ASHP & UFH
Hi all. In the early stages of looking at replacing our oil combi with an ASHP.
One thing I've noticed is the front of our house gets a lot of solar gain and can be approx 3-5⁰ at least warmer then the rooms in the rear. However 1 of these rooms is above an unheated area (garage) so then struggles to get up to and maintain temp when the sun goes down.
Anyone have any ideas on what could be done here?
For reference the first floor is renovated with UFH at 135mm centres and is zoned. Floor finish is carpet, which with underlay is circa 1.8-2tog.

It's easy to say that suggests you need some insulation between your garage and the room above it. What would probably be more sensible is to prove it. I'd say it's worth you getting hold of a thermal camera (hiring is fairly reasonable, I believe) and see where your cold spots are inside and out. We actually bought one so we could lend it out to friends and family too, but when we did it provided some surprising results.
Things we thought would be a problem were in fact fine and one thing we didn't even think of (our front door) turned out to be abysmal. Sorting out what we found before getting heat pump people in to look around and quote turned out to be a REALLY good investment.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; suus solum profundum variat"
Thanks for the reply.
I do have a thermal camera so will get some images with it.
The room has 1 external wall which now has beaded CWI installed. The window in that room has been replaced with a new aluminum framed double glazed unit which has been installed with compriband/foam and membrane.
2 internal walls have rockwool in, more so to reduce noise transfer. The UFH sits on 100mm PIR.
The remaining internal wall is a block wall dividing us and our neighbour (semi detached property).
And finally above the room is 300mm loft insulation.
Always worth insulating the floor from the garage underside if there's reasonable access. If you store much in there, including cars, I would fire proof the floor as well. Inert mineral wool or non-flammable insulation combined with 13mm dry lining + skim or 2x13mm staggered joints would work. Cost is minimal for the thermal and safety benefit it will bring.
Ground floor heating distribution can be compensated for with larger or additional rads, not quite so easy if already UFH. If you have UFH with an oil boiler you'll probably be heating water up way beyond the temperature you need under the floor, and then blending it back down with mixing valves or a manifold. That's thermodynamic lunacy and very wasteful. Older boilers often have a minimum leaving water temperature and can't be set to a suitably low temperature to avoid blending with cooler water for UFH. An ASHP would heat the water to the flow temperature needed automatically compensated for outdoor air temperature.
The 135mm crs could be problematical for a lower UFH supply temperature, but an experienced designer would advise on that. With a reasonably insulated home, say EPC C, you don't want to be designing an ASHP for any higher than 45degC maximum flow temperature. Ideally nearer to 40degC with UFH. Ditch the zone controls, ditch all the blending valves, upgrade the rads where needed, insulate whatever you can, fit an ASHP on open circuit control properly designed and installed, and you'll not regret it.
hi and thanks for the reply.
So the floor in that problematic room has 100mm PIR underneath already. I can get access and will add as much as possible extra.
Ground floor is being renovated starting next month and plan here is to have the existing slab taken up, and dug down enough to install 200mm PIR, then UFH stapled to that (100mm centres), then 100mm concrete. Finished floor here will be tiles.
At present we only have heating on the first floor (UFH) and the oil combi works for that via a buffer. This is just to reduce the short cycling of an on/off oil combi. And yes at present the heating water is taken from that and blended down.
Aim is with an ASHP installed, we'll get rid of the blending valve and have the temp set by the ASHP via WC.
Also at present it's zoned but with the ASHP I'm hoping this is gone and it's just run as a 1 loop over both floors.
I know the house didn't have an EPC of C when we purchased in 2019 but it hasn't taken into account any of the new work.
Posted by: @valaI know the house didn't have an EPC of C when we purchased in 2019
Great stuff - sound like to you a very good plan. EPCs can be notoriously inaccurate. It was only until quite recently the installation of a heat pump could actually make an EPC score lower due to the absurd way EPC SAP software used to consider ASHPs as direct electric heating with 100% efficiency. They finally fixed that, not before time.

Posted by: @vala...
I know the house didn't have an EPC of C when we purchased in 2019 but it hasn't taken into account any of the new work.
...
Just to say that we bought our house with an EPC banding of D. It now has a banding of B and is within spitting distance of an A.
As @allyfish has said, EPCs are notoriously unreliable, being largely at the whim of the assessor who is trying to shoehorn what they've discovered into box-ticking forms. Nonetheless, if you ignore the rating itself and look at the areas being assessed it's not a bad checklist of stuff to consider.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; suus solum profundum variat"
@majordennisbloodnok We received a rating of C (72) with potential to be a B (83) if fitted with solar water heating and 2.5 kWp. of PV panels. We have more than done this with 8.1 kWp. of PV and of course, we have fitted an ASHP, battery and so forth. I think that by that means of assessment, we are now an A. They did not even allow for under-ground floor insulation at all. Regards, a smug Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
So just to update this thread, we have a HG coming over next week to complete a heat loss survey. I don't know/doubt if they'll spill the beans on how to get the house heating up to the target temp, in all rooms, with it all being on 1 loop. What puzzles me here is I'd assume they'll use the Vaillant controls such as the sense comfort, however this surely will have a thermostat in it and will shut off the heating once this hits target temp. And in which case, how can I be sure that the problematic room on the first floor is also up to temp?
Does anyone have any ideas?
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 58 Online
- 2,277 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 2 hours ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 2 hours ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami I think if the heat loss documentation matches a ...
By bontwoody , 2 hours ago
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa I'm afraid that's over my head but if anyon...
By IRMartini , 3 hours ago
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 3 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 3 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 5 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 7 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 9 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 21 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 24 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 9 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 10 hours ago
-
SolarPV tables / online calculator
By MichelleC 17 hours ago
-
By Toodles 2 days ago