Daikin problem
Posted by: @togfather@toodles Thank you for this. I will give it a try 🙂
Although this is generally good advice, as @iancalderbank pointed out, you need to get the very low flow rate fixed first in order to get heat into your house.
@togfather the flow rate is crucial. If that stays at 10.7, you will never move enough heat, there is basic physics in the way, the rate of movement of the water is directly related to the rate of the heat movement, it needs to be 20-25l/m at least.
I don't know enough about daikin to know if there could be some setting causing it to be low. If you are able to turn off the backup heater, please see if that makes any difference to the flow rate, if not then something else may be required.
@toodles @chrislay can you help with where are the pump speed settings on a daikin?
regarding your installer and daikin
1. they are just plain wrong about weather comp costing money. the point of weather comp is that it reduces the heat pumps power in proportion to how warm it is outside (or increases it in proportion to how cold, if you like). The times when its mild spent running at lower power , saves you money. (Bit more to it than that, but thats the "in a nutshell")
2. The low flow rate is a clear and obvious demonstrable fault with the system. There is no way they can "debate" whether its large enough. Its not, the system will never move enough heat to warm your house with this low flow rate. You can legitimately keep on calling them back, asking for your money back, until they get this value to where it should be.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank I have just looked in the Daikin Installer’s Manual and I am attaching a screen grab of the relevant part of a page about pump volume. I am confused to say the least! With my sight and having to magnify the image on my iPad, navigating the pages is very awkward. I will try to find HOW to adjust the flow rate but meanwhile, at the bottom of the image is the manual details so that Tog can look it up if not in possession of a printed copy.
Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Just found this link for the manual in case it helps you.
Toodles
Toodles, heats his home with cold draughts and cooks food with magnets.
I’ve done my best as my sight allows for now, may I suggest Togfather that you look at section 8 on configuration where you will find mention of the back up heater. My system doesn’t have such a heater and therefore, I don’t wish to rootle through the configuration which may not be the same anyway! I’m glad my installers set up my pump correctly, it sounds like your is a real nightmare job and the installer should be putting it right for you - compensation?
Regards, Toodles
Toodles, heats his home with cold draughts and cooks food with magnets.
@iancalderbank I don't know if you can set the actual pump speed. As far as I know the controller sets the speed to maintain the delta t. 10.7 is the minimum and the max is about 40. It will then switch the compressor on/off as well. I think the default dt is 7 or 8.
One other thought - did the installer upgrade any pipework? - oil may have been piped with 22mm - that will be too small.
-
How can we prevent our LG heat pump from freezing up in cold weather?
7 months ago
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
8 months ago
-
Daikin Error Code 7H05
10 months ago
-
British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
12 months ago
-
Daikin COP / energy used measurement from MMI
1 year ago
- 26 Forums
- 2,197 Topics
- 48.4 K Posts
- 59 Online
- 5,854 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Heat Pump Installers: Competence, Illusion and the Hard Truth Homeowners Must Face
We’re going to do a full retrofix in spring with @pirat...
By Mars , 8 minutes ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@agentgeorge err… Pass! I dunno what caused that! I’ll ...
By Toodles , 16 minutes ago
-
RE: Sizing - Save me from my headache
If you get an R290 pump you should be able to heat the ...
By JamesPa , 23 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa can you take a pic of the primaries inside the...
By AdamK , 46 minutes ago
-
RE: Large heat pump options for church building
@aventus-eco Thanks Sean, will drop you a line.
By Josephiah , 48 minutes ago
-
RE: Heat pump and wifi kit connection.
Thanks, how hard was it wiring up? I have a gen6, and t...
By Andehh , 1 hour ago
-
RE: Moving FIT array onto a Tesla Powerwall 3 possible?
@toodles that’s good news for @adamk
By Judith , 2 hours ago
-
RE: How to Understand Wiring Up a Heat Pump
I would recommend youtube videos by Glyn Hudson of open...
By bontwoody , 2 hours ago
-
@drei do you mean running block average, so 6months bef...
By Judith , 2 hours ago
-
RE: Samsung Gen 6 - Schedules not working
@technogeek That sounds very logical :-). I will give i...
By bontwoody , 5 hours ago
-
RE: Who's your electricity provider and what's your tariff?
Considering Octopus states all their electricity is gre...
By AgentGeorge , 5 hours ago
-
RE: Heat Pump + Tado Setup: Smarter Control for Secondary Pumps?
@pirate-rich thanks for the reply. If I were to explo...
By Lloydi , 6 hours ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
@transparent I think the committee might get into some ...
By Toodles , 7 hours ago
-
Samsung ASHP Support in Midlands area?
Hi all, Per title.... can anyone recommend a ASHP ser...
By Andehh , 7 hours ago
-
RE: Why Air Release Valves and Deaerators are Non-Negotiable
When I had my system serviced recently, I asked the guy...
By Old_Scientist , 10 hours ago
-
May I present the maths I referred to earlier when disc...
By Transparent , 10 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
How many times and dates have epc sap rules been change...
By Tim441 , 10 hours ago
-
RE: Rodents! A word of warning for heat pump owners
I think similar care should be taken against vermin ing...
By Transparent , 11 hours ago