Adding auto-adaption to a Midea heat pump controller
Posted by: @derek-mI am pleased to see that you are resisting the urge to 'tinker'. I think that you will find it could takes several hours for the IAT to reduce and stabilise.
It's called masterly inactivity...
Posted by: @derek-mOne improvement that you may wish to consider is varying the offset dependent upon the size of the deviation.
Something along the lines of:-
If the deviation is <0.5C, do nothing.
If the deviation is =>0.5C, offset by 1C.
If the deviation is =>1.5C, offset by 2C.
I had had similar thoughts, thinking about recovering from an overnight setback, for example, when the deviation is likely to be greater.
I have just had a peek at the live minute data for the last 12 hours (auto_adapt went live at 0800 this morning) and the LWT and energy in have gone down a bit, whether due to the increased OAT and/or the auto-adaption, and the IAT has dropped by 0.1 degree C...
This is on a par with watching the paint dry. But that's OK for now, I just need to get a feel for what the increments need to be by trial and error.
Midea 14kW (for now...) ASHP heating both building and DHW
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 27 Online
- 5,673 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
Nice one @toodles... always appreciate your enthusiasm ...
By Mars , 10 hours ago
-
@profzarkov Good to know in case it ever happens to me...
By bontwoody , 14 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@patrickvito We have had car dealers re-powder coat the...
By ASHP-BOBBA , 15 hours ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I mean, is this surprising? The local installers in my ...
By Alex , 15 hours ago
-
@old_scientist sorry, I should have made it clear that ...
By GrahamF , 16 hours ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@thundermink can you provide photos to illustrate your ...
By Morgan , 16 hours ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 19 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 20 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
After our rather lengthy meander off piste, I thought I...
By GrahamF , 22 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - to collect the IAT/OAT data, can I sugges...
By cathodeRay , 23 hours ago
-
RE: Ecodan software update. Real or scam?
@vinz86 Contact Mitsubishi and an engineer attends and ...
By ASHP-BOBBA , 1 day ago
-
@drei When I was in local government we were of cours...
By JamesPa , 2 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 2 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 2 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 3 days ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 3 days ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 3 days ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 3 days ago