Analysing MELcloud heat pump graphs
@boycey what you have there is really bad cycling 10 times an hour.
if you increased the flow rate this will have only worsened it as it has less time to get rid of the heat to the UFH causing the return temp to be too high and the HP can’t modulate down any further.
Set your thermostat in the bedroom to the maximum temp you want it to be so you don’t overheat.
turn the the pump speed back down to 2 have you ever tried 1? What flow rate do you get with it set at 1?
Then see what happens at a range of milder OAT’s. If it’s still cycling more than a couple of times an hour then you will need to increase min flow temp up a bit.
This my ecodan for an hour this afternoon at 11C outside at 32C flow
@sunandair stats set as above so there is just one set above bedroom comfort level, so that the circulation pump operates, I will then set that stat to a set back at night which will turn of the circulation pump and then the HP, .. I hope. No actuators, just the above, so hw will circulate everywhere. and then use WC for flow temp. Make sense?
There was a mesh steainer. And a few tiny bits in there.
I'm trying to get the sales team to get a service done, obviously Xmas has held that up. We shall see. I'm happy finding my way around the ftc6, it's just knowing what settings things are best at
@gary yes pump was on speed 1 for a few days. And yes u I understand what your dying re putting flow rate up. What size HP have you got? UFH ? I just seem to struggle to get that deltaT bigger.
Are you using stats or open loop just running on flow temp
What have you set your WC to?
Are you SE uk as at 11c today, I'm on south coast had same oat
It’s an 8.5kw ecodan UFH and rads.
WC set at 32C at 3C, 45C at -10C.
Running on weather comp with thermostat set to 22C in the hallway. Once it gets to 22C which it has just done this evening for the first time in a few weeks it has turned the heat pump off.
Do not worry about delta T, you can see from the chart I sent it was only 3C at these lower flow temps I only get delta T of 5 plus when I get upto 40C.
if your heat pump is happy running at pump speed 1 without it giving flow errors then use it. That will get you the the largest delta T
Posted by: @sunandairPosted by: @boycey
”*
All actuators taken off all stats set to 17c except one in bedroom set to 21c 6am to 11pm, and setback to 19c 11pm to 6am. But I am getting graphs like I attached this morning every hour now except when dhw is on. “*
?
It's a newbuild, although system was put in 2yrs ago, we are first ones living here, I checked the y strainer.. circulation pump set to 2 for 9 L/M. The flow rate sheet I have shows 7 loops set between 1 and 2 L/M each adding up to 9 L/M.
Above highlight
does this mean you have certain areas not operating above 17c and only one area trying to get heating up to 21c? what % of the whole area floor area is operating at 17c? Or have I misunderstood this description?
thanks
Also was there any debris in the y-strainer, was there a mesh strainer actually in the y strainer housing…. Sometimes these are removed and not replaced… just checking.
PS as it’s a new build and you are the first occupier I think it would be worth pressing for service and induction on how to operate it.. by a Mitsubishi accredited installer.
hi @boycey I’ve read your latest reply. Not sure what you mean by “stats as above” I would suggest you find out if it’s ever been commissioned and if not then get them to set it up. since it’s been installed as a new build and again it would help for you to have a proper handover induction on how it has been set up.
good luck
@sunandair I meant as I had already mentioned. It was commissioned, I have been l, like most here trying to get it set up efficiently. Ie take the actuators of so it open loop, use one stat only as an over heat limiter, run flow temp as low as possible, "low and slow". But in doing so my graphs have been as I've posted, lots of cycling etc.
Yesterday I decided to use the one stat to set a setback last night, set it to 19c from 9pm-6am, interesting the room temp in all rooms only dropped by half a deg, this is with 11c oat but high winds, we are on the sea front so get the weather off the sea, (no snow for us atm) so that is encouraging, I will have to test like this when it gets a colder snap again. But I guess we have a very low heat loss. We are on the 9th floor, so I guess we must get some sort of benefit from flats below us, as apposed to ufh that's on the ground albeit insulated.
We were back up to set temp from 6am by about 8.30-9am. So maybe I just need to put it stat on timed for a couple of times a day, keeping the floor topped up.. I'll post a couple of graphs from this morning see how they look.
-
Ecodan ASHP cycling every couple of hours
2 years ago
-
Ecodan EHST20C-VM2DR1 & PUHZ-FRP71VHA2 error
2 years ago
-
Melcloud app says "the unit failed to respond to the refresh"
3 years ago
-
Getting data
4 years ago
- 26 Forums
- 2,342 Topics
- 53 K Posts
- 265 Online
- 6,000 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@agentgeorge unfortunately mine is a structure borne no...
By swwils , 5 minutes ago
-
RE: Controlling Daikin Altherma via P1P2 and Home Assistant
So to clarify (and rephrase the problem into my own ter...
By Majordennisbloodnok , 44 minutes ago
-
RE: Free Ecoheat Heat Pump Install
This is an interesting way of looking at it, and I can ...
By Mars , 1 hour ago
-
RE: Configuring third party dongle for Ecodan local control
That's a good spot and a valuable insight, @sheriff-fat...
By Majordennisbloodnok , 2 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
@majordennisbloodnok And did ‘Honey’ order it for you? ...
By Toodles , 2 hours ago
-
RE: Setback savings - fact or fiction?
@robs — thanks again for your detailed comments. Some r...
By cathodeRay , 15 hours ago
-
RE: A Smarter Smart Controller from Homely?
@papahuhu I hope you get a swift resolution. Regards, T...
By Toodles , 19 hours ago
-
RE: Poll for Time of Use, tariffs, technology
That’s fine by me too Major, I feel it is a sad reflect...
By Toodles , 20 hours ago
-
Bingo. Sometimes a judiciously placed size 10 bovver bo...
By Majordennisbloodnok , 21 hours ago
-
RE: Mitsubishi Ecodan 11.2kW heat pump with low COP
@ciocoiu-alexandru I can't provide the same level of di...
By Sheriff Fatman , 21 hours ago
-
The three technical issues I'm considering are: BMS...
By Transparent , 23 hours ago
-
RE: LiFePO4 lithium battery fires and explosions
@transparent Your post may fit better in th...
By Batpred , 24 hours ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
@jamespawhite, if you could be bothered, you could also...
By Mars , 1 day ago
-
RE: Commencing on an ASHP Installation Process
I've got a bit of time to draft something today, so the...
By Sheriff Fatman , 2 days ago
-
RE: Help with heat pump sizing
@amin I dont think materially relative to t...
By JamesPa , 2 days ago
-
@majordennisbloodnok I have decided to take the plunge....
By TechnoGeek , 2 days ago
-
RE: Different dT on each radiator?
I cant sorry. Its based on some calculations I did fro...
By JamesPa , 3 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@simonf thats interesting as I’ve noticed my flow and r...
By AdamK , 3 days ago