2 heat pumps - 1 as a slave
Hi
Im really hoping might be able to help and explain in really simple terms as I’m struggling to get my head around our system
Background - we had 2 grant aerona air source heat pumps installed under eco4 grant which turned out to be a bit of a disaster so we’re trying to unravel everything.
The heat loss survey shows we need 24kw at -3
We had two heat pumps - 10 & 15 kw set up in tandem. Trying to reduce our outrageously high bills we were recommended that these should be set with the smaller as a Slave so had an EP002 installed but then it seemed to keep kicking the slave on after 45 mins so I phoned Grants to find out why.
They stated that we will always need them both to come in as we have a need for 24kw, but it doesn’t make sense in my head that we need that when the outside temp is 13 degrees and we are only trying to raise the internal temp by 2 degrees. I thought the slave would kick in just when it was minus outside.
Does anyone have any thoughts on this please.
You are correct.
If your total calculated heat loss is 24kW, then at an outside temperature of 13C, the heat loss will probably be in the region of 8kW, so in theory either of the two heat pumps should be capable of supplying the heating demand.
@derek-m thanks, I thought it didn’t make sense. I phoned Grants back and spoke to someone else who talked me through lots of settings. I think the outdoor ambient temp was set too high so I’ll be checking tonight to see if they still both kick in.
Is weather compensation active? While you require on average a lower heating power when it is say 10C outdoors, without weather compensation both heatpumps would be needed to cycle the radiators on and off to a high setpoint. That is, while the average power is low, the peak would be the same as ever, so both may be needed.
Weather compensation generally requires the use of the heatpump manufacturers own controllers, and is a way to match the power out of the heatpump to the expected power requirement. In doing this, the heatpump can operate more efficiently.
@robl so the initial installers didn’t set the weather compensation even tho they ticked to say they had on the paperwork.
We had a heating engineer out to look at the system and he set it. Not sure what to or where to find this though.
-
Is this ASHP install OK?
2 months ago
-
Help needed in Essex
5 months ago
-
Air source heat pump problems - NIBE F 2040 ASHP
8 months ago
-
Viessmann Vitocal 250-A in the UK
1 year ago
-
Underfloor heating specification for heat pump
2 years ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 36 Online
- 5,744 Members
Podcast Picks
Latest Posts
-
RE: Big Changes Coming to Our Heat Pump System
@editor your engineer's attitude is truly horrifying. ...
By GrahamF , 13 hours ago
-
@cliffhanger - seriously though, I have no idea. What I...
By cathodeRay , 15 hours ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 15 hours ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 17 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 21 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 23 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 23 hours ago
-
@jamespa Ours is a Daikin EDLA03 8 kW and the Delta T =...
By Toodles , 24 hours ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 2 days ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 2 days ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 2 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 2 days ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 3 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 3 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 3 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 3 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 5 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 5 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 6 days ago