it. My delta T probably averages nearer 4 than 5.
I would guess your ASHP will never need to deliver 11.2kW constantly in a steady state. It'll do it in bursts when heating the house up, defrosting, heating DHW, etc.
How is the ASHP working otherwise?
Posted by: @elabIn the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Hi @elab
How are you getting on with getting your flow rate sorted? Do you still need help targeting a DeltaT of 5?
in your post I can’t see what your current temperature difference (DeltaT) is.
If you are trying to increase your DeltaT then the flow rate needs to be reduced to allow the heat to transfer to the circulating water. So it also follows that if you are trying to reduce your DeltaT then the flow rate needs to be increased, therefore spreading the heat transfer to a larger volume of water, at a slightly lower temperature.
As @kev-m states, each size heat pump has a different designed flow rate range. In your case the 11.2 kw ecodan has a stated flow range between 14 lpm and 32 lpm.
you can check your current flow rate on your main controller screen.
hope this helps.
Posted by: @sunandairPosted by: @elabIn the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Hi @elab
How are you getting on with getting your flow rate sorted? Do you still need help targeting a DeltaT of 5?
in your post I can’t see what your current temperature difference (DeltaT) is.
If you are trying to increase your DeltaT then the flow rate needs to be reduced to allow the heat to transfer to the circulating water. So it also follows that if you are trying to reduce your DeltaT then the flow rate needs to be increased, therefore spreading the heat transfer to a larger volume of water, at a slightly lower temperature.
As @kev-m states, each size heat pump has a different designed flow rate range. In your case the 11.2 kw ecodan has a stated flow range between 14 lpm and 32 lpm.
you can check your current flow rate on your main controller screen.
hope this helps.
@sunandair, @elab hasn't been seen on the forum since 1st May so I don't think s/he is worthy of any more attention!
- 26 Forums
- 2,255 Topics
- 50.3 K Posts
- 194 Online
- 5,918 Members
Join Us!
Podcast Picks
Latest Posts
- 
                        
- 
                          RE: Mediation with RECC, what's your experience? Welcome to the forums @treewizard and sorry to hear abo... By Mars , 21 minutes ago 
- 
                        RE: Help me keep the faith with my air source heat pump installation @jamespa ive had a look at the firmware card in the add... By AdamK , 25 minutes ago 
- 
                          RE: New build installation query That accounts for why you start with an overly-high DHW... By Transparent , 37 minutes ago 
- 
                        UFH downstairs and radiators upstairs balancing question I am running pure WC on .4 curve in our new build with ... By Walnut-tree-cottage , 1 hour ago 
- 
                        RE: Daikin Altherma 3 / HomeAssistant I would have thought that (instantaneous) power is a fa... By JamesPa , 2 hours ago 
- 
                          RE: Buying large amp bidirectional RCD and RCBO It's the requirement to have 100mA earth-leakage trippi... By Transparent , 3 hours ago 
- 
                        RE: Are We Sleepwalking Into Another Race to the Bottom? Alright, I concede that the Toyotas are, as you say a v... By JamesPa , 4 hours ago 
- 
                        When to use Octopus Intelligent Go tariff with my heat pump and battery I have underfloor heating with 15 room thermostats thro... By ChrisH , 4 hours ago 
- 
                        RE: Midea ASHP – how to set weather compensation @cathoderay comments duly noted. I don't disagree with ... By pash44pump , 7 hours ago 
- 
                        RE: When will fusion be producing energy? From the time I was a physics undergraduate it’s been 2... By Judith , 16 hours ago 
- 
                        RE: Is it mad to think there should be a minimum SCOP for UK heat pump installs? Sadly I think it is mad. If the BUS is not granted for ... By Judith , 16 hours ago 
- 
                          RE: Who has a V2G EV installation Perfect, @agentgeorge. I’m always up for some edificati... By Majordennisbloodnok , 16 hours ago 
- 
                        RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus Yes but... The evidence is that many heat loss survey... By JamesPa , 17 hours ago 
- 
                          What Adam Chapman gets up to in his Spare Time. Ok, so this just appeared on YouTube (don’t blame me th... By Toodles , 17 hours ago 
- 
                          RE: Radiator Sizing Dilemma: Vertical vs Type 33 for Low-Temperature Heat Pump Systems That's my main concern too. On top of that, I ... By DREI , 19 hours ago 
- 
                        RE: Grant 13kW Aerona3 - issues getting zones to temp Thanks, patience is something I’m trying to ma... By Crimson , 21 hours ago 
- 
                        RE: Solar Power Output – Let’s Compare Generation Figures 2025 - now a record year of Solar PV Generation. Octobe... By AllyFish , 1 day ago 
- 
                        RE: Mitsubishi Ecodan R290 10kW performance Totally agree that any system is reliant on the ability... By Sheriff Fatman , 1 day ago 



 
                                 
                                 
                                 
                                 
                                