Ecodan 11.2 KW Flow Rate
Hi,
I recently had a Mitsubishi Ecodan 11.2 kW ASHP installed and I have a concern regarding the flow rate.
In the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Most of the plumbing to the outdoor unit is 28 mm so I'm surprised it's low. I was wondering if someone who has one of these units can have a look at their flow rate and pump speed settings as a comparison?
Thanks.
Posted by: @elabHi,
I recently had a Mitsubishi Ecodan 11.2 kW ASHP installed and I have a concern regarding the flow rate.
In the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Most of the plumbing to the outdoor unit is 28 mm so I'm surprised it's low. I was wondering if someone who has one of these units can have a look at their flow rate and pump speed settings as a comparison?
Thanks.
The FTC6 manual suggests 14-32 l/min as the acceptable range so 32 would be right at the upper end. My 14kW Ecodan is running at about 24l/min, also well within the acceptable range. The most I have seen it output is 12-13kW so I'm fairly happy and so was the engineer who serviced it. My delta T probably averages nearer 4 than 5.
I would guess your ASHP will never need to deliver 11.2kW constantly in a steady state. It'll do it in bursts when heating the house up, defrosting, heating DHW, etc.
How is the ASHP working otherwise?
Posted by: @elabIn the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Hi @elab
How are you getting on with getting your flow rate sorted? Do you still need help targeting a DeltaT of 5?
in your post I can’t see what your current temperature difference (DeltaT) is.
If you are trying to increase your DeltaT then the flow rate needs to be reduced to allow the heat to transfer to the circulating water. So it also follows that if you are trying to reduce your DeltaT then the flow rate needs to be increased, therefore spreading the heat transfer to a larger volume of water, at a slightly lower temperature.
As @kev-m states, each size heat pump has a different designed flow rate range. In your case the 11.2 kw ecodan has a stated flow range between 14 lpm and 32 lpm.
you can check your current flow rate on your main controller screen.
hope this helps.
Posted by: @sunandairPosted by: @elabIn the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Hi @elab
How are you getting on with getting your flow rate sorted? Do you still need help targeting a DeltaT of 5?
in your post I can’t see what your current temperature difference (DeltaT) is.
If you are trying to increase your DeltaT then the flow rate needs to be reduced to allow the heat to transfer to the circulating water. So it also follows that if you are trying to reduce your DeltaT then the flow rate needs to be increased, therefore spreading the heat transfer to a larger volume of water, at a slightly lower temperature.
As @kev-m states, each size heat pump has a different designed flow rate range. In your case the 11.2 kw ecodan has a stated flow range between 14 lpm and 32 lpm.
you can check your current flow rate on your main controller screen.
hope this helps.
@sunandair, @elab hasn't been seen on the forum since 1st May so I don't think s/he is worthy of any more attention!
- 26 Forums
- 2,318 Topics
- 52 K Posts
- 440 Online
- 5,978 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Battery with existing PV - regulations
@batpred The EPS output can be tricky to do to current ...
By swwils , 39 minutes ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
A2A is really good. Simple. Cheap. Great success in oth...
By swwils , 44 minutes ago
-
RE: Which 6kw to 8kw ASHP can modulate down the lowest ?
That’s one for the installers. @patrickvito @damon @ave...
By Mars , 44 minutes ago
-
RE: 10kw heat pump run in 24*7 data?
Good little test tonight and tomorrow morning weather s...
By jeegnesh , 1 hour ago
-
RE: Replacing my 18 month old ASHP
@trebor12345, asked me to post this video for him which...
By Mars , 2 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@jamespa/p> Run starts at 11. It didn't do a defros...
By swwils , 4 hours ago
-
-
@sune would these work in a horizontal rather than a ve...
By Grantmethestrength , 6 hours ago
-
I had very helpful advice from several forum members ba...
By Steam Powered , 7 hours ago
-
RE: Battery storage to run Heat Pump.
That comment is welcome, but can be read in two differe...
By Transparent , 8 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Oh the installed needs to go somewhere, that's...
By Crimson , 8 hours ago
-
RE: Who's your electricity provider and what's your tariff?
I can confirm a trend with EOn ... From compliance/ethi...
By Batpred , 12 hours ago
-
Given the underspent for the budget of the Solis invert...
By Batpred , 12 hours ago
-
ASHP Model: Daikin Altherma 3M 4KW House loss: Calcul...
By RadWhisperer , 14 hours ago
-
RE: Grant Aerona: Is there a setting to keep the 2-port valve open during pump blockade
Not unless either you allow the AI to turn on cooling w...
By JamesPa , 15 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
If you mean with Home Assistant, I have got a Solis mod...
By Batpred , 23 hours ago
-
RE: Renewables & Heat Pumps in the News
Sorry I did write a reply to @jeff the other day and th...
By Lucia , 1 day ago
-
RE: Electricity price predictions
I expect to be addressing a meeting of residents living...
By Transparent , 1 day ago