Does legionella cycle also heats up radiators?
Hello. Beginner's question:
I have a system with a ASHP and a hot water tank.
When the legionella cycle (Friday 1pm for 1 hour) kicks in my radiators also heat up. Is this supposed to happen?
I am suspecting the valve that controls where the hot water from the pump goes (diverting to DHW or Heating) is not working well, and DHW is leaking to the radiators.
Welcome to the forums @bbmorales
No, that shouldn’t be happening. It sounds like you’re on the right track with your diagnosis though. During the legionella cycle, only your hot water tank should be heating up, not the radiators. This suggests that the diverter valve may be faulty and allowing hot water to flow into the heating circuit. A photo of the diverter valve would be helpful.
The other question this poses is that I assume your heating is off at the moment and you’re only using your heat pump for hot water production. So why is your system coming on at all and distributing heat to your rads. Does your circulation pump come on when the legionella cycles starts?
Buy a copy of the The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Hi @editor Mars, many thanks.
Regarding the images, I've uploaded two, hopefully this gives you an idea of the system.
Regarding your other question
"Does your circulation pump come on when the legionella cycles starts? "
Apologies for the question, but where is this pump and how to I verify this?
I have not disabled completely the heating, but I can try doing so next Friday (disable completely the heating, leaving on only DHW).
Thanks for your help!
@bbmorales let's backtrack a little bit. Can you please share more information about the system you have (brand and model of heat pump would be a good starting point)? We'll need to ascertain whether your heating is in fact off.
Buy a copy of the The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
There is no need, imo, to run a legionella cycle as often and it would be better run during the night on cheaper rate electricity. The ASHP heats to 50c and the immersion takes over to 60c. Expensive on day time rate on a weekly basis. Needn’t be for as long as an hour either so far as I know.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Faulty 3 port diverter….
Easiest fix is to disable the legionella program.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@bbmorales it's a personal preference and depends on the likelihood of bacteria proliferating in your tank. We run a Legionella cycle every two weeks. Since we work from home and use hot water frequently, the water in our cylinder is constantly being drained and replaced, preventing stagnation. This routine works for us. However, some homeowners choose to turn it off completely.
Buy a copy of the The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
- 26 Forums
- 2,208 Topics
- 48.7 K Posts
- 89 Online
- 5,868 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Inventor (Midea) Heat Pump short cycling advice
I installed the 80L tank (volumizer) things got better ...
By immunity , 6 minutes ago
-
RE: Mitsubishi Ecodan F8 error
I absolutely love this. This is the quintessential heat...
By Mars , 7 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@papahuhu at the end of the day if you are happy with h...
By benson , 12 hours ago
-
RE: Can you recommend a Mitsubishi service engineer in the Rochdale area?
@dgclimatecontrol We'll all need annual servicing. How...
By Suzy-shadow , 12 hours ago
-
RE: Renewables & Heat Pumps in the News
@transparent I’ve understood your point now. The point ...
By Judith , 13 hours ago
-
RE: Octopus tariffs - a quick comparison
Does indeed need checking, @tim441. Neither Homely ...
By Majordennisbloodnok , 13 hours ago
-
RE: How not to install a heat pump
Delighted to hear that the buffer has been replumbed as...
By JamesPa , 14 hours ago
-
-
RE: Daikin 9kW to 8kW Swap Offer from Octopus
Yes but 9kW is similarly the 16kW derated. So 8kW subs...
By JamesPa , 15 hours ago
-
Actually, there's a rather greater degree of cattle-her...
By Majordennisbloodnok , 16 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@davidnolan22 So far as I can tell from the 'other p...
By JamesPa , 20 hours ago
-
RE: 5 Star Service from Havenwise
I keep getting havenwise ads on my Facebook feed, so cl...
By benson , 22 hours ago
-
Automation options to maximuse efficiency & ToU tariffs
I started a conversation with ChatGPT. What automation...
By Tim441 , 1 day ago
-
RE: 4 Year Ongoing Heat Pump Battle With Poor Heat Pump Installation
@jamespa Oh, I know some that are good and some not so....
By ASHP-BOBBA , 1 day ago
-
RE: Samsung Heat pump with Yonos Pico circulating pump running all the time
I don't know how many pumps you have but I guess it's o...
By JamesPa , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
That's just human nature unfortunately, not special to ...
By JamesPa , 1 day ago
-
@bontwoody how long has it been now since you started t...
By Mars , 2 days ago
-
RE: Bosch CS5800i 5kW - Experience So Far
Yes, over the last few days I've been keeping a very cl...
By Steelbadger , 2 days ago
-
Absolutely. I am one of those members and I most certai...
By Majordennisbloodnok , 2 days ago