Adding ASHP to thermal store.
I have a new heating system design with thermal store to take advantage of heat produced by log burner and oil fired raeburn. The thermal store is prepared foe ASHP with a coil. The store is designed to run at 45 degrees with appropriate radiators. I'm happy with the design, but I don't understand why coil has been included for the ashp when the log burner, raeburn are both just open circuit. This additional coil is causing problems......
Can I run the ashp on common circuit as well?
I can't ask designer why he specified this, we have parted ways but not because of technical issues.
Might it be because the designer assumed the ASHP would be using antifreeze?
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody could be but the whole thermal store will be treated water, not potable. HW will be DHW.
I know it's needed for solar because of the higher pressures, but can't figure out why for ASHP - I was reading through specs for ASHP for pipe sizings as I need to finalise and order tank when I realised they are OK with common thermal store - as far as I can see.
Need to order tank, there is a significant saving to be made if I drop the extra coil, due to design problems.
@roohairy I plumbed (!) for a thermal store in my last house and was advised to have a splarge pipe rather than a coil in it for the heat pump. I hadnt realised that the whole of the store would then need to have antifreeze in it and the cost of that. In the end I used the solar thermal coil instead which got me out of a hole at the time.
Nowadays I would probably use the splarge pipe and omit the antifreeze using anti freeze valves (or nothing depending on your attitude to risk). In your position I think thats what I would now do if ordering a thermal store.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 11 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Solar Thermal DHW and ASHP
Since you already have the ashp it makes little financi...
By Judith , 6 hours ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
I think you’ll find it depends on the room heat loss. A...
By Judith , 7 hours ago
-
DESNZ doing a survey which asks the right questions!
DESNZ have engaged ICF to do a survey of people who hav...
By Judith , 7 hours ago
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
Just done your survey!
By Judith , 7 hours ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil Fwiw I have the 7kW model with which I'm, ver...
By JamesPa , 8 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@grahamf you appear to value your recirculating loop de...
By Judith , 8 hours ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
@cleardene-ashp just thinking about your issues here. Y...
By Judith , 9 hours ago
-
RE: Midea ASHP – how to set weather compensation
@cathoderay OK let's wait and see, it sounds an interes...
By Tasos , 11 hours ago
-
RE: What is the Heat Geek Guarantee?
@judith, I’m with you on Heat Geek, but there really do...
By Mars , 12 hours ago
-
RE: Electricity price predictions
Community energy installations are a great idea, but th...
By Scalextrix , 1 day ago
-
Inventor (Midea) Heat Pump short cycling advice
Hello, I have a Inventor (Midea) 8kW with a 800meters Φ...
By immunity , 1 day ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Ooh, heat pumps in neon blue wrap 🤣 🤣 &...
By Old_Scientist , 2 days ago
-
@profzarkov Good to know in case it ever happens to me...
By bontwoody , 3 days ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I mean, is this surprising? The local installers in my ...
By Alex , 3 days ago
-
@old_scientist sorry, I should have made it clear that ...
By GrahamF , 3 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@thundermink can you provide photos to illustrate your ...
By Morgan , 3 days ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 3 days ago