Discussion on buffer tanks and heat pumps
Now my install has been plumbed correctly I've turned my attention to the buffer, backup heater and external circulation pump as I believe these are put in purely out of laziness/lack of expertise of the designers, whereas in fact they are making the install and run far more complicated and expensive with these items installed. Get the customers to pay for these extras and pay again in wasted energy using them, so no reason for designers to worry about doing it properly.
There are some key mentions in the Daikin manual which are flags, and just as key there is zero mention of adding an external (CH Circ) pump to the CH system.
the only mention of a field supply pump is here:
My install has a 50 litre buffer, a Grundfos circulation pump and a Backup Heater. So, according to the specs, with a backup heater the minimum volume of water is just 20 litres, that's about 3 radiators panels/ large towel rails. I have the equivalent of 11 doubles, which is 144 litres plus the pipework. So in no circumstance would the install need a buffer tank. That 50 litre buffer represents about 33% of the total volume of the install, so that's 33% lost efficiency, 33% more expense in bills.
Now I have never seen a design for the system, it will be interesting what the handover pack will include.
I have also done some experiments on the CH Circ pump speed.
Turning it off or up to full speed doesn't affect the flow rate displayed on the unit, which must mean the internal pump is pushing water faster than the external Grundfos.
Turning the Grundfos off negatively impacts the CH flow, all the Rads went cold even though the F&R temps on the Daikin were at 37/35. Which means the buffer was acting as a bypass to the heating system without that extra Grundfos inertia
Turning the Grundfos to the slowest speed restored warmth to the Rads and the flow in and out of the buffer was <0.2C (delta).
At the moment my only interest is getting it through RHI. I'm not going to start messing with the layout as I need that MCS certificate but its something I will deal with later. A simple bypass of the buffer or ripping it out completely are my thoughts.
Giving this further thought, the buffer tank should only ever be in circuit as part of an automatic bypass system in case of end user error closing all the Rad valves.
......and in my case limited to a 20l buffer tank
some good analysis there. Have you thought of a change in career?
Seriously though, it isn't right that customers/users end up having to know more about their heating systems that the so-called experts. Imagine if you had to tell your electrician how to rewire your house.
Kev
- 26 Forums
- 2,372 Topics
- 53.8 K Posts
- 204 Online
- 6,053 Members
Join Us!
Worth Watching
Latest Posts
-
Cascade 2x Grant Areona 10kw ASHP - Ongoing setup issues
I initially posted last winter and thanks to both the i...
By adam , 1 hour ago
-
RE: New Fogstar 15.5kWh upright solution
@batpred Maybe you should buy your additional batter...
By Bash , 1 hour ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Thanks all for the suggestions. Might help if I try a...
By benson , 1 hour ago
-
RE: Forum updates, announcements & issues
@dr_dongle There is no such thing as ‘Too Much Informat...
By Toodles , 2 hours ago
-
Weather compensation- why you should use it
Brief update on weather compensation (AI). I have a LG ...
By Tim441 , 2 hours ago
-
RE: Data Accuracy Problem: Daikin 8kW Heat Pump's Onecta App vs MMI Power Consumption
@nursethescreens Yes, comfort and happiness of the fami...
By Toodles , 2 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 I have just realised that I omitted the Decembe...
By Toodles , 2 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
Thanks folks. I had tried googling an ethernet lab adap...
By z8lccda , 16 hours ago
-
RE: Changing from 4-port buffer to volumizer
@toodles I'm not concerned that the behaviour is not no...
By Andy1618 , 17 hours ago
-
-
RE: Setback savings - fact or fiction?
I agree, and I think there are two things in play here....
By cathodeRay , 21 hours ago
-
RE: Water Hammer After Heat Pump Install
That's really helpful. Yor last sentence confirms it'...
By JamesPa , 1 day ago
-
RE: Help needed with Grant Aerona 3 issues
First time posting so bear with me. Some bits that have...
By Adamp , 2 days ago
-
RE: Mitsu PUHZ-SW120YHA + EHSC-VM20Uk - Performance
All understood. Obviously its a bit house de...
By JamesPa , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@majordennisbloodnok This may be a better thread to ...
By Batpred , 3 days ago
-
RE: Best Heat Pump Brand in the UK
Last Call to Vote & Win! Haven't voted for your Hea...
By Mars , 3 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Interesting question. To be frank, since I have no inte...
By Majordennisbloodnok , 3 days ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@9jwr9 Hi, yes this is the issue with every (stand alon...
By ASHP-BOBBA , 4 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk FWIW I managed unintentionally to 'coax' mine in...
By JamesPa , 4 days ago