Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Are antifreeze valves essential for a glycol free ASHP system?
During a recent upgrade to my 12kW Samsung ASHP set up, the glycol was removed as requested. I expected one or more antifreeze valves to be fitted, but I was told on good authority that these were not required. So I wondered if anyone had any views on the pros and cons of fitting antifreeze valves? If fitted, is one on the return flow sufficient or should there be one on the leaving flow too? Is anyone in the same position, having no glycol and no antifreeze valves?
I must admit to feeling a little anxious when all occupants of our three terraced cottages were away at the same time after Christmas, when it went very cold and any power cuts would have gone unnoticed!
Great question. @heacol will know the answer.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
According to Samsung, you either have to have antifreeze valves or glycol. As glycol will add 20%+ to your heating bill, it is not really an option. In reality, if you want top install them, 1 will suffice on the lower pipe, however, it is nearly impossible for ice to damage the Samsung unit as the internal connecting pipes are rubber, and will expand on freezing.
It is up to you, I have about 600 units in the field, of all makes, and no glycol or antifreeze valves, and have not, in the last 15 years, had a single unit damaged by ice.
@heacol I’ve also wondered how that worked. Will the system remain protected if there’s a big winter storm with temperatures below zero and power lines get taken down, and we’re without power for a few days. Wouldn’t that do some damage and wouldn’t stuff that shouldn’t freeze, freeze?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor I am not saying the units will not freeze in some conditions, and I have seen many, however it is the design of the unit it'self that will determine if there is any damage. Units that have standard circulator pumps in them such as Valiant, Midea/Clivet and others are vulnerable as standard circulators can easily be damaged by freezing, some units with pumps like Panasonic are not affected as they have taken the time and effort to make their own pump. Units that have no pump, like Samsung and Mitsubishi, are not usually affected.
As I said, it is your choice. My choice is Panasonic hands down, it is so far ahead of the pack for many, many reasons.
Posted by: @heacolAs glycol will add 20%+ to your heating bill,
Really? That is an enormous claim, citation required. I am aware of talk around a small increase, but 20% plus ( by how much plus) is astonishing.
@abernyte Difficult to get specific figures but I work on
Water 4.184kj/kg.K.
Monopropylene glycol 3.884kj/kg.K (@30%)
Monoethylene glycol 3.712kj/kg.K. (@30%)
Pump at say 50W will cost 1p/hour to run, with glycol added 1.1p/hr.
@david-i interesting. Thanks for sharing. So do you avoid glycol in systems too?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor No Glycol in our Daikin installation but we do have two antifreeze valves. When the ‘Boss’ came to do a little ‘snagging’, he was surprised (and I think, a little miffed due to their cost) that his installers had fitted them in both pipes rather than just one. I was rather pleased that they had fitted them in both as surely, if the pipes are both very cold, isn’t better that they both drain? (Or is not how this precaution is supposed to work perhaps?). (Daikin are coming today to carry out the first annual service) Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Anti-freeze valves provide some guarantee of a fail safe if the system is unpowered for a long period and all other forms of frost protection such as the unit pump circulating water and/or frost protection heating in the circuit fail. You are into double jeopardy however - a long power failure coincident with extreme prolonged low temperatures. Anti-freeze valves should be on both outdoor unit supply and return pipes at the lowest point. Glycol isn't really required in the UK provided external pipework is properly insulated and protected.
Glycol lowers the specific heat of water with increasing concentration, it's the renewable parallel of adding hydrogen gas to mains gas methane, which lowers the calorific value of the resulting blend. That's why using H2 for domestic heating is a dumb idea, aside from the cost of producing it and the safety issues it creates.
Which does not get us anywhere near a 20% plus energy cost increase caused by using glycol.
- 26 Forums
- 2,622 Topics
- 61.2 K Posts
- 1,064 Online
- 6,999 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Heat Pump Pipe Sizing Question
Like with some other minor mistakes made, this is somet...
By ASHP-BOBBA , 4 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@editor It's available here -
By HarrisonC , 5 hours ago
-
@mjr completely fed up with the AI drivel flooding soci...
By Mars , 5 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
The wind didn't blow the hot air balloon the most direc...
By mjr , 7 hours ago
-
@painter26 i am in Lightwater and midea trained. Sounds...
By Wizard , 8 hours ago
-
RE: Renewables & Heat Pumps in the News
@jamespa, for all I know they did have the coupling and...
By Mars , 11 hours ago
-
@andrewj ... well, clearing gutters is a worthwhile ann...
By colinc , 12 hours ago
-
RE: Anyone concerned about GivEnergy?
Here is the latest communication from GivEnergy regardi...
By txmartyn , 15 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Can @editor please clarify: Does the Indevolt App com...
By Transparent , 16 hours ago
-
@editor I too had a long list of questions, some of ...
By Bash , 17 hours ago
-
RE: Tell us about your Solar (PV) setup
3.84kWp of solar on our main South-East facing roof, in...
By Gmuzz , 17 hours ago
-
RE: Mitsubishi Ecodan FTC6, Evohome & Economy 7. Getting Two Zones to Work Together
Lets step back. Why do you need/want 2 zones? The hea...
By JamesPa , 19 hours ago
-
RE: Vaillant arotherm plus heat pump frost protection
Yes, typically as close to the heat pump as possible. ...
By JamesPa , 19 hours ago
-
RE: Brown Oily Residue Blocking Air Vent and Weeping Relief Valve... Anyone Seen This?
Difficult to comment further without being there. If...
By JamesPa , 1 day ago
-
RE: Our 10 year old Grant heat pump failed
Back in the 70’s and through the eighties, one of my re...
By Toodles , 1 day ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 2 days ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 2 days ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 2 days ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 2 days ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 2 days ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 2 days ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 2 days ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 3 days ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 3 days ago