Posted by: @togfather@toodles Thank you for this. I will give it a try 🙂
Although this is generally good advice, as @iancalderbank pointed out, you need to get the very low flow rate fixed first in order to get heat into your house.
@togfather the flow rate is crucial. If that stays at 10.7, you will never move enough heat, there is basic physics in the way, the rate of movement of the water is directly related to the rate of the heat movement, it needs to be 20-25l/m at least.
I don't know enough about daikin to know if there could be some setting causing it to be low. If you are able to turn off the backup heater, please see if that makes any difference to the flow rate, if not then something else may be required.
@toodles @chrislay can you help with where are the pump speed settings on a daikin?
regarding your installer and daikin
1. they are just plain wrong about weather comp costing money. the point of weather comp is that it reduces the heat pumps power in proportion to how warm it is outside (or increases it in proportion to how cold, if you like). The times when its mild spent running at lower power , saves you money. (Bit more to it than that, but thats the "in a nutshell")
2. The low flow rate is a clear and obvious demonstrable fault with the system. There is no way they can "debate" whether its large enough. Its not, the system will never move enough heat to warm your house with this low flow rate. You can legitimately keep on calling them back, asking for your money back, until they get this value to where it should be.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank I have just looked in the Daikin Installer’s Manual and I am attaching a screen grab of the relevant part of a page about pump volume. I am confused to say the least! With my sight and having to magnify the image on my iPad, navigating the pages is very awkward. I will try to find HOW to adjust the flow rate but meanwhile, at the bottom of the image is the manual details so that Tog can look it up if not in possession of a printed copy.
Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Just found this link for the manual in case it helps you.
Toodles
Toodles, he heats his home with cold draughts and cooks his food with magnets.
I’ve done my best as my sight allows for now, may I suggest Togfather that you look at section 8 on configuration where you will find mention of the back up heater. My system doesn’t have such a heater and therefore, I don’t wish to rootle through the configuration which may not be the same anyway! I’m glad my installers set up my pump correctly, it sounds like your is a real nightmare job and the installer should be putting it right for you - compensation?
Regards, Toodles
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@iancalderbank I don't know if you can set the actual pump speed. As far as I know the controller sets the speed to maintain the delta t. 10.7 is the minimum and the max is about 40. It will then switch the compressor on/off as well. I think the default dt is 7 or 8.
One other thought - did the installer upgrade any pipework? - oil may have been piped with 22mm - that will be too small.
-
How can we prevent our LG heat pump from freezing up in cold weather?
5 days ago
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
1 month ago
-
Daikin Error Code 7H05
3 months ago
-
British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
5 months ago
-
Daikin COP / energy used measurement from MMI
11 months ago
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 61 Online
- 2,276 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 11 minutes ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 38 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami I think if the heat loss documentation matches a ...
By bontwoody , 1 hour ago
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa I'm afraid that's over my head but if anyon...
By IRMartini , 1 hour ago
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 2 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 2 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 3 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 6 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 8 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 20 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 22 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 24 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 8 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 9 hours ago
-
SolarPV tables / online calculator
By MichelleC 16 hours ago
-
By Toodles 2 days ago