Advice please on controls for my Daikin 14kw 3H HT heat pump with 3H HT W internal unit and Megaflo cylinder
Hello. I live in an old stone house in Orkney and have just had a Daikin high temperature heat pump installed. The whole heating system is new, including radiators that are sized as if for a regular gas boiler. Finding a local installer willing to quote and then to start work proved difficult and I used the largest electrical contractor on the island. The installation went badly wrong when the plumber who designed the system went off sick, and it has taken a year for them to finally get the system working properly without constantly cutting out. I could write many pages about the saga of the installation, but my worry now is that the system is not running as efficiently as it should, and we have some of the highest electricity charges in the UK here despite being self-sufficient in renewables.
I asked the plumber (the original one after he returned to work) about setting a weather-dependent curve, and he told me that with a high temperature pump this is not needed, so the flow temperature is set at a constant 60 degrees. The controls are TRVs on the radiators and an old-fashioned time switch and thermostat on the wall in the hallway just inside the front door. The thermostat seems to work like an on-off switch - the radiators are either hot or cold. I have not yet tried to fine-tune the TRVs as the heating isn't used constantly yet. As it is an old stone house it would seem to be better to run the heating for longer at a lower temperature, but most of the advice that I have seen is not for high temperature heat pumps.
Ideally I would like an independent heating engineer with experience of Daikin pumps to advise me on how the heat pump could be made to run more efficiently, but as I live on Orkney this doesn't seem to be an option. So I would be grateful for any help that members of this forum can provide.
Hi Jon. Sorry to hear about you installation ordeal.
it sounds like you have a good idea of what needs to be done with weather compensation.
Your installer either doesn’t know what he is doing or is deliberately pointing you down a more expensive route to make his life easier.
High temperature flow, TRVs and thermostats are not the way to run a heat pump efficiently.
You may have a problem with the size of your radiators when trying to run at lower temperature.
I’ve not seen a Daiken so can’t help you with how to set WC up. Someone on here should be able to help or failing that have you searched on YouTube?
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Hello bontwood. Thanks for your prompt response. The problem is that, from what I've read, the heat pump is not being controlled to work efficiently, but the plumber who installed it insisted that a high temperature heat pump is different and the installation is perfectly ok.
I did look in various places for more information, including YouTube, but I couldn't find any information specifically about high temperature pumps. When I contacted Daiken about previous problems with the installation they weren't very helpful. They more-or-less said that it was the installer's job to sort them out. Jon.
Yes, you can run high temp heat pumps just the same as any other kind but I think you need two things that may be missing [I'm no expert but I've seen this discussed in the Daikin Facebook group]
You need radiators sized for lower flow temperatures (bigger than usual in basic terms) and a way of controlling the flow temperatures/weather compensation curves, hot water schedules etc.
This is usually done on ordinary Daikin heat pumps with a Madoka and controller this is a Heat Geek video on using them. I'm not sure how you access the controls on yours but I do know that your installer is talking crap when he says 'you don't need it'. People do run high temp heat pumps at lower flow temperatures.
Look at this article that specifically mentions your heat pump
Do you not have all the manuals? You should have access to the Daikin website and app (which is famously naff but better than nothing.) If I was you I'd ring Daikin and ask.
Hopefully, others will come along who know more than me - what a rotten deal from your installers. I'm sure it is solvable with the right information.
It may help to join a Facebook group or two. There's a Daikin group and maybe a more general ASHP group.
Posted by: @joninorkneyHello bontwood. Thanks for your prompt response. The problem is that, from what I've read, the heat pump is not being controlled to work efficiently, but the plumber who installed it insisted that a high temperature heat pump is different and the installation is perfectly ok.
I did look in various places for more information, including YouTube, but I couldn't find any information specifically about high temperature pumps. When I contacted Daiken about previous problems with the installation they weren't very helpful. They more-or-less said that it was the installer's job to sort them out. Jon.
High temperature heat pumps are no different than other heat pumps, it is just they can operate at higher temperatures, but you would only wish to do so if it is absolutely necessary.
What determines the temperature at which a heat pump needs to operate is the ratio between heat emitter total output capacity and the calculated heat loss of the building.
The starting point to improve your system is to turn all the TRV's to the highest setting, except for possibly those in bedrooms.
Then set any room thermostats to a setting of 2C above the desired temperature. This ensures that the heat pump is always enabled, but is now being controlled by its own controller.
Below I have attached a Youtube video that details how to set the weather compensation on the controller, but as it states, this can be quite a lengthy process to fully optimise your system. Please feel free to as any further questions.
@lucia Good morning Lucia. Thank you for your reply. I've now looked at the Grand Designs article and the YouTube video. The article seems to confirm that a compensation curve is needed with the Daikin heat pump. The Heat Geek video is interesting but a bit above my head unless I do more homework. There is no separate controller on my system, so everything is set via the panel on the internal unit.
I do have the installation manuals. I found them on top of the internal unit after the plumber who did the faulty installation disappeared after causing a flood and said that he was going to fetch a longer drill. He was never seen again! They may have information about setting a curve, but they are not written for a housholder like me.
I finally got the MCS installation certificate needed to claim the grant a couple of weeks ago, over a year after the system was first switched on and after getting the mobile number of the boss of the company and expressing my views to him robustly about how shambolic they are. I think that I should also have a commissioning code so that I can register the unit with Daikin, and I will tackle that when I have the mental energy to do so.
Unfortunately, I'm not on Facebook and don't want to join, but I have a friend who is and perhaps he can have a look at the groups for me.
@derek-m Good morning Derek. Thank you for your reply. The YouTube video is much clearer than some others that I have watched, although it does seem to be quite a complicated process to do the fine tuning. There is no separate controller on my system, but it looks as though the curve can be set on the panel on the inside unit. It looks as though my radiators were sized for a flow temperature of 60 degrees, but this didn't take into account improvements to insulation and draughtproofing. Once the weather gets colder it looks as though I will have to fine-tune the system as you suggest to get it running efficiently.
@joninorkney Hi, here's the installation manual for your heat pump [PDF] it has a section explaining 'weather dependent curves' and low flow temperatures - I hope it helps. Oh... You have this already my bad. 🤦🏻♀️
I understand from others that it takes tweaking and trialling in small increments. The usual advice is to keep a record of settings before changing them so it is easier to revert or map your moves.
Heat pumps bring a whole new language and way of thinking - For me it has been a case of the more I read the more I will gradually absorb and understand. I'm very much at the beginning of this but one good thing is that people here are really helpful.
If you have specific questions you could get your friend to ask in either the Daikin support Facebook or even the Octopus heat pump group - you can find lots on setting curves, flow temps etc.,
@lucia Hello again Lucia. Thanks, that looks useful. The heating season hasn't begun properly yet, so I will probably wait for a few weeks before I seriously start to try to tune the system.
@joninorkney I'll reach out to Daikin tomorrow (Monday) and see if they can help you remotely, and it would be great if you could provide here to see what their customer support is like and whether/how they were able to help you.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Hello Mars. That would be good. I did contact Daikin last year about some problems with the installation and they simply referred me back to the installer. To be fair, when the experienced plumber returned from sick leave he spent a week re-doing the installation. There were some pretty serious problems that he corrected, including the outside unit not being level, the expansion vessel not being upright, pipework not being routed properly, no insulation, a blow-off pipe discharging into a floor void instead of to outside, a radiator being under-sized, and so on. It still cut out 4 or 5 times a day, and at the end of May this year, over a year after work started, he spent another 2 days here. The first day he drained and bled the system and fiddled around with various things. The second day he looked at the installation manual again and removed a circulation pump in the cupboard under the stairs, which apparently isn't needed and had been fighting against the pump in the internal unit and causing a water flow error. So perhaps you can see why I am skeptical about his advice on controls and curves!
Posted by: @joninorkneystill cut out 4 or 5 times a day
What do you mean by cut out. Are you saying the fan stopped (if so that is normal) or just stopped working and the tripped the main breaker? Or something different?
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 56 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
It's INSANE how wrong they have the sizing (and even sh...
By BAMi , 20 minutes ago
-
RE: Towel rails. An unexpected final hurdle. Resolved
@jamespa Solved thanks to your help. I found a ladder t...
By Davesoa , 20 minutes ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 1 hour ago
-
RE: What is the best strategy for operating a very oversized heat pump?
Something else... that works for some people... LG ha...
By Tim441 , 1 hour ago
-
RE: Setback savings - fact or fiction?
@cathoderay I see you are continuing to misquote from t...
By SUNandAIR , 3 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 3 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 3 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 4 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 15 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 18 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 20 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 22 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 23 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 4 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 4 hours ago
-
SolarPV tables / online calculator
By MichelleC 11 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 23 hours ago
-
By Toodles 2 days ago