@clairelp finally I can see that you have a volumiser, not buffer setup. So there should be not extra pumps on the system. The pump built into the Daikin is quite strong, I can't see a bypass (but it's hard to tell with the quality of pictures)
This is what they look like, it maybe in the airing cupboard, do you TRVs on every radiator.
Does the noise stop when doing hot water.???
Technical Manager & Professional Installer: Ultimate Renewables
@clairelp I'd expect the primary pipes - which is the ones that connect your heat pump to to the volumiser, to that black and red Esbe valve, and to any manifolds or branching off in your cupboard, to be at least 28mm diameter. From the pictures it looks like they >may< be 22mm? It's hard to tell though.
Apologies - I've forgotten the output of your heat pump..... There's a limit to how many kWhs you can get down each diameter pipe to not go over 0.9 - 1m/s velocity. For 22mm the limit is around 6kW. For 28mm it's more like 10kWh. * Could you please check what the diameter of the pipes going to your volumiser are please? The volumiser is the small gray tank thing in the attic.
Did you then say that each pipe heading off around the house is 10mm? You can get around 1kW down each one of these to not go over 0.9 - 1m/s velocity.
The reason you would want to keep to that velocity limit is it tends to get noisy above it. Also much above 1.5 and it starts to erode the internal of a copper pipe.
As Ken and others thought previously the pipe clips attach the pipe directly to the wood in your attic. An alternative would be to use a clip that goes to the outside of the insulation material. There is a brand called "Primary Pro" that is a favourite with heat pump installers. As you have a cold attic I'd advise consider this a cold space and upgrading the insulation up there - you'll save money in the long run.
Ken's suggestion to check the air vent is a good one too.
*These numbers assume you have glycol in your system, and that the dT of your heat pump is 5. dT means the delta T - it stands for the temperature difference between the hot pipe from the heat pump and the cold one. Delta means "difference" in Latin. As dT increases you can get more and more heat down a pipe within that velocity limit.
Sustainable Groups - Renewable Heating - Co-founder of Firepower. Book a one-to-one consultation to discuss your heating and sustainability here.
Technical Manager & Professional Installer: Ultimate Renewables
Hi, we not had chance to get in the loft to look at the valve yet, difficult to go up in loft making noise when children asleep in the evening.
I did look at pressure gauge in cupboard and it about 1.6.
Friday installers are coming so I will keep you posted. We also have installers msc compliance department checking the install following week. Hoping they will have an answer 🤞🙏
the ashp does have anti freeze valves, with it not been below freezing hoping be okay to keep turning off for a couple of nights.
also looking into sound proofing and insulation for the loft.
Hi,
Installers, have turned down the velocity to I think he said 21-22 and was previously 24. Think he said in the bypass valve. And I sorry can’t remember exactly but I think he said like it around 21 and maybe 24 was making too much noise.
At moment, I don’t think I could hear it and running quieter, it’s only just done so I will test it later when doing hot water and have to wait for a cold night.
🤞
They also did some settings on the frost cycle. They said it shouldn’t be coming on when not cold enough and shouldn’t be constantly going. Said there is two defrost settings one I think he said for the pipes and one for actual pump. They said if changes didn’t help they will contact Daikain, as some setting they can’t change.
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 25 Online
- 5,656 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Anyone still weathering it out with Agile?
Yes, but now try finding a working phone box….
By Majordennisbloodnok , 4 hours ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 7 hours ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 12 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor @sandy I tried contacting them via Whatsapp b...
By brad , 1 day ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 1 day ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist I have never cleaned the mag filter myse...
By Toodles , 2 days ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 2 days ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 2 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 4 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 4 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 5 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 5 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 5 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 6 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 6 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 1 week ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 1 week ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago
Members Online
No online members at the moment