Hi,
I recently had a Mitsubishi Ecodan 11.2 kW ASHP installed and I have a concern regarding the flow rate.
In the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Most of the plumbing to the outdoor unit is 28 mm so I'm surprised it's low. I was wondering if someone who has one of these units can have a look at their flow rate and pump speed settings as a comparison?
Thanks.
Posted by: @elabHi,
I recently had a Mitsubishi Ecodan 11.2 kW ASHP installed and I have a concern regarding the flow rate.
In the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Most of the plumbing to the outdoor unit is 28 mm so I'm surprised it's low. I was wondering if someone who has one of these units can have a look at their flow rate and pump speed settings as a comparison?
Thanks.
The FTC6 manual suggests 14-32 l/min as the acceptable range so 32 would be right at the upper end. My 14kW Ecodan is running at about 24l/min, also well within the acceptable range. The most I have seen it output is 12-13kW so I'm fairly happy and so was the engineer who serviced it. My delta T probably averages nearer 4 than 5.
I would guess your ASHP will never need to deliver 11.2kW constantly in a steady state. It'll do it in bursts when heating the house up, defrosting, heating DHW, etc.
How is the ASHP working otherwise?
Posted by: @elabIn the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Hi @elab
How are you getting on with getting your flow rate sorted? Do you still need help targeting a DeltaT of 5?
in your post I can’t see what your current temperature difference (DeltaT) is.
If you are trying to increase your DeltaT then the flow rate needs to be reduced to allow the heat to transfer to the circulating water. So it also follows that if you are trying to reduce your DeltaT then the flow rate needs to be increased, therefore spreading the heat transfer to a larger volume of water, at a slightly lower temperature.
As @kev-m states, each size heat pump has a different designed flow rate range. In your case the 11.2 kw ecodan has a stated flow range between 14 lpm and 32 lpm.
you can check your current flow rate on your main controller screen.
hope this helps.
Posted by: @sunandairPosted by: @elabIn the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Hi @elab
How are you getting on with getting your flow rate sorted? Do you still need help targeting a DeltaT of 5?
in your post I can’t see what your current temperature difference (DeltaT) is.
If you are trying to increase your DeltaT then the flow rate needs to be reduced to allow the heat to transfer to the circulating water. So it also follows that if you are trying to reduce your DeltaT then the flow rate needs to be increased, therefore spreading the heat transfer to a larger volume of water, at a slightly lower temperature.
As @kev-m states, each size heat pump has a different designed flow rate range. In your case the 11.2 kw ecodan has a stated flow range between 14 lpm and 32 lpm.
you can check your current flow rate on your main controller screen.
hope this helps.
@sunandair, @elab hasn't been seen on the forum since 1st May so I don't think s/he is worthy of any more attention!
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 58 Online
- 2,277 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 2 hours ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 2 hours ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami I think if the heat loss documentation matches a ...
By bontwoody , 3 hours ago
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa I'm afraid that's over my head but if anyon...
By IRMartini , 3 hours ago
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 3 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 3 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 5 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 7 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 9 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 21 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 24 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 9 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 10 hours ago
-
SolarPV tables / online calculator
By MichelleC 17 hours ago
-
By Toodles 2 days ago