Discussion on buffer tanks and heat pumps
Now my install has been plumbed correctly I've turned my attention to the buffer, backup heater and external circulation pump as I believe these are put in purely out of laziness/lack of expertise of the designers, whereas in fact they are making the install and run far more complicated and expensive with these items installed. Get the customers to pay for these extras and pay again in wasted energy using them, so no reason for designers to worry about doing it properly.
There are some key mentions in the Daikin manual which are flags, and just as key there is zero mention of adding an external (CH Circ) pump to the CH system.
the only mention of a field supply pump is here:
My install has a 50 litre buffer, a Grundfos circulation pump and a Backup Heater. So, according to the specs, with a backup heater the minimum volume of water is just 20 litres, that's about 3 radiators panels/ large towel rails. I have the equivalent of 11 doubles, which is 144 litres plus the pipework. So in no circumstance would the install need a buffer tank. That 50 litre buffer represents about 33% of the total volume of the install, so that's 33% lost efficiency, 33% more expense in bills.
Now I have never seen a design for the system, it will be interesting what the handover pack will include.
I have also done some experiments on the CH Circ pump speed.
Turning it off or up to full speed doesn't affect the flow rate displayed on the unit, which must mean the internal pump is pushing water faster than the external Grundfos.
Turning the Grundfos off negatively impacts the CH flow, all the Rads went cold even though the F&R temps on the Daikin were at 37/35. Which means the buffer was acting as a bypass to the heating system without that extra Grundfos inertia
Turning the Grundfos to the slowest speed restored warmth to the Rads and the flow in and out of the buffer was <0.2C (delta).
At the moment my only interest is getting it through RHI. I'm not going to start messing with the layout as I need that MCS certificate but its something I will deal with later. A simple bypass of the buffer or ripping it out completely are my thoughts.
Giving this further thought, the buffer tank should only ever be in circuit as part of an automatic bypass system in case of end user error closing all the Rad valves.
......and in my case limited to a 20l buffer tank
some good analysis there. Have you thought of a change in career?
Seriously though, it isn't right that customers/users end up having to know more about their heating systems that the so-called experts. Imagine if you had to tell your electrician how to rewire your house.
Kev
- 21 Forums
- 1,964 Topics
- 42.6 K Posts
- 24 Online
- 2,278 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami yes. 8kw = 8000w I would change the areas in th...
By bontwoody , 2 hours ago
-
RE: Towel rails. An unexpected final hurdle
I had a similar issue but convinced the installer to le...
By Pie_Eater , 3 hours ago
-
Cliff, welcome to the forum. You’re running into one ...
By Mars , 3 hours ago
-
RE: What is the best strategy for operating a very oversized heat pump?
This whole discussion highlights just how much of a mes...
By Mars , 3 hours ago
-
RE: NIBE F2040 12 kW heat pump and 100 liter buffer tank
@cheshirejohn thanks for the update and for sharing. I’...
By Mars , 3 hours ago
-
RE: Setback savings - fact or fiction?
Here's the same plot, less the R squared values, done q...
By cathodeRay , 6 hours ago
-
RE: SolarPV tables / online calculator
We've only had our solar since last June, but so far fo...
By Old_Scientist , 6 hours ago
-
@robs useful thread! Thanks for sharing - Octopus are c...
By big_si , 6 hours ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 8 hours ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 9 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 10 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 14 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 1 day ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 1 day ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 2 days ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 2 days ago
Latest Topics
-
By cliffhanger 3 hours ago
-
Heat Pump Sizing & Installation Costs
By Mars 16 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 17 hours ago
-
SolarPV tables / online calculator
By MichelleC 24 hours ago