Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@allyfish the system was flushed maybe 6-8 months before the install happened. I did ask at the time and the installer said the system was already clean and didn't need another flush. Maybe another example of cutting corners
When the heating started after the summer this year I got an FU fault a couple of times but has been good for a while now. This is when Grant said there is a flow issue somewhere in the piping.
Posted by: @soniksYou just reminded me I have a pizza oven thermometer which I can use
In my lounge
There are 4 radiators. I took the readings from
2m K2 radiator new - top : 32c, bottom : 24.8c
1m K2 radiator new - top : 34.1c, bottom : 29.8c
1.6m K2 radiator new - top : 22.3c, bottom : 17.1c
low height 43cm double radiator existing - top: 35.7, bottom : 32.9
Did you get warm water to the cold radiator? If not then remove the TRV actuator head and ensure that the valve plunger moves freely.
@allyfish No I don't have a flow setter/guage AFAIK - where would it be installed normally.
The pump is a Wilo 25/80 pump attached image. Can't see the model number anywhere but I think it may be a Wilo-Yonos Pico pump. I think it's on the highest setting at the moment.
I do agree with you the flow rate needs to be resolved first before balancing. From the discussions the discussions on the forum perhaps it is a piping issue as the property has been extended a couple of times by the previous owners and I wonder whether the piping has been done properly. Are there are any heat detectors that could show where the pipes are layed if I turned on the heat pump to the max and potentially give an indication of the pipe size based on the heat emitted from pipes.
There is a Mag one filter installed. How can I tell if the heat pump heat exchanger is blocked?
@soniks thanks for that, the in-built pump in the Grant Aerona 17kW can provide 50l/min at 5m head on the highest speed setting. A Wilo Pico RP25/80 in series with that can provide 50l/m at 3m head. (25/80 is a common fixed speed CH pump badged up by various manufacturers) Pumps in series raise the head, so in combination you have 50l/m at 8m head. That's more than enough pumping capacity. I would recommend a specialist heating engineer is brought in to investigate further.
Flow gauge and flow setter. For properly commissioning a Grant ASHP setting the flow is essential. The grant units have fixed speed pumps and no internal flow sensing, so they rely on the installer commissioning this to suit the make/model and design water leaving temperature. If you don't have one installed I would recommend fitting one. You can DIY but it's probably a system drain down job.
The condition of the MagOne filter might give you some idea as to how clean or not your system pipework is. You can open that up for inspection & cleaning without drain down, but stop the system first. If there's a lot of build up of black sludge on the magnet and/or evidence of other contamination, then a power flush of the piping system may be a good idea.
You can't really check the plate heat exchanger without a full drain down, disconnection of the outdoor unit flow and return pipes, and reverse flushing to see what comes out! A competent heating engineer who has power flushing equipment could do that for you at the same time.
When the system is being power flushed the engineer would be able to look further into the circuit pipework for any obvious issues.
Sorry I should have clarified in my last post - reliable heating engineers that covers the Surrey region
Posted by: @soniksSorry I should have clarified in my last post - reliable heating engineers that covers the Surrey region
Adam Chapman of heatgeek is based around Guildford, he should be able to advise on any local engineers who are competent.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@derek-m I measured the temperatures on the radiators again the I can see the following readings. Slightly higher than before without changes. Perhaps it's because it's not as cold at the moment.
Top Bottom
K2 1m 36.7 31.1
K2 1.6m 33.1 25.5
K2 2m 31.2 23.9
Out of interest what sort of temperatures would be considered normal for radiators with a heat pump. I set the flow temp to 50c at the moment.
Posted by: @soniksOut of interest what sort of temperatures would be considered normal for radiators with a heat pump. I set the flow temp to 50c at the moment.
Over the last 24 hours, mine have ranged between 28 and 38 degrees while heating. If you set the flow to 50, I expect at least one radiator should be achieving near that (45+?) at the top. There's a discussion on here somewhere where people with temperature sensor guns pointed them at their radiators, which you might find by searching.
Posted by: @soniks@derek-m I measured the temperatures on the radiators again the I can see the following readings. Slightly higher than before without changes. Perhaps it's because it's not as cold at the moment.
Top Bottom
K2 1m 36.7 31.1
K2 1.6m 33.1 25.5
K2 2m 31.2 23.9
Out of interest what sort of temperatures would be considered normal for radiators with a heat pump. I set the flow temp to 50c at the moment.
If the temperature of the water coming out of your heat pump is in the region of 50C, then you should be seeing temperatures not much below that at the top section of your radiators. If you are not getting such temperatures then there must be some mixing and cooling of the water within your system. If that is the case then it can seriously reduce the overall efficiency.
I would suggest that you measure the temperatures on the pipework around your system to try and locate any problem areas.
- 27 Forums
- 2,539 Topics
- 59.1 K Posts
- 1,033 Online
- 6,818 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Balancing is a long process and its possible to mess th...
By JamesPa , 37 minutes ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 2 hours ago
-
Thanks everyone for the help, Havenwise now diasbled. q...
By Boycey , 4 hours ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli Depending on whether you can get an EV tariff, I...
By ChandyKris , 4 hours ago
-
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 6 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@technogeek I think you are correct, but, it didn’t inf...
By Papahuhu , 6 hours ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 7 hours ago
-
@Mars at the time of writing heating oil is £1.28 / ltr...
By TechnoGeek , 7 hours ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 10 hours ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 10 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
The setup for this is a Samsung Modbus card. Connected ...
By antonical , 12 hours ago
-
RE: Forum updates, announcements & issues
@davidalgarve, if the emails are more than roughly a mo...
By Mars , 12 hours ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 12 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Sorry to hear that but I'm not surprised TBH. Stratifi...
By JamesPa , 13 hours ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 1 day ago
-
RE: Setback savings - fact or fiction?
The answer was in two parts in my reply, the second par...
By RobS , 1 day ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 1 day ago
-
Ecodan control return to Melpump from Havenwise trial. settings check
Hi, Just got control back after being on the hav...
By Boycey , 1 day ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
I wonder if heat pump manufacturers will tone these sit...
By JamesPa , 1 day ago
-
RE: Who’s Caved and Switched the Heating On Already?
@editor yesterday we used 12kW of electricity for heat,...
By Judith , 1 day ago
-
RE: Rate the quality of your heat pump design and installation
Loss assessments can be a very serious case of GIGO. I...
By JamesPa , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@jamespa Just bizarre. This is our data. I really don't...
By antonical , 2 days ago
-
RE: Mitsubishi Ecodan 11.2kW review
I think you said its an 11.2kW model and your house is ...
By JamesPa , 2 days ago