Vaillant Arotherm ASHP gets noisier when it gets colder outside
Hi there,
I recently had a Vaillant Arotherm installed and I'm finding when it's cold, the heatpump is very loud. Like around 70db (according to an ios app). It's barely noticable when the outside temperature is a bit higher.
Originally myself and the installers thought that it could be a fault but a Vaillant engineer came out and said he couldn't find any issue with it.
Is anyone able to help me understand why that is? Is it normal? Anything that can be done about it?
Thanks in advance
I have a vaillant arotherm plus too 10kw. Mine gets more audible as well when it’s colder outside. Can’t be heard from inside the house, only when I’m outdoors near the pump.
It’s my understanding that most if not all heat pumps are the same.
Appreciate this is an old post but I’m experiencing the same thing in the current cold snap. At freezing temperatures, my Arotherm Plus 7KW unit makes a sustained loud buzzing noise. I measured this at about 65db and it’s audible inside the house. The buzzing is not audible during regular operation and is definitely not the unit entering defrost. Annoyingly however it doesn’t do this all the time. It is well above the stated noise levels for the unit so I’m assuming it is a fault…? Anyone else experiencing this? Thank you.
@tallmarc stated noise levels are made at a defined outside temperature not the worst case which is what we currently have in the depths of winter, mine is equally noisy at sub zero temps as its working flat out 24/7, I would suggest its probably performing normally they are just noisy in winter, they are especially noisy if just turned on and are trying to get the water up to set temperature same after a defrost for the same reasons.
Our 10kW Grant Aerona also gets noticeably louder when cold. There's a few reasons why:
1. The ASHP is working very hard, the compressor frequency is very high nearly all of the time. That creates more noise and vibration. It also tends to cause other things such as panels, grilles and covers to rattle in sympathy. ASHPs are built to a price, there's acoustic lagging around the compressor, but not on the cover panels or other sheet steel that can start to vibrate.
2. The evaporator coil is icing up. That increases the velocity of the air through it, which makes more noise. The fan is trying to move a large volume of air through very narrow gaps that are increasingly restricted by ice.
3. Sound travels further in colder weather than warmer weather. It's just one of the quirks of the physics of sound.
Last night was the first time my wife complained to me she could hear our ASHP from the bedroom, keeping her awake. The unit is one floor below and the other side of a cavity wall stone & block wall. I could hear it too. However, now the cold spell has ended we'll revert to switching the unit off 9pm - 4am and hopefully that'll be the end of that conversation 😉 It was running 24/7 last week while temperatures never rose above freezing point.
Posted by: @gemiarI have a vaillant arotherm plus too 10kw. Mine gets more audible as well when it’s colder outside. Can’t be heard from inside the house, only when I’m outdoors near the pump.
It’s my understanding that most if not all heat pumps are the same.
My 7kW Arotherm does the same. Its especially noticeable during recovery from defrost, when the compressor is going at 100%, and at this point its has a tonal component and is just slightly annoying. Fortunately defrost recovery is 5 mins once per hour or thereabouts. A near neighbour of mine, with the same model, reports similarly.
Turning on NR mode kills the noise, but also compromises recovery performance too much. Obviously limiting compressor modulation to only 60% (which is what NR does) is going too far. I have tried reducing 'max compressor current' from 16A (the default) to 13A (the minimum available), which appears to reduce the max compressor modulation to 90%. This makes quite a difference and almost fixes the problem without materially compromising defrost performance.
Unfortunately there doesn't seem to be a way to adjust the max compressor modulation to somewhere between 90% and 60%. I have a suspicion that ~85% would do the job, but that option isn't available (unless I have missed something).
I have actually just asked Vaillant about this and will post any response.
My heat pump is surrounded on 3 sides by hard surfaces and I think the tonality might actually be a resonance effect. The distance between two of the surfaces (which are parallel to each other) is exactly twice the wavelength of the principal tone - a bit suspicious to say the least. I'm trying to find a reasonably priced sound absorber (it needs to be an absorber not just a barrier) with a tolerable appearance suitable for outdoors. Solflex (solflex.eu) do something which appears absolutely perfect and will ship to anywhere in the EU, which is not helpful! I have yet to find an equivalent product available in the UK.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa nice analysis
or neoprene?
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
@gary This was at -1.1 so not a particularly taxing operating temperature. The pump was also heating the house at the time, not defrosting or heating the hot water. It made enough noise to be heard in two rooms away through the double glazing.
I am a bit shocked as one of the myths that I have tried to counter when showing people the pump - I support the Nesta Visit-a-heat-pump scheme - is that heat pumps are noisy. It usually isn't but it now appears that, unless faulty, the Arotherm Plus sometimes it operates at a much louder level than the stated specifications suggest.
Posted by: @judith@jamespa nice analysis
or neoprene?
Thanks for the suggestion.
This appears to have a solid shiny surface and be designed to reduce transmission. I think what I need to do in my situation is reduce reflection, which needs a broken-up surface. I dont think either this or neoprene this it the right product in the particular use case I have (and am loathe to buy and install until I have reasonable confidence it is).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I suspect it’s not reflective to audio waves and rough surface matting is available too. Patterned door mat perhaps ☺️
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
Posted by: @judithPatterned door mat perhaps ☺️
Quite possibly. As I mentioned above the 'ideal' product seems only to be available in the EU. There is a UK product which looks like grass, (and therefore also like a door mat) which I could believe might work. Much more expensive than the EU product though. Still looking.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Googling noise with ashps and found this technical document https://www.apexacoustics.co.uk/wp-content/uploads/2023/10/NOISE-FROM-ASHPS-WHAT-WE-KNOW.pdf#page5
it identifies several noise related issues
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
- 22 Forums
- 2,058 Topics
- 44.9 K Posts
- 14 Online
- 3,308 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
This is indeed welcome news. In addition the new legi...
By JamesPa , 1 hour ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
On our original boiler install, I did have a 140L buffe...
By Johnmo , 10 hours ago
-
RE: Is your heat pump insured?
@benson fairly typical of some insurers.
By KevinPotts , 12 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@majordennisbloodnok I am wearing a glazed expression n...
By Toodles , 13 hours ago
-
RE: Rate the quality of your heat pump design and installation
Yes the HP is running weather compensation and I’ve lef...
By Davesoa , 19 hours ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
OK, so when the HP comes on it becomes obvious.It's on ...
By tdudgeon , 1 day ago
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
@johnmo I think we’ve been trudging through the same...
By SUNandAIR , 1 day ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 3 days ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 3 days ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 3 days ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 3 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 3 days ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Hopefully iv done the right thing today by signing up t...
By Westkent , 3 days ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 4 days ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 4 days ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
The useful bit is the bit that specifies the heat loss ...
By JamesPa , 4 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 4 days ago
-
@editor thanks Mars that’s the same table I found in th...
By Gary , 4 days ago
-
RE: Tariff and charging strategy advice please
They haven't asked me to prove that I have an EV (I do)...
By JamesPa , 5 days ago