Considering a heat pump for a '50s house

36 Posts
11 Users
22 Reactions
3,935 Views
(@southweststokie)
Active Member Member
142 kWhs
Joined: 3 years ago
Posts: 5
Topic starter  

Southweststokie here, hello !

Sit rep - just started significant extension and refurb work on 50's house, and now getting more and more entwined into the whole heat pump debate etc as we get closer to selecting a system and then get it installed. Original house has just blown rockwool cavity installation - prob over 40 years old, but it's there - and a prior extension circa 20 years ago has high density insulation slabs in the cavity as deemed by regs at that time. New extension doing similar, though specs of insulation may have improved, and this will leave some, but not many older parts of the building still forming outside walls. Opting in final refurb phase to add further insulation from the inside for these areas. Loft on the 'add insulation' list as well. Hardwood double glazing throughout, but now needing attention to address issues inc leaky areas, doors etc. Underfloor heating throughout ground floor, but will be a mix of underfloor and legacy rads upstairs. Total annual KwH usage circa 37KwH (dual fuel), and new build will add circa 20% area, so with headroom, think we'll be heading for circa 45 KwH requirement. All in all, fairly representative of a house that must be replicated 1000's of times across the UK. Mains gas, leccy (80A fuse I think - Western Power are checking out) and that about completes the picture.

EV on order, though delivery will be god knows when - last I heard was Sept this year, and will be replacing the gas boiler with an ASHP. As much PV as we can put on the roof is the intent, and not now opting for solar water.

Being recommended a Daikin Altherma 3 H HT based system, and tenders are out for supply, fitting, etc. This is a High Temperature system, and is proposed as the right solution considering the full picture of the house.

Wanting to ask if anyone has experience of this specific ASHP, and to generally ask if there are an other considerations we should be taking in to account. Slight concern that the HT spec will mean higher running costs, but not sure how much. Daikin suggesting not much more the low temp but not quantifying currently. Believe Julian Clarke has one of these, but as a newbie, I can't message him directly -think that's how it goes. Hi Julian, any comments ?

Great site, has to be the most informative on the internet for UK householders.

Thank you

SWS

 


   
👍
2
Quote
Transparent
(@transparent)
Illustrious Member Moderator
12955 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 2278
 
Posted by: @southweststokie

Mains gas, leccy (80A fuse I think - Western Power are checking out) and that about completes the picture.

As you're with WPD I have the distribution network data for your area, including the sizes of cable and local substation information. I can't publish that on an open Forum of course. But I've been given access so that we can have discussions to resolve problem sites.

So once we can work out if you can Direct Message me, I'll stand-by to help. I'd need a post-code to start the ball rolling.

Even if your single-phase supply must be constrained to 80A max (which it might), this forum is discussing other possible ways forward using hybrid off-grid battery storage.

Have a look at the comment from @derek-m in the topic on New Valiant ASHP system in Scotland to get a glimpse where this is heading.

It would help if we also knew what the house offered by way of space for solar panels, both roof-top and/or ground mounted. Thanks.

Save energy... recycle electrons!


   
👍
2
ReplyQuote
(@kev-m)
Famed Member Member
5606 kWhs
Joined: 4 years ago
Posts: 1276
 
Posted by: @southweststokie

Southweststokie here, hello !

Sit rep - just started significant extension and refurb work on 50's house, and now getting more and more entwined into the whole heat pump debate etc as we get closer to selecting a system and then get it installed. Original house has just blown rockwool cavity installation - prob over 40 years old, but it's there - and a prior extension circa 20 years ago has high density insulation slabs in the cavity as deemed by regs at that time. New extension doing similar, though specs of insulation may have improved, and this will leave some, but not many older parts of the building still forming outside walls. Opting in final refurb phase to add further insulation from the inside for these areas. Loft on the 'add insulation' list as well. Hardwood double glazing throughout, but now needing attention to address issues inc leaky areas, doors etc. Underfloor heating throughout ground floor, but will be a mix of underfloor and legacy rads upstairs. Total annual KwH usage circa 37KwH (dual fuel), and new build will add circa 20% area, so with headroom, think we'll be heading for circa 45 KwH requirement. All in all, fairly representative of a house that must be replicated 1000's of times across the UK. Mains gas, leccy (80A fuse I think - Western Power are checking out) and that about completes the picture.

EV on order, though delivery will be god knows when - last I heard was Sept this year, and will be replacing the gas boiler with an ASHP. As much PV as we can put on the roof is the intent, and not now opting for solar water.

Being recommended a Daikin Altherma 3 H HT based system, and tenders are out for supply, fitting, etc. This is a High Temperature system, and is proposed as the right solution considering the full picture of the house.

Wanting to ask if anyone has experience of this specific ASHP, and to generally ask if there are an other considerations we should be taking in to account. Slight concern that the HT spec will mean higher running costs, but not sure how much. Daikin suggesting not much more the low temp but not quantifying currently. Believe Julian Clarke has one of these, but as a newbie, I can't message him directly -think that's how it goes. Hi Julian, any comments ?

Great site, has to be the most informative on the internet for UK householders.

Thank you

SWS

 

Hello and welcome to the forum. I have no experience if Daikin but hopefully Julian and/or others will help. will help.

How big is your house?  Do you mean 37-45 thousand kWh per year? That is a lot.  Is that from your EPC?  I think you'd have to have an unusually large and/or poorly insulated house to need more than 40 thousand kWh per year to heat it.  That would cost a lot whatever fuel you use. A proper heat loss survey will confirm though.  Some data below about average usage.

 


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
26280 kWhs
Veteran
Joined: 4 years ago
Posts: 2986
 

Welcome to the forums @southweststokie, and thank you for the kind words.

Julian is definitely your guy because he has a high temperature Daikin air source heat pump.

This is the interview with Julian where he discussed his system: https://renewableheatinghub.co.uk/homeowners-experience-with-a-daikin-ht-air-source-heat-pump

 

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote
(@heacol)
Noble Member Contributor
2477 kWhs
Expert
Joined: 4 years ago
Posts: 393
 

Hi Southweststokie, Heating your house will not be a problem with a heat pump if it is controlled properly.
I would open zone your ground floor allowing your heat pump to control your room temperature and install TRV valves on the upstairs radiators in the bedrooms and just lock shields on the rest. Seal your house as tight as possible and install these heat recovery extractor fans in the bathrooms, toilets, utility, and kitchen. ( https://www.blauberg.co.uk/en/blauberg-uk-mvhr-heat-recovery-ventilation-range/decentralised-single-room-heat-recovery-ventilation-units/blauberg-aeris-midi-decentralised-single-room-ductless-heat-recovery-unit-ventilator-wall-mounted-silent-heat-recycling-ventilation-filtered-fresh-a )These will substantially reduce your heating load.

If you control your house like this it will be comfortable and at the lowest possible cost.

High temperature unit enable you to supply a higher temperature to the heating system. At the same flow temperature, they are usually slightly less efficient than standard units as they are optimised for higher temperatures. However, they are not efficient at higher temperatures. Heat pumps are not gas boilers, there performance is not directly related to the flow temperature. Heat pumps move heat from one place to another (from low temperature to a high temperature (working against the laws of thermodynamics)) just like a water pump pumps water up hill (working against gravity). Think about it in a different way:- if you are required to carry 1 bucket of water per minute, up one story or 3 stories, moving it up one story is a leisurely task and requires little exertion, however moving that bucket up 3 stories will take significant effort and exertion. the stories is your flow temperature and the exertion is your electricity bill.

High temperature heat pumps are very expensive to run at high temperatures, it can but it is very inefficient. Another analogy is:- your car can do 130 mph but it will cos in more ways than one, if you travel at 60 mph, it is efficient and will last. It really is as simple as that.
Therefore, run your heat pump low and slow for long periods for best performance.

Solar thermal is an ethical decision if you install a heat pump and or PV. When the Thermal will supply enough heat for your water, your heat pump will have a COP of around 6. Therefor as Thermal will only supply 30% to 40% of your hot water requirement, it will take a very long time to pay it off. We do install solar thermal, but attach it to a ground source collector. This substantially increases the performance of a ground source heat pump.

 

 

Director at Heacol Consultants ltd


   
👍
2
ReplyQuote
(@cycleneil)
Estimable Member Member
714 kWhs
Joined: 3 years ago
Posts: 40
 

@heacol Hi Brendan, are there any more flexible versions of those Blauberg extractors? The house I am buying has ceiling-mounted extractors in the bathrooms that vent via flexible ducting  that passes through the attic space. Similarly, the kitchen extractor is the cooker hood that has hard plastic ducting running quite a way before reaching a wall. Only the utility room and small downstairs toilet have direct through-wall extractors where the Blauberg units would work in the way they show.


   
👍
2
ReplyQuote



(@southweststokie)
Active Member Member
142 kWhs
Joined: 3 years ago
Posts: 5
Topic starter  

@kev-m thanks for the reply. Will check my background data re current KwH's. Got me slightly concerned. It will be quite a big house, but not absolutely massive. Will be 5/6 beds when finished, but rooms aren't that huge. Based on my own records over the past 5 years, we've averaged usage as below

image

 Maybe this just shows how leaky we are currently.

 


   
ReplyQuote
(@southweststokie)
Active Member Member
142 kWhs
Joined: 3 years ago
Posts: 5
Topic starter  

@heacol Thanks Brendon. Our consultant is coming this week, and I'll flag those units to him.


   
ReplyQuote
(@heacol)
Noble Member Contributor
2477 kWhs
Expert
Joined: 4 years ago
Posts: 393
 

@cycleneil I have installed them into the loft with a flex pipe. Just make sure the flex is as short as possible and can collect and discharge in to fresh air. The longer the pipe, the worse the performance will be. I was involved with the developement of these units some years ago untill BRE refused to test them. They are over 85% efficient if installed through the wall.

I have 1 in my bathroom and have no condensation isses at all.

Director at Heacol Consultants ltd


   
ReplyQuote
(@cycleneil)
Estimable Member Member
714 kWhs
Joined: 3 years ago
Posts: 40
 

@heacol Very interesting. I could see that being extremely useful as full MVHR is just not practical without massive disruption.


   
ReplyQuote
(@kev-m)
Famed Member Member
5606 kWhs
Joined: 4 years ago
Posts: 1276
 
Posted by: @southweststokie

@kev-m thanks for the reply. Will check my background data re current KwH's. Got me slightly concerned. It will be quite a big house, but not absolutely massive. Will be 5/6 beds when finished, but rooms aren't that huge. Based on my own records over the past 5 years, we've averaged usage as below

image

 Maybe this just shows how leaky we are currently.

 

Well your gas is quite high but not extreme. Electricity is well above average for a gas heated home though. Worth a bit of investigation though.  What is the floor area of your house?

 


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
26280 kWhs
Veteran
Joined: 4 years ago
Posts: 2986
 

@cycleneil, excellent question and you’ve pretty much described our house room by room as we have the issues with extractors. I didn’t realise you get “heat saving” options.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote



Page 1 / 3



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security