@allyfish the system was flushed maybe 6-8 months before the install happened. I did ask at the time and the installer said the system was already clean and didn't need another flush. Maybe another example of cutting corners
When the heating started after the summer this year I got an FU fault a couple of times but has been good for a while now. This is when Grant said there is a flow issue somewhere in the piping.
Posted by: @soniksYou just reminded me I have a pizza oven thermometer which I can use
In my lounge
There are 4 radiators. I took the readings from
2m K2 radiator new - top : 32c, bottom : 24.8c
1m K2 radiator new - top : 34.1c, bottom : 29.8c
1.6m K2 radiator new - top : 22.3c, bottom : 17.1c
low height 43cm double radiator existing - top: 35.7, bottom : 32.9
Did you get warm water to the cold radiator? If not then remove the TRV actuator head and ensure that the valve plunger moves freely.
@allyfish No I don't have a flow setter/guage AFAIK - where would it be installed normally.
The pump is a Wilo 25/80 pump attached image. Can't see the model number anywhere but I think it may be a Wilo-Yonos Pico pump. I think it's on the highest setting at the moment.
I do agree with you the flow rate needs to be resolved first before balancing. From the discussions the discussions on the forum perhaps it is a piping issue as the property has been extended a couple of times by the previous owners and I wonder whether the piping has been done properly. Are there are any heat detectors that could show where the pipes are layed if I turned on the heat pump to the max and potentially give an indication of the pipe size based on the heat emitted from pipes.
There is a Mag one filter installed. How can I tell if the heat pump heat exchanger is blocked?
@soniks thanks for that, the in-built pump in the Grant Aerona 17kW can provide 50l/min at 5m head on the highest speed setting. A Wilo Pico RP25/80 in series with that can provide 50l/m at 3m head. (25/80 is a common fixed speed CH pump badged up by various manufacturers) Pumps in series raise the head, so in combination you have 50l/m at 8m head. That's more than enough pumping capacity. I would recommend a specialist heating engineer is brought in to investigate further.
Flow gauge and flow setter. For properly commissioning a Grant ASHP setting the flow is essential. The grant units have fixed speed pumps and no internal flow sensing, so they rely on the installer commissioning this to suit the make/model and design water leaving temperature. If you don't have one installed I would recommend fitting one. You can DIY but it's probably a system drain down job.
The condition of the MagOne filter might give you some idea as to how clean or not your system pipework is. You can open that up for inspection & cleaning without drain down, but stop the system first. If there's a lot of build up of black sludge on the magnet and/or evidence of other contamination, then a power flush of the piping system may be a good idea.
You can't really check the plate heat exchanger without a full drain down, disconnection of the outdoor unit flow and return pipes, and reverse flushing to see what comes out! A competent heating engineer who has power flushing equipment could do that for you at the same time.
When the system is being power flushed the engineer would be able to look further into the circuit pipework for any obvious issues.
Sorry I should have clarified in my last post - reliable heating engineers that covers the Surrey region
Posted by: @soniksSorry I should have clarified in my last post - reliable heating engineers that covers the Surrey region
Adam Chapman of heatgeek is based around Guildford, he should be able to advise on any local engineers who are competent.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@derek-m I measured the temperatures on the radiators again the I can see the following readings. Slightly higher than before without changes. Perhaps it's because it's not as cold at the moment.
Top Bottom
K2 1m 36.7 31.1
K2 1.6m 33.1 25.5
K2 2m 31.2 23.9
Out of interest what sort of temperatures would be considered normal for radiators with a heat pump. I set the flow temp to 50c at the moment.
Posted by: @soniksOut of interest what sort of temperatures would be considered normal for radiators with a heat pump. I set the flow temp to 50c at the moment.
Over the last 24 hours, mine have ranged between 28 and 38 degrees while heating. If you set the flow to 50, I expect at least one radiator should be achieving near that (45+?) at the top. There's a discussion on here somewhere where people with temperature sensor guns pointed them at their radiators, which you might find by searching.
Posted by: @soniks@derek-m I measured the temperatures on the radiators again the I can see the following readings. Slightly higher than before without changes. Perhaps it's because it's not as cold at the moment.
Top Bottom
K2 1m 36.7 31.1
K2 1.6m 33.1 25.5
K2 2m 31.2 23.9
Out of interest what sort of temperatures would be considered normal for radiators with a heat pump. I set the flow temp to 50c at the moment.
If the temperature of the water coming out of your heat pump is in the region of 50C, then you should be seeing temperatures not much below that at the top section of your radiators. If you are not getting such temperatures then there must be some mixing and cooling of the water within your system. If that is the case then it can seriously reduce the overall efficiency.
I would suggest that you measure the temperatures on the pipework around your system to try and locate any problem areas.
- 21 Forums
- 1,964 Topics
- 42.6 K Posts
- 22 Online
- 2,278 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami yes. 8kw = 8000w I would change the areas in th...
By bontwoody , 2 hours ago
-
RE: Towel rails. An unexpected final hurdle
I had a similar issue but convinced the installer to le...
By Pie_Eater , 3 hours ago
-
Cliff, welcome to the forum. You’re running into one ...
By Mars , 3 hours ago
-
RE: What is the best strategy for operating a very oversized heat pump?
This whole discussion highlights just how much of a mes...
By Mars , 3 hours ago
-
RE: NIBE F2040 12 kW heat pump and 100 liter buffer tank
@cheshirejohn thanks for the update and for sharing. I’...
By Mars , 3 hours ago
-
RE: Setback savings - fact or fiction?
Here's the same plot, less the R squared values, done q...
By cathodeRay , 6 hours ago
-
RE: SolarPV tables / online calculator
We've only had our solar since last June, but so far fo...
By Old_Scientist , 6 hours ago
-
@robs useful thread! Thanks for sharing - Octopus are c...
By big_si , 6 hours ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 8 hours ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 9 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 10 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 14 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 1 day ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 1 day ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 2 days ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 2 days ago
Latest Topics
-
By cliffhanger 3 hours ago
-
Heat Pump Sizing & Installation Costs
By Mars 16 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 17 hours ago
-
SolarPV tables / online calculator
By MichelleC 24 hours ago