Does legionella cycle also heats up radiators?
Hello. Beginner's question:
I have a system with a ASHP and a hot water tank.
When the legionella cycle (Friday 1pm for 1 hour) kicks in my radiators also heat up. Is this supposed to happen?
I am suspecting the valve that controls where the hot water from the pump goes (diverting to DHW or Heating) is not working well, and DHW is leaking to the radiators.
Welcome to the forums @bbmorales
No, that shouldn’t be happening. It sounds like you’re on the right track with your diagnosis though. During the legionella cycle, only your hot water tank should be heating up, not the radiators. This suggests that the diverter valve may be faulty and allowing hot water to flow into the heating circuit. A photo of the diverter valve would be helpful.
The other question this poses is that I assume your heating is off at the moment and you’re only using your heat pump for hot water production. So why is your system coming on at all and distributing heat to your rads. Does your circulation pump come on when the legionella cycles starts?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Hi @editor Mars, many thanks.
Regarding the images, I've uploaded two, hopefully this gives you an idea of the system.
Regarding your other question
"Does your circulation pump come on when the legionella cycles starts? "
Apologies for the question, but where is this pump and how to I verify this?
I have not disabled completely the heating, but I can try doing so next Friday (disable completely the heating, leaving on only DHW).
Thanks for your help!
@bbmorales let's backtrack a little bit. Can you please share more information about the system you have (brand and model of heat pump would be a good starting point)? We'll need to ascertain whether your heating is in fact off.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
There is no need, imo, to run a legionella cycle as often and it would be better run during the night on cheaper rate electricity. The ASHP heats to 50c and the immersion takes over to 60c. Expensive on day time rate on a weekly basis. Needn’t be for as long as an hour either so far as I know.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Faulty 3 port diverter….
Easiest fix is to disable the legionella program.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@bbmorales it's a personal preference and depends on the likelihood of bacteria proliferating in your tank. We run a Legionella cycle every two weeks. Since we work from home and use hot water frequently, the water in our cylinder is constantly being drained and replaced, preventing stagnation. This routine works for us. However, some homeowners choose to turn it off completely.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
- 26 Forums
- 2,152 Topics
- 47.2 K Posts
- 36 Online
- 5,671 Members
Podcast Picks
Latest Posts
-
RE: What crazy nonsense are inverter limits and why are they imposed?
@old_scientist Thanks for the reply. For some inexplica...
By HowardP99 , 2 minutes ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump Since you will inevitably have to deal with...
By Tasos , 20 minutes ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 4 hours ago
-
RE: Octopus tariffs - a quick comparison
@scalextrix yes, battery is vital to maximise TOU tarif...
By Tim441 , 4 hours ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 4 hours ago
-
@mars That response surely deserves a nomination for Tu...
By JamesPa , 17 hours ago
-
Specifying batteries, pv solar etc using ChatGPT
I thought I'd try to use ChatGPT to specify my requirem...
By Tim441 , 19 hours ago
-
RE: Ecodan & MelCloud scheduling
When I interviewed Mitsubishi Electric at Installer ear...
By Mars , 23 hours ago
-
RE: Rodents! A word of warning for heat pump owners
@lucia One look at that protection and the rodents will...
By Toodles , 24 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
🙁🙁🙁🙁🙁
By Lucia , 1 day ago
-
What is the Heat Geek Guarantee?
We regularly hear from homeowners who are researching i...
By Mars , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk, interesting point. I’ve not focused much on Hea...
By Mars , 1 day ago
-
Intelligent Octopus Flux (IOF) Review
I promised @toodles that I would provide an update and ...
By Old_Scientist , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@julianc Our solar PV has produced more this August tha...
By Toodles , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
I am pleased to see the change. We definitely need t...
By Jeff , 3 days ago
-
RE: How Do I Know When the Hot Water Has Run Out?
@transparent that is a very interesting suggestion, tha...
By GrahamF , 4 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
Sorry to resurrect this thread, but it is sort of relev...
By cathodeRay , 4 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
I missed your 22nd June post on this. I am sure it can ...
By cathodeRay , 4 days ago
-
Now posting on the right topic.... With general build...
By benson , 4 days ago