Defrost Cycles - How Common Are They?
@rupes If you could add outside air temp to that chart that may help. In my experience, defrost cycle rate is a combination of outside air temp and humidity and flow temperature/heat demand.
Here is a period where my OAT was around 2 deg, with no defrost cycles. Heat pump is Samsung Gen6 16kW [flow temperature peaks is DHW runs]
Chart #1 - 4 hour period no defrost cycles
Chart #2 - Same heat pump, slightly cooler OAT, a couple of defrost cycles 11 hour period - defrost about once per 90 minutes
Chart #3 - Bit more difficult to get data out quickly further back, but here is some data showing about a 50 min gap between defrosts, this is when OAT was below zero.
Posted by: @mikefl@rupes This is very interesting. I'm trying to wire up my LLH heater atm, but it's a tricky cabling path for both power, and the control switch from the external unit. I want to just "try it" for a while to see the impact, before I see if it's worth the cost of adding a new circuit to my consumer unit.
From what you show, 15:00-19:30 ish is standard defrost (every 40 mins) and you aren't hitting target LWT; then after that the cycles extend to around 1 hour, and you are hitting LWT target. It's whether that improvement is worth the cost of the COP=1 power of the LLH heater.
Can you add external air temp to your graph? Maybe it was just warmer after 19:30? The key temp for a Grant seems to be 3C and lower.
Do you know how much power the LLH is drawing? It's a 3kW element, but the Grant docs suggest it'll only pull 250W in "defrost cycle help" mode. I'm a little sceptical.
I will add another version of that chart with outside temperature later in the week - I'm away from my home assistant server right now so can't access the data unfortunately. The temperature was mostly between 0 and 2deg during that day and did rise slightly into the evening but only to about 3deg and the unit was still defrosting fairly frequently into the night. I would agree with you that the issue is mainly confined to around 3deg outdoor temperature and below.
I'm also a bit sceptical about the 250W figure - for starters, presumably they mean 250Wh rather than 250W. It would also depend on how you set it up - you can define the flow temperature at which the immersion heater will switch off. I set mine at 40degC and looking at the data the defrost cycle results in flow temperature being below that level for about 12 minutes. I'm not sure at what point the immersion heater kicks in but 12 minutes out of every 37 minutes is about 1/3rd of the time so that would equate to about 1kWh of electricity consumption every hour - on a day like last Thursday that would have been quite an uplift on my total electricity consumption. I don't currently have any means to check exactly how much is being used by the immersion.
I did give some further thought to my idea of switching off the central heating circulation pumps during the defrost cycle. With the data I am collecting from the heat pump I have a sensor for "Defrost Temperature". It appears that just before the Defros cycle begins the defrost temperature drops to about -7deg. At the moment the defrost cycle starts the compressor switches off and the heat pump power consumption drops to 100W and stays there for 3 minutes before the defrost process begins. So using the combination of the defrost temperature being below -6deg and the power consumption going to 100W I can trigger an automation which switches my three underfloor heatings zones off for 10 minutes. This immediately switches off the underfloor heating pump an means that the colder water is not being pumped around my underfloor heating circuits. The heating demand remains on from the other zones so the heat pump will go into recovery mode as soon as the defrost is finished. This should provide two benefits - 1. the heated floors are not being actively cooled during the defrost - the water in the UFH pipes should stay warm and continue dissipating heat into the floor. 2. The remaining zones should be able to heat up more quickly as there is a smaller body of water to be heated by the heat pump during it's recovery from the defrost and by the time the UFH switches back on the heat pump is more or less back up to temperature. That's my theory anyway - but I'm probably displaying a complete lack of understanding of the laws of thermodynamics. Now I just need some more cold weather to test it out properly - I did have it running overnight and the trigger was working correctly but I didn't quite have my signals to the ufh heating zones working correctly. I also may need to fine tune the 10 minutes upwards a bit.
Grant Aerona3 13kW
@rupes Thanks for the info. I've seen a defrost temp of -3 and -4 trigger the cycle. It's definitely the 100W consumption figure which shows we're in defrost (or the HP has made the decision to defrost).
Grant Aerona 3 10kW
- 21 Forums
- 1,825 Topics
- 39.4 K Posts
- 53 Online
- 2,141 Members
Join Us!
Latest Posts
-
RE: Grant Aerona3 R32 HPIDI17 performance in low temperatures
@davidmo6 When we had the gas boiler we used to set the...
By Judith , 52 minutes ago
-
RE: Ideal Logic 10kW Heat Pump Pipes Noisy and Very Expensive to Run
@Ajbevster If the OAT is reading 10C high then it might...
By JohnR , 1 hour ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Thanks ! Head banging , haha !
By Alfapat , 10 hours ago
-
RE: Totally bewildered with my ECO4 heat pump installation
ECO4, and the previous iterations, are funded by Energy...
By Lenny , 10 hours ago
-
RE: Vaillant Arotherm ASHP gets noisier when it gets colder outside
At last caught the ashp on its peak after de-icing. Dra...
By Judith , 10 hours ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
Are heat pumps more affordable to run than gas boilers?...
By Mars , 11 hours ago
-
Hi @jamespa There are other modes as you have queri...
By SUNandAIR , 12 hours ago
-
RE: Hybrid ASHP and gas boiler - operating together
I have a home brew hybrid system (didn't want to scrap ...
By Johnmo , 12 hours ago
-
RE: Heat Pump starting current
Hi @transparent, that sounds interesting. I have some c...
By s_gatorator , 15 hours ago
-
RE: 6 Red Flags to Avoid When Considering a Heat Pump Installation
Read your Red Flags with interest. Presently tweaking m...
By Alfapat , 18 hours ago
-
RE: hum/whine from Wilo circulation pump
@Richard24738 Thanks for the clarification. I await you...
By JohnR , 19 hours ago
-
RE: Is My Midea Heat Pump Inherently Defective?
Yes, this and the paragraph it ends is a good descripti...
By cathodeRay , 20 hours ago
-
RE: ASHP for small garage and workshop
Mitsubishi heat pumps works great in low temperatures. ...
By jamespipe , 21 hours ago
-
I have only just realised, thanks to my Planet Device, ...
By Broadsman , 23 hours ago
-
RE: Investment or not Solar/Battery instllation
Hi, no, quite the reverse, the quotation, based on your...
By s_gatorator , 1 day ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
Mike - There are strategies whereby both goals could be...
By Transparent , 2 days ago
-
Another question. Wired Remote Controller internal ther...
By Raiph , 2 days ago
-
RE: Solar thermal with combi boiler
ASHP - air source heat pump PDHW - priory demand hot...
By Johnmo , 2 days ago
-
RE: Nibe S2125 - anybody had experience with this relatively new heat pump?
Apologies to ressurect this old thread but I am conside...
By ambient , 2 days ago
Latest Topics
-
Grant Aerona3 R32 HPIDI17 performance in low temperatures
By davidm06 19 hours ago
-
By Broadsman 23 hours ago
-
By s_gatorator 3 days ago
-
Investment or not Solar/Battery instllation
By Alfapat 4 days ago
-
By Jancold 5 days ago
-
By MikeF 6 days ago
-
Running my new Nibe ASHP efficiently
By jamieheatpumpnew 6 days ago