Ecodan Legionella cycle - immersion heater problem

25 Posts
3 Users
4 Reactions
456 Views
(@clockworks)
Estimable Member Member
268 kWhs
Joined: 2 months ago
Posts: 54
Topic starter  

I've had my 6kW Ecodan and (non-Mitsubishi) cylinder for 6 weeks.

I noticed that the Legionella cycle wasn't raising the tank temperature as high as it should have, so I fitted a Shelly EM clamp current monitor to the immersion supply cable from the consumer unit.

This is set up in Home Assistant,  along with monitors for the ASHP supply and some Shelly temperature sensors, so that I can get graphs of what's actually happening.

The DHW is set to come on at midnight, target temp 49 degrees.

The Legionella cycle is set to every 15 days, starting at 01:00, max duration 2 hours, and 10 minutes holding at max temperature.

The Legionella cycle ran last night, and the temperature only got to 54 degrees

 

Screenshot 20250126 072622 Home Assistant
Screenshot 20250126 072329 Home Assistant
Screenshot 20250126 072226 Home Assistant

 

First graph is the heat pump power consumption, second is the tank temperature (from the Ecodan tank sensor), third is the immersion power consumption.

 

Everything looks right - heat pump heats the tank water as normal, then runs for the first part of the Legionella cycle, and goes to idle when the immersion takes over.

Immersion runs normally for about 20 minutes, then starts switching on and off.

Legionella heating cycle ends on schedule, and a few minutes later the heat pump comes back on for heating.

Tank never got above 54 degrees.

Dodgy immersion, or the Mitsubishi controller playing up?

I took the cover off the immersion 2 weeks ago, and it looks like the thermostat is set for 65 degrees.

This topic was modified 1 month ago by Mars

   
Quote
Toodles
(@toodles)
Famed Member Contributor
11253 kWhs
Veteran
Joined: 2 years ago
Posts: 1818
 

Possibly a dodgy immersion heater thermostat? An immersion heater element would normally run (the 3 kW power level is right) until it reaches the set temperature then cutout; looks as though your thermostat needs attention (or replacement?). Toodles.

Toodles, he heats his home with cold draughts and cooks his food with magnets.


   
ReplyQuote
(@clockworks)
Estimable Member Member
268 kWhs
Joined: 2 months ago
Posts: 54
Topic starter  

I've had a closer look at the immersion heater. It seems that this model (Thermowatt RTS 3 ERP) is available in 3 different versions. I managed to find the proper instructions, and the different models gave different colour adjustment knobs, deniting different temperature ranges. Mine has a yellow knob, and is only adjustable between 52 and 60 degrees!

 

I've turned it up to full whack, and set the Legionella cycle to start at 11:00....


   
ReplyQuote



Toodles
(@toodles)
Famed Member Contributor
11253 kWhs
Veteran
Joined: 2 years ago
Posts: 1818
 

@clockworks Sounds like you may have your answer there then! Regards, Toodles.

Toodles, he heats his home with cold draughts and cooks his food with magnets.


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
12942 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 2276
 

Hi Clockworks. Have a look at this existing discussion about  Ecodan - Legionella Operation Time and Target Temperature.

Not only is there heaps of technical detail, but that topic was the second occasion on which members here suggested that the Mitsubishi software is flawed in respect of the anti-legionella target temperature.

Posted by: @clockworks

Immersion runs normally for about 20 minutes, then starts switching on and off.

Good observation. That doesn't sound right.

 

@editor -- can we move this discussion to the end of that other topic please?

Save energy... recycle electrons!


   
ReplyQuote
(@clockworks)
Estimable Member Member
268 kWhs
Joined: 2 months ago
Posts: 54
Topic starter  

Reading the thread linked to, very similar setup to mine.

To me, it seems like the installers have made an error by fitting an immersion that will cut off at 60 degrees, and then setting the heatpump controller to run the legionella cycle for 2 hours with a target temp of 60 degrees (as measured by a pocket sensor in the cylinder).

Chances are, the sensor will never actually read 60 degrees, so the cycle will just run for 2+ hours with the immersion cycling every few minutes. During all this time, the heatpump will be in "standby" doing nothing, and the house will cool down.

They should really be fitting immersion thermostats that enable running at above the maximum legionella setting of the heatpump controller. That way, the controller would actually be in control, not waiting for an event that will never happen, and then timing out.

 

Assuming I'm correct, the answer in my case will be to set the Mitsubishi's Legionella temperature to 58 degrees for now. It should then actually reach 58 degrees, hold for 10 minutes, and revert to heating mode.

 

I'll raise my concerns with installer.


   
ReplyQuote
(@clockworks)
Estimable Member Member
268 kWhs
Joined: 2 months ago
Posts: 54
Topic starter  

Seems like I can't force it to run a Legionella cycle, and setting it to run at 11:00 daily didn't work, presumably because it knew it had already run a cycle overnight?

I have set it back to the usual time of 01:00, but daily, so I'll see what happens tonight.

 

I've also realised that I can't set a temperature lower than 60 degrees!

 

I'll contact the installer, try and get them to fit an immersion heater that will operate at over 60 degrees.


   
👍
1
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
12942 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 2276
 

Posted by: @clockworks

Assuming I'm correct, the answer in my case will be to set the Mitsubishi's Legionella temperature to 58 degrees for now. It should then actually reach 58 degrees, hold for 10 minutes, and revert to heating mode.

Yes. You've got it.

And you should definitely throw the problem back at the installers.
You musn't have the thermostat in the immersion heater and the heat-pump control fighting each other around 60°C

 

As for your 'workaround':-

A. I doubt the Mitsubishi software is that accurate.
You may need to drop lower than 58°C before you see any difference.

B. Others have reported that the Mitsubishi code itself is flawed.
Be prepared for the system still not working.

C. I also understand the biology of bacterial growth.
If you drop the temperature then you need to elongate the time at which the peak is being held.

 

And, on another issue, would you mind moving your anti-legionella cycle start-time away from it coinciding with a half-hour interval?

That's when there are surge-demands on the electricity grid because tariffs get changed at half-hourly intervals in UK.

It's 'grid-friendly' if you choose a more random time, such as 01:17

Save energy... recycle electrons!


   
ReplyQuote
(@clockworks)
Estimable Member Member
268 kWhs
Joined: 2 months ago
Posts: 54
Topic starter  

The Mitsubishi controller only allows for setting the Legionella cycle start time in hourly increments.

All the other timers/schedules are adjustable in shorter increments.

 

The immersion thermostat is available as a "blue knob" version, which is adjustable between 63 and 71 degrees. That's the one they should have fitted.

 


   
ReplyQuote



Toodles
(@toodles)
Famed Member Contributor
11253 kWhs
Veteran
Joined: 2 years ago
Posts: 1818
 

@clockworks It rather sounds as though the heat pump manufacturers (or rather their software programmers) are not taking on board the need to lessen surges on the grid yet😒 Toodles

This post was modified 1 month ago by Toodles

Toodles, he heats his home with cold draughts and cooks his food with magnets.


   
ReplyQuote
Transparent
(@transparent)
Illustrious Member Moderator
12942 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 2276
 

Posted by: @toodles

Posted by: @clockworks

The Mitsubishi controller only allows for setting the Legionella cycle start time in hourly increments.

It rather sounds as though the heat pump manufacturers [...] are not taking on board the need to lessen surges on the grid yet

I'll raise that with the DESNZ committee who are creating the 'Standard' for Demand Side Response de-coupling of heat-pumps from the grid.

There are representatives of the ENA who are members,
and they have an interest in the avoidance of demand surges.

Save energy... recycle electrons!


   
ReplyQuote
(@clockworks)
Estimable Member Member
268 kWhs
Joined: 2 months ago
Posts: 54
Topic starter  

To be fair, the total demand for the period was a maximum of 3kW - the ASHP goes idle while the immersion is running.

In contrast, my electric car's demand was 7.4 kW, but the charger is controlled by the energy supplier (Octopus). They tell the charger when to run, and can also knock the max current back if needed.

I was given a charging slot of 05:00 to 07:30, so I got an extra 2 hours at 7p for the whole house.

 

I think I read somewhere that Octopus will be able to do similar demand matching with their "Cosy" range of heatpumps?

It might be a good idea if some "randomisation" of schedules and timers was standard on electric heating systems though - just 5 minutes either side could make a difference in surges, and be transparent to the consumer.


   
ReplyQuote
Page 1 / 3



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security