Defrost behaviours
Since we are currently experiencing essentially 'worst' conditions for frosting, it might be useful to look at defrost behaviours and how they vary with the key parameters. People have variously reported everything from their heat pump fails to keep up to very infrequent defrosts. It would be useful if people post graphs over the period perhaps 3rd Jan - now, together with some basic system information. here is a starter for 10
ASHP Model: '7kW' Vaillant (spec says 8.5kW at design FT and OAT)
House loss: ~7kW at -2
Control mode: Pure weather compensation only
Volumiser/buffer tank & size: none
Zoning?: 5/16 rads are on TRVs otherwise completely open
General comment: defrosting frequently but managing to maintain room temperature across the house (the drop off towards the end is probably because I turned down a fancoil radiator in the room adjacent to the one where the sensor is)
Performance Graphs:
Flow Temp; OAT; IAT
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I can't give you graphs but....
ASHP Daikin Altherma 3-6kw
Heat loss? Dunno design temp by me 39º @ -3º
Control mode: pure weather compensation
Volumiser yes - size? (I'll have to look)
No Zoning totally open with radiators throughout.
Defrosting approx every 2 hours - for about 15 minutes - no noticeable heat loss just a slightly noisy high speed water flow around the system which is how I know it's defrosting and a sudden brief drop off in electrical consumption in the Octopus app (it's when the valve does a reverse ferret apparently 😁).
If I look at the MMI data while it's happening the flow temp between flow & return rapidly equalises - in front of my eyes - like 7º in a few seconds. It moves to defrost, the flow speeds up and stays that way throughout. Outside, it's almost silent as small black dots appear then become spaces of thawing and expand across the vents. It's quite fast and efficient.
But a bit disappointing drama-wise - no steam. 🙈
ASHP Daikin Altherma 3-8kw
House loss? 5431 @ -3.4
Control mode: pure weather compensation
Volumiser yes - don't know size
No Zoning open with radiators throughout.
Defrosting approx every 1.5/2 hours - for about 6 mins
Big spike in power on restart, yesterday trundling along using 900w, defrost for 6 mins, restart, and didn't get back down to the 900w level for 53 mins, 40 mins of that was over 2200w peaking at 3350w.
In that whole time the room temperature didn't change from before defrost so no idea why it went to those extremes.
Last night I turned off modulation (temperature the heat pump can modulate from the curve, was initially set to 5) and switched to quiet mode (slightly lowers the heat pump output).
So far so good, restarts after defrost today only went over 1400w for 18 mins and peaked briefly at 2000w getting back down in 40 mins
No noticible difference in performance .
Got to be down to -4 over the next 3 to 4 days so will see how that goes.
Here is my heat pump's behaviour (Midea 14kW running in weather compensation mode) over the last week, including cold outdoor air temperature periods when the heat pump ran regular defrost cycles. The set LWT is about where it should be, but, because of the defrost cycles, the effective (mean) LWT is far less than it should (and needs) to be. The unwanted fall in indoor air temperatures during these cold spells can also be clearly seen (ie it is an MCS fail), as can the slow recovery when the it warms up outside. Weather compensation is the problem here, the weather compensation logic says it is warmer outside, the house needs less heat, when in fact it needs more, because it is still colder than it should be because of the preceding cold snap. My auto-adapt script (boosts the LWT a bit when the room temp is below what it should be) does help a bit, but not enough, I still have the slow recovery, as seen during 5th Jan.
Midea 14kW (for now...) ASHP heating both building and DHW
Thats a brilliant plot with a full range of temperatures. Your 'no cycle' window is clearly shown as about 8C-5C. The cycles even only just above 8C look quite short and frequent, whereas you might hope that they would be long and infrequent at just a small delta above the max 'no-cycle' temp. I do realise we have already discussed this but the plot really nicely brings it all together.
Here is mine (showing FT only - I haven't yet worked out how to superimpose graphs in HA) over the same time. Actually a very similar pattern but with longer 'on' periods.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa - I agree, it is a useful plot. Sometimes nature does oblige, and provide a convenient operating range which we can observe. I do however wish the steady state (no cycling) window wasn't so small. There is also a question of whether I can tweak the around zero and below behaviour ie when defrost cycles dominate the picture. I have addressed this in the other Is my heat Pump Defective thread.
Posted by: @jamespaI haven't yet worked out how to superimpose graphs in HA
I don't think you can. You can use the 'History Explorer Card' add-on if it is still available to get multiple plots on the same page (and the plots are far easier on the eye than HA's native plotting). However, HA stores all its data in a sqlite database, and if you export the data in csv format, then you can chart it any way you want. You can use the SQLite Web add-on to get at the data, and use Query Tab (you have to run a query) > Export CSV to get the data. Don't be tempted to work on the database from outside HA when HA is running, it will corrupt and destroy it (you might however be able to copy the database file, and work on that copy, the point is don't work on a live database).
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderay@jamespa I do however wish the steady state (no cycling) window wasn't so small. There is also a question of whether I can tweak the around zero and below behaviour ie when defrost cycles dominate the picture.
I think we commented on this briefly earlier and I agree.
I also think it might be more or less inherent with our climate and the 3:1 (or in reality poorer) modulation ratio of current heat pumps.
Defrost is more or less bound to occur between 0 and 4C, when its both cold and damp.
For much of the UK we design for around -2C OAT/20C IAT, but stop heating at 16C because the 'waste' heat is sufficient to cover the difference. So deltaT at design OAT is 16--2 =18C) Even with a 3:1 modulation depth and perfectly matched sizing, this means that it will start cycling at deltaT=6, which is 10C, leaving a steady state window of 4C-10C only! Fortunately that is where our climate sits for much of the time, but of course by no means all the time.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,104 Topics
- 46.3 K Posts
- 54 Online
- 3,393 Members
Join Us!
Latest Posts
-
RE: Cooling with Samsung Gen6 and Flow error
@iaack The system isnt running long enough for any cond...
By EcoBaker , 2 hours ago
-
@heacol thanks for confirming we can only hope NAPIT ag...
By Bart , 4 hours ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@jeff And now for something I have never noticed before...
By Toodles , 5 hours ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@editor If it is of any interest, we had the BUS grant,...
By Toodles , 1 day ago
-
Sorry to hear that @bruce. Sadly I’ve heard from multip...
By Mars , 2 days ago
-
RE: Crystal Ball Time: Communal or even Area Energy Storage?
I am invested in a couple of listed energy storage fund...
By Old_Scientist , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
That would be my biggest commitment -time to gain great...
By SUNandAIR , 2 days ago
-
RE: Who has a V2G EV installation
As has been discussed on other threads, trying to justi...
By Majordennisbloodnok , 3 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Thanks @mikeh. Then I will also go back to non smart ta...
By ChandyKris , 3 days ago
-
RE: Location of hot water isolation valve on cylinder
@transparent Thank you so much and very helpful. Earlie...
By rossowheels , 4 days ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
It does indeed look like that, @skyefarmer. There is ...
By Majordennisbloodnok , 4 days ago
-
RE: Plug and play solar. Thoughts?
Have a read of my previous posts on so-called Balcony S...
By Lucia , 5 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 5 days ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 6 days ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 6 days ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 7 days ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 7 days ago