Creating a second zone on Mitsubishi Ecodan ASHP
I am trying to set up a second zone with my Mitsubishi Ecodan ASHP system. Zone 1 is the existing radiator circuit and zone 2 will be the new UFH in an extension. Zone 1 is controlled via the wireless programmer and zone 2 via a separate thermostat and separate pump.
I have the contacts from the UFH thermostat via the UFH wiring centre connected to IN6 (Room Thermostat 2 input) and the UFH Pump to OUT3 (Zone 2 space heating).
I have turned on DIP switches SW2-6 and SW2-7 but keep getting an L5 error (Indoor FTC temperature thermistor reading incorrect value, thermistor disconnected or wired into the wrong connection on the board, incorrect dip switch setting on the FTC board). The manual tells me I don’t need an indoor thermistor if I’m using the remote wireless controller. I have also tried changing SW3-1 and SW4-1 but still get an error code.
With SW2-6 and SW2-7 on, the controller shows 2 zones (Z1 - Z2) under the House symbol but then goes into the error mode.
What am I doing wrong? Any help much appreciated.
Do you have SW3-1 turned on that is required to allow the input from the 2nd thermostat.
mine is wired as 2 zones and if I had my time again I would wire it as 1 zone running off a single thermostat as a max temp cut off. If you have 2 zones that work independently the HP is more likely to cycle on and off due to low water volume to heat leading to poor efficiency and increased wear
Thanks, Gary, - I've tried it with SW3-1 turned on - but still get the L5 error. I assumed that SW3-1 was purely to change the operation depending upon the thermostat contacts being normally open or normally closed.
There is also a statement in the installation manual that says "When Dip SW 4-1 is OFF, 2-zone temperature control and 2-zone valve ON/OFF control is not available." So I've changed SW4-1 as well, although in the table of DIP Switches it states that SW4-1 is for multiple outdoor units. I've also tried changing SW4-2 to set to Master - but in each case I get the L5 error.
Posted by: @garymine is wired as 2 zones and if I had my time again I would wire it as 1 zone running off a single thermostat
I take your point about a single zone -it has been running as a single zone but I'd like to try with more control. Also it has now become a challenge to achieve it!
Derek's video link makes a good point, what have you got the zones set up as in the FTC controller, if you are using the main FTC controller to measure room temperature to control the rads that should be set as main RC and if you are using a third party thermostat as the controller for the UFH for zone 2 that confusingly should also be set as main RC, if its set as anything else it will be looking for a signal from a Mitsubishi wireless controller that you don't have, that could create the error you are seeing.
Thank you Derek and Gary. I'm using the wireless thermostat to control the temp for the rads and a third party one to control the UFH. So from the video it looks as if Zone 1 should be set to Room RC and Zone 2 to Main RC. I'll try that later. Thanks.
Posted by: @bryanbThank you Derek and Gary. I'm using the wireless thermostat to control the temp for the rads and a third party one to control the UFH. So from the video it looks as if Zone 1 should be set to Room RC and Zone 2 to Main RC. I'll try that later. Thanks.
The main point that I was making was the need to switch the controller off and then back on for DIP Switch changes to take effect.
I had been doing that - the whole system was shut down between changes. But I hadn't made any changes to the main controller but it looks as if I can't do that without changing the DIP switches again to enable a second zone.
Still no joy! With SW2-6 and SW2-7 turned on I can see two zones and set Zone 1 sensor to be Room RC1 and Zone 2 to be mainRC (instead of TH1). However I am still getting the L5 error to do with the indoor FTC thermistor.
I've also tried with SW4-1 and SW4-2 turned on - as in the manual it states these need to be on for 2 zone control - but it doesn't affect the L5 error.
Mine may be older and different but on mine SW2-6 is for a mixing tank and the manual states that SW2-7 only works if SW2-6 is off.
SW4-1 and SW4-2 on mine relate to using multiple outdoor units as master and slave and don't relate to multiple zones so these are also off.
Posted by: @bryanbStill no joy! With SW2-6 and SW2-7 turned on I can see two zones and set Zone 1 sensor to be Room RC1 and Zone 2 to be mainRC (instead of TH1). However I am still getting the L5 error to do with the indoor FTC thermistor.
I've also tried with SW4-1 and SW4-2 turned on - as in the manual it states these need to be on for 2 zone control - but it doesn't affect the L5 error.
I suspect that you are getting an L5 error because under 'Room Sensor Settings' you are trying to allocate RC1 or MainRC to zone 2, whereas the device installed is actually a thermostat (On/Off device) rather than a temperature sensor (Thermistor). I suggest that you set Zone 1 to TH1 or MainRC and leave Zone 2 unselected.
- 24 Forums
- 1,416 Topics
- 29.8 K Posts
- 38 Online
- 1,203 Members
Join Us!
Latest Posts
-
RE: SCOP and seasonal variations
Unfortunately, I have already baked in the savings. I f...
By Majordennisbloodnok , 2 mins ago
-
RE: Advice on potential HW Cylinder size
@toodles We thought about the sunamp but decided agains...
By JWilliams89 , 4 mins ago
-
RE: Gas Combi to ASHP - Making sense of survey results and proposal.
@irmartini Hello Ian, I wonder if your house is really ...
By JEH , 2 hours ago
-
@hubb84 No experience here I’m afraid, but I think your...
By Toodles , 2 hours ago
-
RE: Samsung ASHP scheduling help
@morh Your post was music to my ears! I am getting a ...
By Elgreco69 , 3 hours ago
-
RE: Issues with Vaillant connectivity via the MyCONNECT gateway
@drew-pa I have given up on the app - right now it is s...
By dr_dongle , 3 hours ago
-
RE: Optimising Energy Efficiency in Rural Aberdeenshire - GSHP vs. ASHP
@transparent Good points! Do you know if because of ...
By bontwoody , 4 hours ago
-
RE: ASHP Advice: High Temperature vs. Low Temperature Heat Pump For Microbore
Hi - we have a Daikin 16kW HT ASHP installed which was ...
By Marzipan71 , 8 hours ago
-
RE: New Fogstar 15.5kWh upright solution
I'm sorry to hear this is the case. This is not th...
By ChickenBig , 11 hours ago
-
RE: Question about Ecodan's Room Autoadapt mode
@gary Thanks. I'm emboldened to give it a go!
By afarmery , 23 hours ago
-
RE: My ASHP is not performing as well as I’d hoped: COP just over 2
@toodles No. But I wasn't forced there either and The K...
By Morgan , 1 day ago
-
RE: Viessmann Vitocal 250-A in the UK
We have a 10Kw Viessmann 200A it SCOP is currently 5.2,...
By MikeF , 1 day ago
-
RE: Jokes and fun posts about heat pumps and renewables
Recent advances in AI are stunning. I enabled 'facial...
By Transparent , 1 day ago
-
RE: Maximising Savings: Navigating My First Year with Octopus Energy and Heat Pump Running Costs
@allyfish Having been on Agile tariff again for several...
By Toodles , 2 days ago
-
RE: Say hello and introduce yourself
@dr_dongle Living as we do on a hill, one side of our p...
By Toodles , 2 days ago
-
RE: Fossil Fuel Fired Heating v Heat Pump?
Another aspect was the DHW heating; the coal fire in th...
By Toodles , 2 days ago
-
In an ideal world a heat pump unit would contain two co...
By Derek M , 3 days ago
-
RE: Installing your own ASHP - DIY
@tomasmcguinness Have you been able to perform any sani...
By IanMK13 , 3 days ago
-
RE: Vaillant Arotherm Settings for New Installation
@drew-pa Ah thanks. Good to know I dont have a misconce...
By bontwoody , 3 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
On the whole marketing claims vs reality on performance...
By GunboatDiplomat , 3 days ago
Latest Topics
-
Advice on potential HW Cylinder size
By JWilliams89 5 hours ago
-
By Graeme 1 day ago
-
Interesting heat pumps installations
By Mars 4 days ago
-
What is Wrong with our Heat Pump Installation?
By Mars 5 days ago
-
Fossil Fuel Fired Heating v Heat Pump?
By Toodles 5 days ago