Daikin problem
Posted by: @togfather@toodles Thank you for this. I will give it a try 🙂
Although this is generally good advice, as @iancalderbank pointed out, you need to get the very low flow rate fixed first in order to get heat into your house.
@togfather the flow rate is crucial. If that stays at 10.7, you will never move enough heat, there is basic physics in the way, the rate of movement of the water is directly related to the rate of the heat movement, it needs to be 20-25l/m at least.
I don't know enough about daikin to know if there could be some setting causing it to be low. If you are able to turn off the backup heater, please see if that makes any difference to the flow rate, if not then something else may be required.
@toodles @chrislay can you help with where are the pump speed settings on a daikin?
regarding your installer and daikin
1. they are just plain wrong about weather comp costing money. the point of weather comp is that it reduces the heat pumps power in proportion to how warm it is outside (or increases it in proportion to how cold, if you like). The times when its mild spent running at lower power , saves you money. (Bit more to it than that, but thats the "in a nutshell")
2. The low flow rate is a clear and obvious demonstrable fault with the system. There is no way they can "debate" whether its large enough. Its not, the system will never move enough heat to warm your house with this low flow rate. You can legitimately keep on calling them back, asking for your money back, until they get this value to where it should be.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank I have just looked in the Daikin Installer’s Manual and I am attaching a screen grab of the relevant part of a page about pump volume. I am confused to say the least! With my sight and having to magnify the image on my iPad, navigating the pages is very awkward. I will try to find HOW to adjust the flow rate but meanwhile, at the bottom of the image is the manual details so that Tog can look it up if not in possession of a printed copy.
Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Just found this link for the manual in case it helps you.
Toodles
Toodles, he heats his home with cold draughts and cooks his food with magnets.
I’ve done my best as my sight allows for now, may I suggest Togfather that you look at section 8 on configuration where you will find mention of the back up heater. My system doesn’t have such a heater and therefore, I don’t wish to rootle through the configuration which may not be the same anyway! I’m glad my installers set up my pump correctly, it sounds like your is a real nightmare job and the installer should be putting it right for you - compensation?
Regards, Toodles
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@iancalderbank I don't know if you can set the actual pump speed. As far as I know the controller sets the speed to maintain the delta t. 10.7 is the minimum and the max is about 40. It will then switch the compressor on/off as well. I think the default dt is 7 or 8.
One other thought - did the installer upgrade any pipework? - oil may have been piped with 22mm - that will be too small.
-
How can we prevent our LG heat pump from freezing up in cold weather?
2 months ago
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
3 months ago
-
Daikin Error Code 7H05
5 months ago
-
British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
7 months ago
-
Daikin COP / energy used measurement from MMI
1 year ago
- 22 Forums
- 2,057 Topics
- 44.9 K Posts
- 38 Online
- 3,302 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
A lot of things can work if you are SCoP chaser, do the...
By Johnmo , 38 minutes ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@johnmo yes that is the current workaround to access th...
By benson , 44 minutes ago
-
RE: Rate the quality of your heat pump design and installation
Yes the HP is running weather compensation and I’ve lef...
By Davesoa , 3 hours ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
OK, so when the HP comes on it becomes obvious.It's on ...
By tdudgeon , 18 hours ago
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
@johnmo I think we’ve been trudging through the same...
By SUNandAIR , 18 hours ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 2 days ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 2 days ago
-
RE: Is your heat pump insured?
@johnmo sorry it comes across like that. The post is au...
By KevinPotts , 2 days ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 3 days ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 3 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 3 days ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Hopefully iv done the right thing today by signing up t...
By Westkent , 3 days ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 3 days ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 3 days ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
The useful bit is the bit that specifies the heat loss ...
By JamesPa , 3 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 4 days ago
-
@editor thanks Mars that’s the same table I found in th...
By Gary , 4 days ago
-
RE: Tariff and charging strategy advice please
They haven't asked me to prove that I have an EV (I do)...
By JamesPa , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Took a while to find on the OFGEN site: ”The FIT sche...
By AgentGeorge , 4 days ago