Thanks @bridgetjohn. So from those pics I'm fairly certain you've got a non-Daikin thermostat which is controlling the operation. You have a fixed leaving water temperature (ie the radiator water) of 60 deg C. That looks to me like a classic case of it being set up like a gas boiler !!
With Derek's invaluable help I've set mine up like a heat pump - so my radiator water varies with the outside temp. It was 12 deg C when I took these pics and the system set the radiator water at 29 deg. The pump ran on tick-over all day long and kept the house at a steady 21/22 deg. All was silent ! As the outside cools the system will increase the radiator water temp. @Derek-m will advise some numbers...
Incidentally your leaving water hadn't reached 60 deg, which is a push (possibly even impossible!) for your heat pump. The little blue arrowhead on the circle indicates where 60 would be and the end of the blue curve indicates what the temperature actually is.
@heat-pump-newbie thank you. You are right - we have a honeywell thermostat control which is clicking it on and off as the heat drops / increases.
And yes it seems to want to "fire up" like a gas boiler - blast round the pipes and make a noise and then settle down.
Posted by: @bridgetjohn@heat-pump-newbie thank you. You are right - we have a honeywell thermostat control which is clicking it on and off as the heat drops / increases.
And yes it seems to want to "fire up" like a gas boiler - blast round the pipes and make a noise and then settle down.
Hi Bridget,
Thanks to Newbie's guidance you have discovered that your system has been set with a fixed water flow temperature setting of 60C, which is about the worst possible setting that could have been made. 😡
I would strongly recommend that you change your system to weather dependent (WD) control, with the following initial settings water flow temperature (WFT) 45C at outdoor air temperature of -5C and WFT of 20C at outdoor air temperature of 18C.
Newbie, would you be kind enough to guide Bridget through the adjustment process. 😎
As the name suggests I am new to this but here goes:
Go to Main > Setpoint mode > and left dial to highlight in blue 'WD heating fixed cooling' Press left dial to select.
**Derek - my system's not set up for cooling so is different here **
Then dial down to highlight 'Heating WD curve', press to select. Can you take a photo of that and post it here please !! Then we'll see what's next... I'm assuming there will be a default curve already there??
Posted by: @heat-pump-newbieAs the name suggests I am new to this but here goes:
Go to Main > Setpoint mode > and left dial to highlight in blue 'WD heating fixed cooling' Press left dial to select.
**Derek - my system's not set up for cooling so is different here **
Then dial down to highlight 'Heating WD curve', press to select. Can you take a photo of that and post it here please !! Then we'll see what's next... I'm assuming there will be a default curve already there??
Hi Newbie,
Thank you for helping. Because I don't have access to a Daikin controller and the manual is not that clear, I thought that you would be of greatest help to Bridget. I hope that you don't mind.
As far as cooling is concerned, you don't really want it to operate unless you have fan coil units within your system. Passing cold water through radiators will probably lead to puddles of water on the floor.
Posted by: @heat-pump-newbiemaybe its shouldn't be set up with that option ?
Hi Newbie,
If it is possible I would suggest disabling the cooling option. If not then set the parameters such that it will never operate.
Maybe then @bridgetjohn keep scrolling on the Setpoint Mode screen and select Weather Dependant if that is an option..
@derek-m actually this description from Daikin says it's heating only ! Not sure the commissioning procedure was followed very well !
From reading the various manuals it would appear that the operation of the controllers is fairly standard, though some settings may be excluded if the necessary equipment has not been installed.
If you could explain to Bridget, step by step, how you set up weather compensation on your system that would be very useful.
Bridget, make a note of the parameter settings prior to making any changes, so that you can always reverse any changes.
- 26 Forums
- 2,114 Topics
- 46.4 K Posts
- 93 Online
- 3,410 Members
Join Us!
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
@chandykris I watched that video with interest too. F...
By Old_Scientist , 32 minutes ago
-
Benefits of an extra horizontal loop for GSHP
Hello everyone, We're in the process of installin...
By thewiseoldbird , 17 hours ago
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 1 day ago
-
RE: Buffers, hot water and cooling
The principal reason that heat pumps have minimum flow ...
By JamesPa , 1 day ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 2 days ago
-
RE: Wood burner with ASHP - direct air?
I love the new fully Viking look... best personal avata...
By Mars , 2 days ago
-
RE: No-code, plug-and-play monitoring for your heat pump
I think I have found “The One!” Waveshare ESP32-S3-POE-...
By Grantmethestrength , 3 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 4 days ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 4 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 4 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 4 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 6 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 6 days ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 7 days ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 7 days ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 7 days ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 7 days ago
-
RE: Compute heat loss from energy used
@jamespa Ebac must be similar to Mitsubishi as they buy...
By marcinwloch69@gmail.com , 7 days ago
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 1 week ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 1 week ago