buffer/volumizer cupboard space eater, do i need one?
Posted by: @sunandair@heacol I’ve also herd that a volumiser can help with short cycling.
I wondered if short cycling would be reduced if it was caused by mild outdoor ambient circa 10c and a corresponding low flow temperatures and possibly insufficient radiator capacity at low flow temperatures…. Can you use a volumiser as a replacement for increased radiator capacity to reduce cycling? Eg. Flow temps down to 30c and rad capacity sized for 50c at -3c might not be large enough… as an example.
or is this just a red herring?
As you say, short cycling can occur during milder ambient conditions where the flow temps are reduced and the radiators/emitters then cannot dissipate the heat that is being produced. This causes the return temperature to rise (as the heat cannot be effectively dissipated into the property) thus narrowing the dT between flow and return. When this happens, the heat pump can cycle off to allow the water to cool and maintain a more optimal dT (somewhere in the controller logic the heat pump decides when dT drop below a certain value, the heat pump should cycle off).
Having a volumiser is not going to change the above fundamentals, as unlike a radiator it cannot dissipate heat (it's well insulated so it is reasonable to assume near zero heat loss relative to a radiator or other emitter). Consider it as simply a well lagged fat pipe, so there is more volume of water in the system. It may take longer to reach the initial point of cycling as there is initially more water to heat, so at best it may extent the periods between cycling (so short cycling now becomes longer cycling). Extending this premise, if the system volume were infinitely large, the return temperature would never rise to the point where the dT narrows to cause cycling, so there is a point of diminishing returns and as long as the system volume is large enough, then short cycling shouldn't be an issue. I do not know what this point is, but I have heard recommendations of having a system volume that is 3-4 times the recommended minimum system volume.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
Posted by: @old_scientistWhen this happens, the heat pump can cycle off to allow the water to cool and maintain a more optimal dT (somewhere in the controller logic the heat pump decides when dT drop below a certain value, the heat pump should cycle off).
Not sure this is precisely what happens or how the control loop works. What I observe on plots I have seen (including mine) is that the flow temperature rises above the set point (because the heat pump is putting in more heat than the radiators are emitting). Eventually the flow temperature exceeds the target + allowable hysteresis, at which point the heat pump will shut down. You could in fact restore deltaT by simply slowing down the water pump, but the flow temperature will still rise above the target value because the heat pump is putting in more heat than the radiators are emitting.
Posted by: @old_scientistHaving a volumiser is not going to change the above fundamentals, as unlike a radiator it cannot dissipate heat (it's well insulated so it is reasonable to assume near zero heat loss relative to a radiator or other emitter). Consider it as simply a well lagged fat pipe, so there is more volume of water in the system. It may take longer to reach the initial point of cycling as there is initially more water to heat, so at best it may extent the periods between cycling (so short cycling now becomes longer cycling)
Agreed, particularly with the sentence in brackets. A volumiser changes the period of the cycling but not the on/off ratio.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaNot sure this is precisely what happens or how the control loop works. What I observe on plots I have seen (including mine) is that the flow temperature rises above the set point (because the heat pump is putting in more heat than the radiators are emitting).
Here might be a case in point James.
Here are 2 hourly charts showing flow and return. These are supposed to be operating at fixed flow 34C and 35C respectively. They both have a little burst of temperature before closing down for around 4 minutes. I’ve always assumed this was a deliberate duty cycle function to bridge the shutdown temp drop… but it’s just a guess. There is no thermostat controlling, it’s just fixed flow. The room temp is close to 21 with an ambient of around4C last night and 9C for this afternoons chart
This 24 hour indoor/outdoor temp chart covers both hourly graphs above.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 58 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I doubt it, many 'improvements' are quite the opposite....
By cathodeRay , 2 hours ago
-
RE: Electricity price predictions
@julianc Expressed as a flow diagram, I suspect one wou...
By Toodles , 2 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
@jamespa The dormitories at my boarding school (in Exet...
By Toodles , 3 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
In the last week, the external temperature in south Man...
By GrahamF , 18 hours ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 18 hours ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 19 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 21 hours ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 22 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump Referring to the problem of rooms with diff...
By Tasos , 23 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 24 hours ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 2 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 3 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 3 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 4 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 4 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 4 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 4 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 4 days ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 5 days ago