Hello. Beginner's question:
I have a system with a ASHP and a hot water tank.
When the legionella cycle (Friday 1pm for 1 hour) kicks in my radiators also heat up. Is this supposed to happen?
I am suspecting the valve that controls where the hot water from the pump goes (diverting to DHW or Heating) is not working well, and DHW is leaking to the radiators.
Welcome to the forums @bbmorales
No, that shouldn’t be happening. It sounds like you’re on the right track with your diagnosis though. During the legionella cycle, only your hot water tank should be heating up, not the radiators. This suggests that the diverter valve may be faulty and allowing hot water to flow into the heating circuit. A photo of the diverter valve would be helpful.
The other question this poses is that I assume your heating is off at the moment and you’re only using your heat pump for hot water production. So why is your system coming on at all and distributing heat to your rads. Does your circulation pump come on when the legionella cycles starts?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk
Hi @editor Mars, many thanks.
Regarding the images, I've uploaded two, hopefully this gives you an idea of the system.
Regarding your other question
"Does your circulation pump come on when the legionella cycles starts? "
Apologies for the question, but where is this pump and how to I verify this?
I have not disabled completely the heating, but I can try doing so next Friday (disable completely the heating, leaving on only DHW).
Thanks for your help!
@bbmorales let's backtrack a little bit. Can you please share more information about the system you have (brand and model of heat pump would be a good starting point)? We'll need to ascertain whether your heating is in fact off.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk
There is no need, imo, to run a legionella cycle as often and it would be better run during the night on cheaper rate electricity. The ASHP heats to 50c and the immersion takes over to 60c. Expensive on day time rate on a weekly basis. Needn’t be for as long as an hour either so far as I know.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
Faulty 3 port diverter….
Easiest fix is to disable the legionella program.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@bbmorales it's a personal preference and depends on the likelihood of bacteria proliferating in your tank. We run a Legionella cycle every two weeks. Since we work from home and use hot water frequently, the water in our cylinder is constantly being drained and replaced, preventing stagnation. This routine works for us. However, some homeowners choose to turn it off completely.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk
- 25 Forums
- 1,513 Topics
- 31.8 K Posts
- 22 Online
- 1,283 Members
Join Us!
Latest Posts
-
RE: Additional Battery v Wind Turbine v Ripple
I should add, being an investment, the value of your in...
By Old_Scientist , 5 hours ago
-
RE: Ecodan - flow rates, sensors, settings
Achieving an accurate flow measurement is probably the ...
By Derek M , 8 hours ago
-
RE: Ecodan ASHP - How to optimise my set up?
Again, thank you for another thorough post, @derek-m - ...
By rhh2348 , 10 hours ago
-
RE: Delivering a smart and secure electricity system: government consultation
@Transparent.Now that I am represented by a new MP I th...
By IanMK13 , 12 hours ago
-
RE: Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
Similar thread here
By Johnmo , 13 hours ago
-
RE: VDI 2035 heating water specification
Been looking and it seems a good little project. Ever...
By Johnmo , 2 days ago
-
RE: Do I accept an ASHP and Solar Panel retrofit under the HUG 2 scheme?
Will do. I'm currently waiting for another survey / vis...
By dssr , 2 days ago
-
The company that did the borehole were expecting us to ...
By Johnmo , 2 days ago
-
-
RE: The Misquote That Ruined the Heating Industry
@abernyte manufacturer training is pretty average. They...
By Mars , 2 days ago
-
-
RE: ECO4 Scheme and EPC ratings
@mellow Thanks. Given there is a scheme requirement to ...
By Old_Scientist , 3 days ago
-
RE: Do I just go with the lowest quote for my heat pump?
@jancold To me its a no-brainer then, a max 40C flow te...
By bontwoody , 3 days ago
-
-
RE: Heat Pump Books Beginners – Bodge Buster & From Zero To Heat Pump Hero
@editor Presumably he had some good weather Compensatio...
By Toodles , 4 days ago
-
RE: New Vaillant 7kW aroTherm ASHP or oil boiler dilemma/decision??
Storage capacity really is dependent on storage tempera...
By Johnmo , 4 days ago
-
RE: HP Cycling, Expected or Undesirable
Just a little update. I ordered a longer shielded twin ...
By bontwoody , 4 days ago
-
RE: Domestic hot water timer doing crazy things on my Grant Aerona3 10kW air source heat pump
Thanks @allyfish for the pics and info. Spoke to the in...
By Mellow , 4 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
It's been a busy day for calls and emails from Aira. I ...
By MikeH , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Hmm. A bit of a nuanced answer, methinks. As I've alr...
By Majordennisbloodnok , 5 days ago
Latest Topics
-
Ecodan - flow rates, sensors, settings
By rhh2348 11 hours ago
-
Replacing mains water with well water
By Johnmo 2 days ago
-
Additional Battery v Wind Turbine v Ripple
By bontwoody 2 days ago
-
By jamespipe 3 days ago
-
VDI 2035 heating water specification
By Johnmo 3 days ago
-
Do I just go with the lowest quote for my heat pump?
By Jancold 5 days ago
-
The Misquote That Ruined the Heating Industry
By Alec Morrow 6 days ago
-
Battery Storage Wiring Gauge Question
By Puff 6 days ago
Members Online
No online members at the moment