Daikin problem
Posted by: @togfather@toodles Thank you for this. I will give it a try 🙂
Although this is generally good advice, as @iancalderbank pointed out, you need to get the very low flow rate fixed first in order to get heat into your house.
@togfather the flow rate is crucial. If that stays at 10.7, you will never move enough heat, there is basic physics in the way, the rate of movement of the water is directly related to the rate of the heat movement, it needs to be 20-25l/m at least.
I don't know enough about daikin to know if there could be some setting causing it to be low. If you are able to turn off the backup heater, please see if that makes any difference to the flow rate, if not then something else may be required.
@toodles @chrislay can you help with where are the pump speed settings on a daikin?
regarding your installer and daikin
1. they are just plain wrong about weather comp costing money. the point of weather comp is that it reduces the heat pumps power in proportion to how warm it is outside (or increases it in proportion to how cold, if you like). The times when its mild spent running at lower power , saves you money. (Bit more to it than that, but thats the "in a nutshell")
2. The low flow rate is a clear and obvious demonstrable fault with the system. There is no way they can "debate" whether its large enough. Its not, the system will never move enough heat to warm your house with this low flow rate. You can legitimately keep on calling them back, asking for your money back, until they get this value to where it should be.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank I have just looked in the Daikin Installer’s Manual and I am attaching a screen grab of the relevant part of a page about pump volume. I am confused to say the least! With my sight and having to magnify the image on my iPad, navigating the pages is very awkward. I will try to find HOW to adjust the flow rate but meanwhile, at the bottom of the image is the manual details so that Tog can look it up if not in possession of a printed copy.
Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Just found this link for the manual in case it helps you.
Toodles
Toodles, heats his home with cold draughts and cooks food with magnets.
I’ve done my best as my sight allows for now, may I suggest Togfather that you look at section 8 on configuration where you will find mention of the back up heater. My system doesn’t have such a heater and therefore, I don’t wish to rootle through the configuration which may not be the same anyway! I’m glad my installers set up my pump correctly, it sounds like your is a real nightmare job and the installer should be putting it right for you - compensation?
Regards, Toodles
Toodles, heats his home with cold draughts and cooks food with magnets.
@iancalderbank I don't know if you can set the actual pump speed. As far as I know the controller sets the speed to maintain the delta t. 10.7 is the minimum and the max is about 40. It will then switch the compressor on/off as well. I think the default dt is 7 or 8.
One other thought - did the installer upgrade any pipework? - oil may have been piped with 22mm - that will be too small.
-
Daikin 6kw setup with Dixell controller
4 weeks ago
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
4 months ago
-
Heating Turned Off but Radiators Still Warm
5 months ago
-
How can we prevent our LG heat pump from freezing up in cold weather?
12 months ago
-
Daikin Error Code 7H05
1 year ago
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 379 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
@editor has said a lot but let me address this one head...
By JamesPa , 2 hours ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
Well I've had an interesting few days and would like to...
By giganto , 4 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
Yes, here's mine. From the service manual parts numbers...
By bobflux , 8 hours ago
-
RE: Underfloor Heating Installation Issues with Heat Pump
Thanks for sharing your observations, both of you. From...
By Jonatan , 8 hours ago
-
Had to learn the hard way 🤣 now I'm sharing T...
By bobflux , 8 hours ago
-
RE: Issue with a Grant Air Source Heat Pump & Tado Smart Thermostat
Im assuming from your original post that hysterisis ref...
By JamesPa , 9 hours ago
-
RE: Heat Pump vs New Gas Boiler for Inherited House - Worth the Extra Cost?
Hi @fretless6 Mike, I have experience with Taggas (Re...
By Old_Scientist , 11 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@bobflux With my limited HA skills I can't ad...
By Ubert767 , 12 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Now seems a good time to summarise the costs and effici...
By benson , 15 hours ago
-
RE: Tell us about your Solar (PV) setup
@mk4 Charge to 100%, discharge down to 10%.
By bobflux , 17 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 22 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 1 day ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 1 day ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 1 day ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 2 days ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 2 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 3 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 3 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 4 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 4 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 4 days ago