Ecodan 11.2 KW Flow Rate
Hi,
I recently had a Mitsubishi Ecodan 11.2 kW ASHP installed and I have a concern regarding the flow rate.
In the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Most of the plumbing to the outdoor unit is 28 mm so I'm surprised it's low. I was wondering if someone who has one of these units can have a look at their flow rate and pump speed settings as a comparison?
Thanks.
Posted by: @elabHi,
I recently had a Mitsubishi Ecodan 11.2 kW ASHP installed and I have a concern regarding the flow rate.
In the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Most of the plumbing to the outdoor unit is 28 mm so I'm surprised it's low. I was wondering if someone who has one of these units can have a look at their flow rate and pump speed settings as a comparison?
Thanks.
The FTC6 manual suggests 14-32 l/min as the acceptable range so 32 would be right at the upper end. My 14kW Ecodan is running at about 24l/min, also well within the acceptable range. The most I have seen it output is 12-13kW so I'm fairly happy and so was the engineer who serviced it. My delta T probably averages nearer 4 than 5.
I would guess your ASHP will never need to deliver 11.2kW constantly in a steady state. It'll do it in bursts when heating the house up, defrosting, heating DHW, etc.
How is the ASHP working otherwise?
Posted by: @elabIn the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Hi @elab
How are you getting on with getting your flow rate sorted? Do you still need help targeting a DeltaT of 5?
in your post I can’t see what your current temperature difference (DeltaT) is.
If you are trying to increase your DeltaT then the flow rate needs to be reduced to allow the heat to transfer to the circulating water. So it also follows that if you are trying to reduce your DeltaT then the flow rate needs to be increased, therefore spreading the heat transfer to a larger volume of water, at a slightly lower temperature.
As @kev-m states, each size heat pump has a different designed flow rate range. In your case the 11.2 kw ecodan has a stated flow range between 14 lpm and 32 lpm.
you can check your current flow rate on your main controller screen.
hope this helps.
Posted by: @sunandairPosted by: @elabIn the "Commissioning Wizard" it's showing as 20 l/min with the pump speed setting at 3. I changed this to 5 and it's gone up to 24 l/min
My understanding is that the Ecodan targets a delta t of 5 degrees so I need a flow rate of about 32 l/min to get the full output power.
Hi @elab
How are you getting on with getting your flow rate sorted? Do you still need help targeting a DeltaT of 5?
in your post I can’t see what your current temperature difference (DeltaT) is.
If you are trying to increase your DeltaT then the flow rate needs to be reduced to allow the heat to transfer to the circulating water. So it also follows that if you are trying to reduce your DeltaT then the flow rate needs to be increased, therefore spreading the heat transfer to a larger volume of water, at a slightly lower temperature.
As @kev-m states, each size heat pump has a different designed flow rate range. In your case the 11.2 kw ecodan has a stated flow range between 14 lpm and 32 lpm.
you can check your current flow rate on your main controller screen.
hope this helps.
@sunandair, @elab hasn't been seen on the forum since 1st May so I don't think s/he is worthy of any more attention!
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 428 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
@painter26 — they (the analogue gauges) are subtly diff...
By cathodeRay , 20 minutes ago
-
I cannot see the complete rcbo, since the photo is cut....
By Batpred , 33 minutes ago
-
RE: What determines the SOC of a battery?
The answer from Fogstar was crisp. My hypothesis, su...
By Batpred , 43 minutes ago
-
RE: Electricity price predictions
I am always impressed with how you keep abreast of so m...
By Batpred , 52 minutes ago
-
RE: Setback savings - fact or fiction?
I fully understand your reasoning, same steady inputs s...
By cathodeRay , 1 hour ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
@majordennisbloodnok I’m glad I posted this. There see...
By AndrewJ , 1 hour ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@tasos and @cathoderay thanks. I have some history grap...
By benson , 3 hours ago
-
Our Experience installing a heat pump into a Grade 2 Listed stone house
First want to thank everybody who has contributed to th...
By Travellingwave , 4 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 7 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 7 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 8 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 23 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 1 day ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 1 day ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago