Discussion on buffer tanks and heat pumps
Now my install has been plumbed correctly I've turned my attention to the buffer, backup heater and external circulation pump as I believe these are put in purely out of laziness/lack of expertise of the designers, whereas in fact they are making the install and run far more complicated and expensive with these items installed. Get the customers to pay for these extras and pay again in wasted energy using them, so no reason for designers to worry about doing it properly.
There are some key mentions in the Daikin manual which are flags, and just as key there is zero mention of adding an external (CH Circ) pump to the CH system.
the only mention of a field supply pump is here:
My install has a 50 litre buffer, a Grundfos circulation pump and a Backup Heater. So, according to the specs, with a backup heater the minimum volume of water is just 20 litres, that's about 3 radiators panels/ large towel rails. I have the equivalent of 11 doubles, which is 144 litres plus the pipework. So in no circumstance would the install need a buffer tank. That 50 litre buffer represents about 33% of the total volume of the install, so that's 33% lost efficiency, 33% more expense in bills.
Now I have never seen a design for the system, it will be interesting what the handover pack will include.
I have also done some experiments on the CH Circ pump speed.
Turning it off or up to full speed doesn't affect the flow rate displayed on the unit, which must mean the internal pump is pushing water faster than the external Grundfos.
Turning the Grundfos off negatively impacts the CH flow, all the Rads went cold even though the F&R temps on the Daikin were at 37/35. Which means the buffer was acting as a bypass to the heating system without that extra Grundfos inertia
Turning the Grundfos to the slowest speed restored warmth to the Rads and the flow in and out of the buffer was <0.2C (delta).
At the moment my only interest is getting it through RHI. I'm not going to start messing with the layout as I need that MCS certificate but its something I will deal with later. A simple bypass of the buffer or ripping it out completely are my thoughts.
Giving this further thought, the buffer tank should only ever be in circuit as part of an automatic bypass system in case of end user error closing all the Rad valves.
......and in my case limited to a 20l buffer tank
some good analysis there. Have you thought of a change in career?
Seriously though, it isn't right that customers/users end up having to know more about their heating systems that the so-called experts. Imagine if you had to tell your electrician how to rewire your house.
Kev
- 22 Forums
- 2,047 Topics
- 44.6 K Posts
- 17 Online
- 3,274 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Warm weather and heat pumps.
@editor Oh nothing right now because $ needed for struc...
By Lucia , 6 hours ago
-
RE: Yes, the "zoning with ASHP" topic again...
@ccap as an aside, I think you pose some interesting qu...
By Mars , 6 hours ago
-
Maybe you could do a video on it please? Ask all the ma...
By Lucia , 6 hours ago
-
RE: Renewables & Heat Pumps in the News
This is from data provided by a serious researcher with...
By Lucia , 6 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Well, as i was hoping, this month over here just smashe...
By Andris , 6 hours ago
-
@iantelescope - I do appreciate I am becoming something...
By cathodeRay , 8 hours ago
-
RE: Potentially more choice including air to air heat pump grants
@jeff Such documents are far too wordy for my ‘daily re...
By Toodles , 10 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@grahaml I cannot agree that it is a small percentage o...
By benson , 1 day ago
-
RE: Commencing on an ASHP Installation Process
In that case treating it as a separate space seems emin...
By JamesPa , 1 day ago
-
RE: Samsung Gen6 16kW tribulations
@emceed, can you please give us an update on your syste...
By Mars , 2 days ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15 Sorry to hear that, we are all the way down ...
By ASHP-BOBBA , 3 days ago
-
What's the problem you are trying to solve. The answer...
By JamesPa , 4 days ago
-
Good luck. For what it is worth my system was very def...
By JamesPa , 5 days ago
-
RE: Massive Electricity Cost for Running My Air Source Heat Pump
I agree @mark-h The Building Regs are now very readable...
By Transparent , 5 days ago
-
RE: Help me understand my Mitsubishi Ecodan system
@carpenterstation When changing settings in the ser...
By RobS , 5 days ago
-
RE: Ecodan Legionella cycle - immersion heater problem
Thanks for letting us know @clockworks I admire your ...
By Transparent , 6 days ago
-
RE: Revised version of MCS-020 (noise standards for heat pumps)
As you say this is no change, which I personally think ...
By JamesPa , 7 days ago
-
RE: What happens when the outside temperature exceeds the upper WC point?
@editor not via the WC curve but as @old_scientist ment...
By bontwoody , 7 days ago
-
RE: MHHS and Heat Pump compatibility
@toodles to be clear I don't know if there will be a re...
By Scalextrix , 1 week ago