Adding underfloor heating
We currently have an ASHP installed, which was fitted with our existing radiators and one zone for both upstairs and downstairs. We are currently building a small extension (12 sq.m.), and we want to put underfloor heating in it. We also intend, at a later date, to replace the downstairs radiators with underfloor heating, possibly in the next 5 years.
My question is, how should the plumber add underfloor heating to the extension, given (a) the small area currently, and (b) the plan in the future to put UFH all through the downstairs? Is this something that any plumber can do, or do we need to go back to the original installers?
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
if your ashp has hydraulic schematics for these types of install (vaillant for example) then copy those exactly. Otherwise:
The plumber should use close coupled Ts on the return line to take a parallel circuit to the UFH mixer/pump station. They should use an Ivar unimix3 blending valve (unless your your rad sizing was done to a suitable ufh temperature such as 35 degrees) because these are suitable for blending down low flow temps.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @hughfif your ashp has hydraulic schematics for these types of install (vaillant for example) then copy those exactly. Otherwise:
The plumber should use close coupled Ts on the return line to take a parallel circuit to the UFH mixer/pump station. They should use an Ivar unimix3 blending valve (unless your your rad sizing was done to a suitable ufh temperature such as 35 degrees) because these are suitable for blending down low flow temps.
Thanks so much, that's really helpful!
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
@scrchngwsl I can't advise you on the technical aspects of it but can give you my opinion after carrying out similar works.
We were adding an extension and switching to a heat pump. We had specified ufh in the extension but mid works asked for a quote for the existing concrete floors to be removed, insulation and ufh to be retrofitted downstairs - approx 85sqm. The quote came back as €12k which was too much so just went for the kitchen and wetroom shower for €5k.
We are in about a year and recently switched electricity providers and went for a smart tariff with a cheap rate for 3 hours (2am - 5am). We now heat the ufh to 22 degrees overnight and those rooms don't need any more heat during the day.
- 25 Forums
- 1,513 Topics
- 31.8 K Posts
- 36 Online
- 1,284 Members
Join Us!
Latest Posts
-
-
RE: Delivering a smart and secure electricity system: government consultation
Compared to a poorly executed development and rollout, ...
By ChickenBig , 1 hour ago
-
RE: Ecodan ASHP - How to optimise my set up?
That would seem logical, however do you know if the FTC...
By rhh2348 , 1 hour ago
-
RE: Ecodan - flow rates, sensors, settings
As mentioned above, the one I have 1) has the MITSUBISH...
By rhh2348 , 2 hours ago
-
RE: Additional Battery v Wind Turbine v Ripple
I should add, being an investment, the value of your in...
By Old_Scientist , 9 hours ago
-
RE: Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
Similar thread here
By Johnmo , 17 hours ago
-
RE: VDI 2035 heating water specification
Been looking and it seems a good little project. Ever...
By Johnmo , 2 days ago
-
RE: Do I accept an ASHP and Solar Panel retrofit under the HUG 2 scheme?
Will do. I'm currently waiting for another survey / vis...
By dssr , 2 days ago
-
The company that did the borehole were expecting us to ...
By Johnmo , 2 days ago
-
RE: The Misquote That Ruined the Heating Industry
@abernyte manufacturer training is pretty average. They...
By Mars , 3 days ago
-
-
RE: ECO4 Scheme and EPC ratings
@mellow Thanks. Given there is a scheme requirement to ...
By Old_Scientist , 4 days ago
-
RE: Do I just go with the lowest quote for my heat pump?
@jancold To me its a no-brainer then, a max 40C flow te...
By bontwoody , 4 days ago
-
-
RE: Heat Pump Books Beginners – Bodge Buster & From Zero To Heat Pump Hero
@editor Presumably he had some good weather Compensatio...
By Toodles , 4 days ago
-
RE: New Vaillant 7kW aroTherm ASHP or oil boiler dilemma/decision??
Storage capacity really is dependent on storage tempera...
By Johnmo , 4 days ago
-
RE: HP Cycling, Expected or Undesirable
Just a little update. I ordered a longer shielded twin ...
By bontwoody , 4 days ago
-
RE: Domestic hot water timer doing crazy things on my Grant Aerona3 10kW air source heat pump
Thanks @allyfish for the pics and info. Spoke to the in...
By Mellow , 4 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
It's been a busy day for calls and emails from Aira. I ...
By MikeH , 5 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Hmm. A bit of a nuanced answer, methinks. As I've alr...
By Majordennisbloodnok , 5 days ago
Latest Topics
-
Ecodan - flow rates, sensors, settings
By rhh2348 15 hours ago
-
Replacing mains water with well water
By Johnmo 2 days ago
-
Additional Battery v Wind Turbine v Ripple
By bontwoody 3 days ago
-
By jamespipe 3 days ago
-
VDI 2035 heating water specification
By Johnmo 3 days ago
-
Do I just go with the lowest quote for my heat pump?
By Jancold 5 days ago
-
The Misquote That Ruined the Heating Industry
By Alec Morrow 6 days ago
-
Battery Storage Wiring Gauge Question
By Puff 6 days ago