Defrost behaviours
Since we are currently experiencing essentially 'worst' conditions for frosting, it might be useful to look at defrost behaviours and how they vary with the key parameters. People have variously reported everything from their heat pump fails to keep up to very infrequent defrosts. It would be useful if people post graphs over the period perhaps 3rd Jan - now, together with some basic system information. here is a starter for 10
ASHP Model: '7kW' Vaillant (spec says 8.5kW at design FT and OAT)
House loss: ~7kW at -2
Control mode: Pure weather compensation only
Volumiser/buffer tank & size: none
Zoning?: 5/16 rads are on TRVs otherwise completely open
General comment: defrosting frequently but managing to maintain room temperature across the house (the drop off towards the end is probably because I turned down a fancoil radiator in the room adjacent to the one where the sensor is)
Performance Graphs:
Flow Temp; OAT; IAT
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I can't give you graphs but....
ASHP Daikin Altherma 3-6kw
Heat loss? Dunno design temp by me 39º @ -3º
Control mode: pure weather compensation
Volumiser yes - size? (I'll have to look)
No Zoning totally open with radiators throughout.
Defrosting approx every 2 hours - for about 15 minutes - no noticeable heat loss just a slightly noisy high speed water flow around the system which is how I know it's defrosting and a sudden brief drop off in electrical consumption in the Octopus app (it's when the valve does a reverse ferret apparently 😁).
If I look at the MMI data while it's happening the flow temp between flow & return rapidly equalises - in front of my eyes - like 7º in a few seconds. It moves to defrost, the flow speeds up and stays that way throughout. Outside, it's almost silent as small black dots appear then become spaces of thawing and expand across the vents. It's quite fast and efficient.
But a bit disappointing drama-wise - no steam. 🙈
ASHP Daikin Altherma 3-8kw
House loss? 5431 @ -3.4
Control mode: pure weather compensation
Volumiser yes - don't know size
No Zoning open with radiators throughout.
Defrosting approx every 1.5/2 hours - for about 6 mins
Big spike in power on restart, yesterday trundling along using 900w, defrost for 6 mins, restart, and didn't get back down to the 900w level for 53 mins, 40 mins of that was over 2200w peaking at 3350w.
In that whole time the room temperature didn't change from before defrost so no idea why it went to those extremes.
Last night I turned off modulation (temperature the heat pump can modulate from the curve, was initially set to 5) and switched to quiet mode (slightly lowers the heat pump output).
So far so good, restarts after defrost today only went over 1400w for 18 mins and peaked briefly at 2000w getting back down in 40 mins
No noticible difference in performance .
Got to be down to -4 over the next 3 to 4 days so will see how that goes.
Here is my heat pump's behaviour (Midea 14kW running in weather compensation mode) over the last week, including cold outdoor air temperature periods when the heat pump ran regular defrost cycles. The set LWT is about where it should be, but, because of the defrost cycles, the effective (mean) LWT is far less than it should (and needs) to be. The unwanted fall in indoor air temperatures during these cold spells can also be clearly seen (ie it is an MCS fail), as can the slow recovery when the it warms up outside. Weather compensation is the problem here, the weather compensation logic says it is warmer outside, the house needs less heat, when in fact it needs more, because it is still colder than it should be because of the preceding cold snap. My auto-adapt script (boosts the LWT a bit when the room temp is below what it should be) does help a bit, but not enough, I still have the slow recovery, as seen during 5th Jan.
Midea 14kW (for now...) ASHP heating both building and DHW
Thats a brilliant plot with a full range of temperatures. Your 'no cycle' window is clearly shown as about 8C-5C. The cycles even only just above 8C look quite short and frequent, whereas you might hope that they would be long and infrequent at just a small delta above the max 'no-cycle' temp. I do realise we have already discussed this but the plot really nicely brings it all together.
Here is mine (showing FT only - I haven't yet worked out how to superimpose graphs in HA) over the same time. Actually a very similar pattern but with longer 'on' periods.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa - I agree, it is a useful plot. Sometimes nature does oblige, and provide a convenient operating range which we can observe. I do however wish the steady state (no cycling) window wasn't so small. There is also a question of whether I can tweak the around zero and below behaviour ie when defrost cycles dominate the picture. I have addressed this in the other Is my heat Pump Defective thread.
Posted by: @jamespaI haven't yet worked out how to superimpose graphs in HA
I don't think you can. You can use the 'History Explorer Card' add-on if it is still available to get multiple plots on the same page (and the plots are far easier on the eye than HA's native plotting). However, HA stores all its data in a sqlite database, and if you export the data in csv format, then you can chart it any way you want. You can use the SQLite Web add-on to get at the data, and use Query Tab (you have to run a query) > Export CSV to get the data. Don't be tempted to work on the database from outside HA when HA is running, it will corrupt and destroy it (you might however be able to copy the database file, and work on that copy, the point is don't work on a live database).
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderay@jamespa I do however wish the steady state (no cycling) window wasn't so small. There is also a question of whether I can tweak the around zero and below behaviour ie when defrost cycles dominate the picture.
I think we commented on this briefly earlier and I agree.
I also think it might be more or less inherent with our climate and the 3:1 (or in reality poorer) modulation ratio of current heat pumps.
Defrost is more or less bound to occur between 0 and 4C, when its both cold and damp.
For much of the UK we design for around -2C OAT/20C IAT, but stop heating at 16C because the 'waste' heat is sufficient to cover the difference. So deltaT at design OAT is 16--2 =18C) Even with a 3:1 modulation depth and perfectly matched sizing, this means that it will start cycling at deltaT=6, which is 10C, leaving a steady state window of 4C-10C only! Fortunately that is where our climate sits for much of the time, but of course by no means all the time.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @davidi like those graphs. how do you generate them
Thank you!
I use plotly in python, with the data coming from csv files. If you are already familiar with python, you will find it a doddle, if you aren't familiar with python but are fairly computer literate you should be able to get to grips with it in hours rather than days. If you a computing novice then it will be more of a diddle than a doddle, but still achievable.
Midea 14kW (for now...) ASHP heating both building and DHW
- 26 Forums
- 2,306 Topics
- 51.7 K Posts
- 221 Online
- 5,970 Members
Join Us!
Podcast Picks
Latest Posts
-
Thank you! I use plotly in python, with the data comi...
By cathodeRay , 18 minutes ago
-
RE: Commencing on an ASHP Installation Process
I've re-read your initial response regarding this, and ...
By Sheriff Fatman , 23 minutes ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
Hey all, read through this and other documents but want...
By Vanq , 1 hour ago
-
RE: Maintaining temperature on windy day
It sounds like you have the 'cold' end of the WCC set u...
By benson , 2 hours ago
-
RE: Cashback Incentives That Reward Shorter Heat Pump Warranties
Quite aside from any blurring or crossing of legal line...
By Majordennisbloodnok , 2 hours ago
-
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Interesting temperatures this morning: this is what I'm...
By AndrewJ , 5 hours ago
-
RE: Don’t Install a Heat Pump Until You Read This
Understood. Solutions I can see if you cant somehow sq...
By JamesPa , 5 hours ago
-
RE: 10kw heat pump run in 24*7 data?
Vaillant are pretty good maintaining their ...
By JamesPa , 5 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
So this morning marked 24 hours up for installer. Rooms...
By Crimson , 13 hours ago
-
RE: Buffer tank bypass on EDF Ideal heat pump installation
@kevb, many of these companies look for the smallest of...
By Mars , 15 hours ago
-
RE: Electricity price predictions
Simple article with a DENZ graph showing how gas which ...
By Jeff , 17 hours ago
-
RE: Heat Pump on Flat Roof Low Frequency Noise from Detached Neighbor
@davidnolan22 Yes have been communicating woth the neig...
By People_Noise , 17 hours ago
-
Power Cut - Heat Pump Evaporator Iced Up
We have just had a power cut and 1 hour later power was...
By trebor12345 , 18 hours ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
A few weeks ago, I was having a discussion with someone...
By Majordennisbloodnok , 20 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk Hi I see you posted on openenergymon...
By JamesPa , 22 hours ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira
@editor When do “Mars Heat Pump Installation and Servic...
By Toodles , 24 hours ago
-
@morgan Likewise, I realise that some readers will appr...
By Toodles , 24 hours ago
-
A Smarter Smart Controller from Homely?
I received an email from Homely this morning enquiring ...
By Toodles , 1 day ago
-
RE: Grant Aerona 3 and Drayton system questions
Yes in general terms (obviously I cant tell if its exac...
By JamesPa , 1 day ago