Baxi Air Source Heat Pump tips and tricks please
The installation of my Baxi air source heat pump was completed yesterday.
The subcontractors who installed the system gave a very cursory overview before they left.
My supplier should be coming to see me to go over the workings of it next week.
Here is the schedule on the thermostat. Does this look ok to you or should I change anything? Many thanks for any advice.
@cathyem1 - welcome to the forum.
Posted by: @cathyem1My supplier should be coming to see me to go over the workings of it next week.
It might be sensible to wait until after this visit - the supplier could just as well get things right or wrong! However, in preparation for the visit, it won't do any harm to mention some basics.
1. You do not want to use a room thermostat to control the heat pump (yes, the subcontractor got that wrong). You want the heat pump to be always on, which means setting the room stat very high - say 28 degrees all the time.
2. The control comes from something called weather compensation. Basically this controls the temperature of the water leaving the heat pump according to the outside air temperature. When it's cold outside, you need more heat, so the LWT (leaving water temperature) goes up, when it's milder you need less heat, and the LWT goes down.
3. You then aim to get the weather compensation settings such that they are at the lowest LWT consistent with keeping your home warm. This is a trial and error process: you start with some initial best guess settings, and watch happens. Home too cool? Up the weather compensation settings a bit, and see what happens. Home too warm? Lower the weather compensation settings a bit, and see what happens. Carry on until you get it just right.
4. The ease of setting the weather compensation settings varies with heat pump brand. If you have a manual (or can find one online) it should tell you how to adjust the settings. Your supplier when he visits should also be able to show you how to set them. Normally there are two pairs of settings, one for low outside air temperatures eg 45 @ -2 which means LWT at 45 degrees when it's -2 degrees outside, and one for high outside air temperatures eg 30 @ 15 degrees which means LWT at 30 degrees when it is 15 degrees outside. In between these outside air temperatures, the weather compensation operates on a sliding scale between the lower and upper outside air temperature end points.
5. You also want to mostly run the system as 'open circuit' as possible. What this means is no obstructions, specifically no TRVs (to start with, occasional bedroom use may be OK once you have the system set up).
That may all seem rather daunting if you are new to heat pumps, but it basically the bread and butter of how we run them. Always on, low and slow, with control coming from weather compensation.
Good luck, and let us know how you get on!
Midea 14kW (for now...) ASHP heating both building and DHW
That's the sort of schedule we'd expect to see for a typical gas boiler installation @cathyem1
but it doesn't best reflect how your heat pump should operate.
It is a requirement of the Building Regulations (Part-L) that you are supplied with site-specific documentation,
and instruction on how to operate the system such that the (electricity) fuel being used is minimised.
Ie, that's the definition of an efficient heating system.
Simply handing you the manufacturers' instructions for the heat-pump, thermostat, and domestic hot water (DHW) cylinder is inadequate to comply with Part-L.
You should have the system diagram for your particular house, and the Commissioning Procedure sheet, with the results for each of the 'tests'.
That will include the settings which the contractor arrived at to optimise the system.
You should have already received the Household Energy Survey report, which was completed prior to installation.
That gives you the design parameters which were used to dictate which specific hardware was required for your home.
It will show the total energy losses for the entire house, which are used to decide the size of heat-pump required (in kilowatts),
and the losses for each room, which dictates the size of radiator required, and the size of pipework to deliver that heat.
Can you also please tell us the model of Baxi which has been fitted?
and basic description of your house
- when it was built
- detached/terraced etc
- number of floors
- number of bedrooms
- floor area in square meters (or any other units, and we'll do the calculations for you!)
- what insulation is in the attic/roof, and the walls
Looking forward to helping you get this sorted. 🙂
Save energy... recycle electrons!
@transparent Thank you. We did receive a lot of information from the supplier after he did our survey with all the recommended specifications for the new system.
I have been told today, after emailing and texting the supplier about my issues with the system, that their “process” is to send out a handover pack which will include the warranties, certificates and manuals in due course. They will come to see us and talk through the system sometime next week. I wasn't aware of this when the subcontractors left yesterday.
As an aside, I also have solar thermal water heating which was fitted a few years ago, so our cylinder is dual coil.
House is a semi that was built in 2005
2 floors and 2 bedrooms
Floor space is 71 m2
The loft has 200mm of fibreglass insulation that was in when we bought the house new in 2007.
The walls have insulation built in.
The heat loss is noted as 2.74kw on the heat loss report and system design.
The heat pump is a Baxi HP40 Heat Pump air/water “inverter” and the cylinder is a Cyclone 180l dual coil.
That's interesting @cathyem1
Many installers don't like reconnecting an existing solar-thermal to a newly installed heat-pump system.
It can be more tricky to commission.
The Baxi controller needs to 'understand' that the energy being supplied from the solar-thermal coil might be greater than its own flow (output).
But let's note that it's only feeding into the Domestic Hot Water tank.
There's no solar-thermal gain supplying the radiator 'space'-heating element of your installation, which accounts for 80% of your heat requirement.
Save energy... recycle electrons!
@transparent Thank you, yes, I realise that the solar is only helping the hot water and not the heating.
I really hope the supplier comes to see me on Monday as my bill is rising and rising and i don’t know what to do about that other than turn the thermostat own or switch the system off 😬
I suspect that the heat-pump is 'cycling'.
Ie it's switching on/off every few minutes in response to temperature sensors.
If you have Thermostatic Radiator Valves (TRVs) then these need to be fully open.
They're not required for heat-pumps and shouldn't be fitted.
Radiators should be 'balanced' by the installer, using the lockshield valve on the other end.
Only then might you achieve any 'success' by reducing the 21°C setting on the main controller.
Do have any other large 'tank' installed?
It might be called a volumiser or a buffer.
Save energy... recycle electrons!
@transparent I have controls at the end of each radiator but they just look like my old radiator valves. They are all fully open.
I have several other tanks. One in the loft and two in the airing cupboard. See the attached photos,
@cathyem1 - do you happen to know if Baxi is a Midea clone? The reason I ask is the first photo of your wired controller looks very like a Midea controller. If it is a Midea clone, there is a lot more known about them than Baxi.
From the controller I can see the OAT (outside air temperature) is 5 degrees and also rather interestingly you may be in a time warp (2016)!
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay Haha! Yes, the current date needs to be input.
I don't know about Midea I’m afraid.
What sort of temperature should my system be showing overnight?
Posted by: @cathyem1What sort of temperature should my system be showing overnight?
There are lots of temperatures! The key space heating ones are outside air temperature (as seen on the display, by the house icon), leaving water temperature (temperature of the water as it leaves the heat pump) and returning water temperature (some thing for return). These can be viewed on a Midea controller and very likely clones (I am pretty sure it is a Midea clone from the appearance). The display can be confusing at times to say the least, especially the space heating panel on the left hand side. Try unlocking the keypad (long press on the padlock symbol, padlock top left of display should disappear then press Menu repeatedly to see if you can find OPERATIONAL PARAMETER, if you can, select it and go to page 3 of the operational parameters and if possible take a photo of it and then also take a photo of page 4 of the operational parameters and post them here.
Midea 14kW (for now...) ASHP heating both building and DHW
- 21 Forums
- 1,985 Topics
- 43.3 K Posts
- 40 Online
- 2,311 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
Dont worry about this. Long story and discussion but d...
By JamesPa , 42 minutes ago
-
@eliuccio I was wondering how things are going with t...
By JamesPa , 57 minutes ago
-
RE: Database of heat pump performance data?
You could try/p> BUT i spent ages on it before real...
By Judith , 2 hours ago
-
😆 I would have been tempted to see how good the...
By Mars , 11 hours ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
No not auto adapt running hotter at cheaper times coole...
By Gary , 12 hours ago
-
RE: Ecodan Auto Adapt Questions
Hi @richard24738 we weren’t happy with our FTC Contr...
By SUNandAIR , 12 hours ago
-
RE: To relocate or add extra PV panels..advice required
You can't forecast the annual generation by simple extr...
By JohnR , 13 hours ago
-
@toodles whilst I agree with toodles the actions he de...
By Potatoman , 13 hours ago
-
RE: Plug and play solar. Thoughts?
They are 'exporting to the grid' within the EREC defini...
By Transparent , 14 hours ago
-
RE: Are MCS are finally improving (some of) their guidelines?
@johnr I think OE argue that the lower running costs as...
By Toodles , 15 hours ago
-
RE: Additional Battery v Wind Turbine v Ripple
@lucia Yes, that is the response to which I referred ea...
By Toodles , 16 hours ago
-
RE: Is it worth siting panels on an East facing roof?
Yes. Thanks all. I have used the guides and have found ...
By Carpenterstation , 1 day ago
-
RE: The EPC Dilemma: How Current Ratings Fail Heat Pumps
I've commented earlier in this thread, finding the same...
By Mike Patrick , 2 days ago
-
RE: SolarPV tables / online calculator
This guy did a good analysis in summary go down a...
By Judith , 2 days ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@dnagre delayed reply! It worked again for a bit but ha...
By Phoenix15 , 2 days ago
-
RE: Vaillant Arotherm Plus - new build no heating, no radiator
@john1756 did you ever get to the bottom of this?
By Mars , 2 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
We tested the away mode for the first time as we were a...
By ChandyKris , 2 days ago
-
RE: Confused about Samsung Gen6 Hot Water Controller
Found a copy on this really good website 🤣 ...
By DerekDeLeon , 2 days ago
-
RE: Smart TRV experiences (ideally integrating with Midea heat pump)
@madbilly - I think you may risk over-complicating this...
By cathodeRay , 2 days ago
Latest Topics
-
Plug and play solar. Thoughts?
By Lucia 3 days ago
-
By JamesPa 3 days ago
-
Vaillant water pressure gauge vs Analogue gauge
By jeegnesh 3 days ago
-
Database of heat pump performance data?
By madbilly 3 days ago
-
By madbilly 3 days ago
-
Confused about Samsung Gen6 Hot Water Controller
By ntruby 4 days ago
-
help with new bathroom and towel radiator
By AdamK 5 days ago