Creating a second zone on Mitsubishi Ecodan ASHP
I am trying to set up a second zone with my Mitsubishi Ecodan ASHP system. Zone 1 is the existing radiator circuit and zone 2 will be the new UFH in an extension. Zone 1 is controlled via the wireless programmer and zone 2 via a separate thermostat and separate pump.
I have the contacts from the UFH thermostat via the UFH wiring centre connected to IN6 (Room Thermostat 2 input) and the UFH Pump to OUT3 (Zone 2 space heating).
I have turned on DIP switches SW2-6 and SW2-7 but keep getting an L5 error (Indoor FTC temperature thermistor reading incorrect value, thermistor disconnected or wired into the wrong connection on the board, incorrect dip switch setting on the FTC board). The manual tells me I don’t need an indoor thermistor if I’m using the remote wireless controller. I have also tried changing SW3-1 and SW4-1 but still get an error code.
With SW2-6 and SW2-7 on, the controller shows 2 zones (Z1 - Z2) under the House symbol but then goes into the error mode.
What am I doing wrong? Any help much appreciated.
Do you have SW3-1 turned on that is required to allow the input from the 2nd thermostat.
mine is wired as 2 zones and if I had my time again I would wire it as 1 zone running off a single thermostat as a max temp cut off. If you have 2 zones that work independently the HP is more likely to cycle on and off due to low water volume to heat leading to poor efficiency and increased wear
Thanks, Gary, - I've tried it with SW3-1 turned on - but still get the L5 error. I assumed that SW3-1 was purely to change the operation depending upon the thermostat contacts being normally open or normally closed.
There is also a statement in the installation manual that says "When Dip SW 4-1 is OFF, 2-zone temperature control and 2-zone valve ON/OFF control is not available." So I've changed SW4-1 as well, although in the table of DIP Switches it states that SW4-1 is for multiple outdoor units. I've also tried changing SW4-2 to set to Master - but in each case I get the L5 error.
Posted by: @garymine is wired as 2 zones and if I had my time again I would wire it as 1 zone running off a single thermostat
I take your point about a single zone -it has been running as a single zone but I'd like to try with more control. Also it has now become a challenge to achieve it!
Derek's video link makes a good point, what have you got the zones set up as in the FTC controller, if you are using the main FTC controller to measure room temperature to control the rads that should be set as main RC and if you are using a third party thermostat as the controller for the UFH for zone 2 that confusingly should also be set as main RC, if its set as anything else it will be looking for a signal from a Mitsubishi wireless controller that you don't have, that could create the error you are seeing.
Thank you Derek and Gary. I'm using the wireless thermostat to control the temp for the rads and a third party one to control the UFH. So from the video it looks as if Zone 1 should be set to Room RC and Zone 2 to Main RC. I'll try that later. Thanks.
Posted by: @bryanbThank you Derek and Gary. I'm using the wireless thermostat to control the temp for the rads and a third party one to control the UFH. So from the video it looks as if Zone 1 should be set to Room RC and Zone 2 to Main RC. I'll try that later. Thanks.
The main point that I was making was the need to switch the controller off and then back on for DIP Switch changes to take effect.
I had been doing that - the whole system was shut down between changes. But I hadn't made any changes to the main controller but it looks as if I can't do that without changing the DIP switches again to enable a second zone.
Still no joy! With SW2-6 and SW2-7 turned on I can see two zones and set Zone 1 sensor to be Room RC1 and Zone 2 to be mainRC (instead of TH1). However I am still getting the L5 error to do with the indoor FTC thermistor.
I've also tried with SW4-1 and SW4-2 turned on - as in the manual it states these need to be on for 2 zone control - but it doesn't affect the L5 error.
Mine may be older and different but on mine SW2-6 is for a mixing tank and the manual states that SW2-7 only works if SW2-6 is off.
SW4-1 and SW4-2 on mine relate to using multiple outdoor units as master and slave and don't relate to multiple zones so these are also off.
Posted by: @bryanbStill no joy! With SW2-6 and SW2-7 turned on I can see two zones and set Zone 1 sensor to be Room RC1 and Zone 2 to be mainRC (instead of TH1). However I am still getting the L5 error to do with the indoor FTC thermistor.
I've also tried with SW4-1 and SW4-2 turned on - as in the manual it states these need to be on for 2 zone control - but it doesn't affect the L5 error.
I suspect that you are getting an L5 error because under 'Room Sensor Settings' you are trying to allocate RC1 or MainRC to zone 2, whereas the device installed is actually a thermostat (On/Off device) rather than a temperature sensor (Thermistor). I suggest that you set Zone 1 to TH1 or MainRC and leave Zone 2 unselected.
- 22 Forums
- 2,029 Topics
- 44.2 K Posts
- 63 Online
- 3,235 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Many thanks JamesPa - that's great advice which is well...
By Tomdad , 1 hour ago
-
RE: Bathroom Radiator replacement
@rob-nezard can you please offer your professional advi...
By Mars , 1 hour ago
-
The radiator output at any given ft will increase if th...
By JamesPa , 2 hours ago
-
RE: Performance of Heat Pumps in Mild Weather
@heatgeek The switches to the flow rate were manua...
By RobS , 4 hours ago
-
-
RE: Questions on my Hitachi Yutaki SCombi Heat Pump
OK, thats good and low. With low flow temperatures lik...
By JamesPa , 20 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa “They are all equal but, some are more equal t...
By Toodles , 21 hours ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
@cliffhanger Mine has a 'space heating off' setting! O...
By JamesPa , 1 day ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
Thank you, that helped in my understanding. I believe ...
By trebor12345 , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@old_scientist As another example of errors / differenc...
By Toodles , 1 day ago
-
RE: Replacing Worcester oil boiler with an ASHP
Is this something you are thinking of doing? Or has thi...
By Cliff-Arnold , 2 days ago
-
RE: Say hello and introduce yourself
Hi Mars Thanks for inviting me to join the forum, I h...
By Cliff-Arnold , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@agentgeorge Not with Eon Next. The only reson I left O...
By Andris , 2 days ago
-
RE: How hard and expensive would it be to change panel and add battery?
The difficulty with this discussion is that it's referr...
By Transparent , 2 days ago
-
Is this normal? Click of the DHW returning to space heating
This has been bugging me for a while and I just wanted ...
By Grantmethestrength , 3 days ago
-
@sandman1600 you need to measure whats going on real...
By davidnolan22 , 4 days ago
-
@brandon-r is this a project that you could assist with...
By Mars , 4 days ago
-
Has anyone installed these on their ASHP fed radiator s...
By Grantmethestrength , 5 days ago
-
Just an update on the responses received by Smart Heati...
By Eliuccio , 5 days ago
-
RE: Is your gut better than Math
By SUNandAIR , 5 days ago