Is this a bad installation and is there something wrong with my Samsung heat pump?

360 Posts
15 Users
89 Reactions
10.4 K Views
(@ant87)
Eminent Member Member
116 kWhs
Joined: 11 months ago
Posts: 16
 

@david999 out of interest what was the heatloss figure for the property?

46lpm is correct for a 16kw heatload, however the Samsung can only output around 12.5kw at most design conditions so is not as black and white as Samsung would make out.

Did you sort your defrost issue I have seen in older posts?


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
17915 kWhs
Veteran
Joined: 3 years ago
Posts: 2389
 

@david999 I asked a few installers to look at your question regarding pipe sizes. The general consensus is that the length of the primary pipes from the heat pump to the system is crucial, as pressure loss is the main concern. A 35mm pipe results in a flow velocity of about 0.9m/s with a pressure drop of 320Pa/m, which can accumulate with other components. If the circulator doesn’t have enough residual head to meet the system's needs, you might need to use 42mm copper pipes and increase the size of some secondary pipes, or consider a circulator with a larger head.

From our personal experience adding more pumps (and more powerful pumps) adds covertly to running costs, and it can make the system noisier as the majority of these pumps will be indoors.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk


   
ReplyQuote
Transparent
(@transparent)
Famed Member Moderator
8840 kWhs
Veteran Expert
Joined: 2 years ago
Posts: 1464
 

@david999 - since you need this information in order to decide whether to challenge your installer, I think you'll need a regulation/directive that you can point to.

Part-L, sect-8 of the current Building Regs provides you with a valid foundation on which your argument can be based.

Part L8a

As @editor has stated, under-sized pipes cause greater pressure loss. That can be compensated for by using more powerful pumps (or running a pump at a higher velocity), but that uses more electricity. It's that additional electrical energy which reduces the overall efficiency, and hence fails Sect 8.1

I will also add that elbow bends cause significant pressure loss. Newton's 1st Law of Motion states that an object will remain at (rest or...) a constant velocity in its direction of travel unless an external force acts on it. The tighter the angle of a bend, the more energy is required to change the direction of a given mass of water.

Swept bends (long radius) are preferable to tight right angles.

image

Bends formed by using a pipe-bender on a straight length of pipe are better still.

Everything about the design of a heat-pump installation must be founded on the principle of it using as little energy as possible.

 

Save energy... recycle electrons!


   
Mars and Derek M reacted
ReplyQuote



(@david999)
Reputable Member Member
753 kWhs
Joined: 3 months ago
Posts: 166
Topic starter  

@transparent thanks for that, at the minute since they moved a pump to the correct location its chucking up e911 error codes and since it’s warm outside I think it’s only when it gets chilly and it tries to heat the house. 

samsung was talking to me initially and I made no mention of my installer but now since my installer got involved with samsung they won’t discuss anything with me. 


   
ReplyQuote
Transparent
(@transparent)
Famed Member Moderator
8840 kWhs
Veteran Expert
Joined: 2 years ago
Posts: 1464
 

Well your contract is with the installer, so the withdrawal of Samsung from direct discussions with you simply puts more pressure on him.

If he can't resolve error codes and malfunctions which are possibly related to external temperature, then it's he who should be requesting help from Samsung Tech Support.

Should there be a dispute which comes down to arbitration under the Consumer Rights Act, the less communication you've had with Samsung, the better.

Save energy... recycle electrons!


   
ReplyQuote
(@david999)
Reputable Member Member
753 kWhs
Joined: 3 months ago
Posts: 166
Topic starter  

@transparent thanks for that, I fear I have a long way to go yet but if installations like this are the norm then MCS will need to step up to the bar or step down and have someone like building control regulate it.  My installer took numerous photos during and after and my impression was that these went to MCS for review as you do with building control. But if so then it was so obviously installed badly that it would have been noticed and no commission report was ever completed which I would have thought mandatory. 

perhaps the governments necessity to meet targets means they lower standards, or my installer sent other photos.  

I suspect it was all meant to be run in copper, and perhaps I’m wrong but I thought it strange they ran it in plastic then the areas visible in copper. Plastic is generally frowned on in that the inside diameters are much smaller and more friction, and flow is everything with these pumps. 

how hard it it to get this right. 


   
ReplyQuote
Transparent
(@transparent)
Famed Member Moderator
8840 kWhs
Veteran Expert
Joined: 2 years ago
Posts: 1464
 

MCS is the delivery route for Net Zero oriented technologies favoured by BEIS/DESNZ.

Ofgem is a non-ministerial Government Department... which is a problem,
... but they've have just authorised the formation of the new Independent System Operator and Planner (ISOP) with its main remit being to "reach Net Zero by 2050".

ISOP is recruiting engineers from National Grid ESO and the GDOs of very great experience.
These guys could actually get us to Net Zero faster than 2050, provided that

  • the strategies are based on the laws of physics rather than government favour
  • the community sector (us consumers) get inspired and mobilised to play our part in the Future Energy Scenario (diagram below)
  • we reverse the trend for private companies with foreign shareholders to 'invest' in the UK's energy future
FESdiag shaded

If MCS doesn't fit within the energy strategies wanted by the next Government, then it will either be required to change, or it will be axed.

I'm busy communicating with PPC (Prospective Parliamentary Candidates).
To get elected, they need to informed (by us) of what's happening and how to solve it.

My message is that they must reduce the politicisation of energy, and instead embrace the physics.
It's being well received.

MCS' days of unenforced 'standards' are numbered.

This post was modified 1 month ago by Transparent

Save energy... recycle electrons!


   
ReplyQuote
(@david999)
Reputable Member Member
753 kWhs
Joined: 3 months ago
Posts: 166
Topic starter  

@ant87 I don’t have the heat loss figures or the design figures for the system, I asked several times but no reply


   
ReplyQuote
(@ant87)
Eminent Member Member
116 kWhs
Joined: 11 months ago
Posts: 16
 

@david999 if it's an MCS registered install you must be given a copy of the heat loss calculations which should be your starting point.

29lpm is roughly around 10kw with a DT5, if the heat loss is less then 35mm could be considered overkill and it's the heat pump size that's questionable. Any more than 11kw and you would really need to be at 35mm (or more dependent on index circuit pressure drop etc.). And ofcourse remember your heat pump is not capable of 16kw at design temperature so I'm not sure it could handle 45lpm @ DT5. I think it would max out at around 36lpm.

I was speaking to a homeowner not long ago and a 12kw was installed,  Samsung stated it needed 35lpm to operate... however the house heat loss was only 6kw... and so needed around 18lpm (hence why the house was never cold but the heat pump cycled all year round).

With the heat loss calcs you can the determine flow/pipe size/heat pump size etc. Etc. It might be worth having a quick go yourself if you are unable to get them from the Installer, I know there's quite a few excel sheets available on here.

 


   
ReplyQuote



(@david999)
Reputable Member Member
753 kWhs
Joined: 3 months ago
Posts: 166
Topic starter  

@ant87 thanks for that.


   
ReplyQuote
(@david999)
Reputable Member Member
753 kWhs
Joined: 3 months ago
Posts: 166
Topic starter  

@ant87 I have asked a couple of heat pump suppliers, both with a tech department what components I need to convert my 28mm pipes to 35mm and they have come back saying they can’t supply and don’t know anybody who could.  If you are selling 14 and 16kw ASHPs then how can that be so. Perhaps we are ahead of ourselves in terms of this tech.


   
ReplyQuote
(@ant87)
Eminent Member Member
116 kWhs
Joined: 11 months ago
Posts: 16
 

@david999 Hi David, sorry I'm not quite sure what you mean? Heat pump systems can go into 100's of kw, even megawatt systems.

If your heat loss is infact "12kw say" then it might be that your primary pipework would need increasing to 35mm (or more) which would mean 35mm copper, maybe swapping the 3 port valve for an ESBE or a Belimo valve. This is all to reduce velocity and reduce the pressure drop across the index circuit, increasing flow rate.

The likelihood hood with most Samsungs is that the primary pump is too small with most being installed on a 15/60 pump. There are installers who increase the primary pump size but you are limited to around 100w, adding an additional pump on the return to increase head OR using a relay and a larger pump.

This is all dependent on the heat loss of the building which will determine your flow rate required to deliver said heat. And the flow rate determines velocity, pressure drop and so on. 

Your velocity should be around 0.9m/s but can be upto 1.5m/s which is the maximum. With modulating heat pumps this varies wildly dependent on load and is always changing, with Samsung it's fixed unless you use their PWM signal (although I am under the impression it only works when the flow temperature is above 45degC but might be wrong).

The only way to determine all of the above is via the heat loss calculations and working from there, theoretically your 16kw Samsung can only deliver 12kw, the heatloss might only be 10kw and so 28mm would be OK... however the pump needs increasing.

Equally due to the small pump it might mean that you need 42mm to reduce pressure drop thus increasing flow rate, however both giving the same end result but in a different way. A pump would likely be far easier to change, but could cost you a small amount more in electricity.

If the heat loss was infact a theoretical 14kw, your velocity would be around 1.25m/s on 28mm copper, however the pressure drop would be very high, so 35mm would be the better solution as the pump would be huge 🙂

 


   
Transparent reacted
ReplyQuote