Comparing COP (coefficient of performance)
I ran an experiment this week to see what our COP and electricity consumption would be like by varying flow rates (45C and 40C):Â https://myhomefarm.co.uk/air-source-heat-pump-cop
As the winter comes to an end, please share your COP figures for your systems. It should make for some interesting reading.
Buy a copy of the The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Hi Mars,
I suspect that the method being used to calculate COP in your system is not that accurate. I do believe that the MMSP system, even when correctly installed, is of the order of +/- 5% accurate. I don't think that any heat pump manufacturers system will come close to that.
Whilst electrical energy consumption can be measured with reasonable accuracy, to accurately measure the heat energy produced would require not only accurate temperature measurements, but also reasonably accurate mass flow measurement, which is not that easy to do.
Your tests proved what I think most people already know, that lowering the water flow temperature improves efficiency and reduces running costs. By using weather compensation this should be achieved automatically, without continual user intervention.
@derek-m, good points. Because we have a bivalent system, we've had to install two separate metres that are exclusively connected to our heat pump so that we can submit these readings to RHI on a quarterly basis to get our payments. I would therefore assume that the two metres provide us with two accurate data points: ASHP electricity consumption and ASHP heat generated. If it's of interest, I'll provide the names of both metres later this evening.
Buy a copy of the The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @editor@derek-m, good points. Because we have a bivalent system, we've had to install two separate metres that are exclusively connected to our heat pump so that we can submit these readings to RHI on a quarterly basis to get our payments. I would therefore assume that the two metres provide us with two accurate data points: ASHP electricity consumption and ASHP heat generated. If it's of interest, I'll provide the names of both metres later this evening.
Hi Mars,
I am assuming that an electrical energy meter was installed along with a heat energy meter. Did the installers provide any form of calibration certificates?
@derek-m, you always give me some very useful homework to do 😀. I have no idea whether they were calibrated and I don't think I have any certificates to this effect, but I'll rummage through the paperwork tomorrow. Failing that, I'll contact the installers and enquire. I'll also post some photos in the morning of the two metres. The one that registers heat generated is extremely helpful as it also keeps tabs on physical flow of water through the pipes, which I use regularly. We're now averaging 30 litres/minute on the ASHP which is good. When that drops, it's time to give the mesh filter a clean, but thankfully we've been running very clean of late.
Buy a copy of the The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
3 days ago
-
Rodents! A word of warning for heat pump owners
1 week ago
-
Retrofitting: moving to ASHP old oil boiler in large old property - experience/advice please on MSC calcs
2 weeks ago
-
How to choose Towel Rails for an ASHP
2 weeks ago
-
How to Zone with a Single Room with UFH
2 weeks ago
- 26 Forums
- 2,208 Topics
- 48.7 K Posts
- 67 Online
- 5,868 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Mitsubishi Ecodan F8 error
@hjd F8 is uncommon and could indicate incorrect heat e...
By ASHP-BOBBA , 10 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@papahuhu at the end of the day if you are happy with h...
By benson , 28 minutes ago
-
RE: Can you recommend a Mitsubishi service engineer in the Rochdale area?
@dgclimatecontrol We'll all need annual servicing. How...
By Suzy-shadow , 46 minutes ago
-
RE: Renewables & Heat Pumps in the News
@transparent I’ve understood your point now. The point ...
By Judith , 1 hour ago
-
RE: Octopus tariffs - a quick comparison
Does indeed need checking, @tim441. Neither Homely ...
By Majordennisbloodnok , 1 hour ago
-
RE: How not to install a heat pump
Delighted to hear that the buffer has been replumbed as...
By JamesPa , 2 hours ago
-
-
RE: Daikin 9kW to 8kW Swap Offer from Octopus
Yes but 9kW is similarly the 16kW derated. So 8kW subs...
By JamesPa , 4 hours ago
-
Actually, there's a rather greater degree of cattle-her...
By Majordennisbloodnok , 4 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@davidnolan22 So far as I can tell from the 'other p...
By JamesPa , 8 hours ago
-
RE: 5 Star Service from Havenwise
I keep getting havenwise ads on my Facebook feed, so cl...
By benson , 10 hours ago
-
Automation options to maximuse efficiency & ToU tariffs
I started a conversation with ChatGPT. What automation...
By Tim441 , 15 hours ago
-
RE: 4 Year Ongoing Heat Pump Battle With Poor Heat Pump Installation
@jamespa Oh, I know some that are good and some not so....
By ASHP-BOBBA , 20 hours ago
-
RE: Samsung Heat pump with Yonos Pico circulating pump running all the time
I don't know how many pumps you have but I guess it's o...
By JamesPa , 21 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
That's just human nature unfortunately, not special to ...
By JamesPa , 21 hours ago
-
@bontwoody how long has it been now since you started t...
By Mars , 1 day ago
-
RE: Bosch CS5800i 5kW - Experience So Far
Yes, over the last few days I've been keeping a very cl...
By Steelbadger , 1 day ago
-
Absolutely. I am one of those members and I most certai...
By Majordennisbloodnok , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@darrell-p There's another new Forum Member, @wully who...
By Transparent , 1 day ago