Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
17kW Grant Aerona 3 - advice needed for pre-commissioning struggles
thanks Derek, we do have a LLH my understanding thats to provide hydraulic seperation of primary and secondary circuits and cope with having multiple pumps on secondary
Regarding the temp I will try the 50 at -5 ..... will also discuss with the plumber come commissioning
Posted by: @denevilthanks Derek, we do have a LLH my understanding thats to provide hydraulic seperation of primary and secondary circuits and cope with having multiple pumps on secondary
Regarding the temp I will try the 50 at -5 ..... will also discuss with the plumber come commissioning
If you have a suitable thermometer, I would suggest measuring the temperature of the pipes coming from your ASHP, and also measure the temperature of the pipes going out to your heat emitters. The temperature of the pipes going to the heat emitters should be about the same temperature as the supply pipe from your heat pump. If there is quite a difference in temperature then this would indicate a flow imbalance, which can adversely affect both operation and efficiency.
As I dont have an electric car and averge less than 30% electric between 00:30 and 6:30 I decided to switch from Economy 7 to single tariff .... now I can heat my DHW in afternoon and not worry what time the dryer is on. The ASHP is failing to reach 55 degrees for DHW heating as it has at least one defrost cycle in an hour .... almost got there at 49 degrees ....
Posted by: @denevilHi @AllyFish, thanks for the detailed reply, ... I had no idea of the defrost details ....
answers follow
"17kW ASHP. Who sized it & on what basis? "
Plumber working with Grant and Stone who sized and recommended unit. Simon at Grant did the calcs and has been here and checked the plumbers implementation of the standard plan in Appendix A.
"The best time of day to generate your hot water from an ASHP is from mid-day to early afternoon. "
My logic was that in afternoon the tariff is 48p/kwh at night its 18p/kwh .... it seemed effective at night when it wasnt freezing ... now its simply not heating the water .... its tepid .....
"Hot water cylinder in the loft. Is the loft converted & the roof itself insulated? "
No the cylinder is new and is factory insulated with 50mm celotex equiv.
There is still a fair amount of unlagged pipework including in loft ... thats on plumber todo list.
"What's the flow rate on the primary side during heating and during hot water generation? What's the ASHP internal pump flow rate dip switch set to? You would benefit from a flow gauge/setter valve on the return of the secondary circuit, because you can balance the LLH that way, and check primary and secondary flows are closely matched, to avoid water passing through the header in either direction. "
Only thing I can see is flow rate on the gauge in primary return to ASHP and its around 32
"What's the ASHP internal pump flow rate dip switch set to"
I believe it was set to max
"TRVs - set them all to at least one number higher than you want the room temperature to be"
They are all on max and the weather compensation is enabled on the ASHP
I had increased TM1 to 45 but I could see the flow temp going up to 45 then down to 30 .... then backup .... I wasnt given a monitoring option so its just from random checking at the remote control. Took 15 hours to raise temp of kitchen to 19 which fell to 18 overnight even tho thermostat was 19.5. ...... and thats with DHW turned off.
This is becoming somewhat depressing ... last week all seemed good, house was warm and I had hot water in the morning which stayed hot all day ...
Hi @Denevil, OK, the low rate overnight tariff is a good reason to generate HW overnight, if not the most thermally advantageous time. Defrosts are annoying but unavoidable with ASHPs. I long for a unit designed for the UK climate that has wider fin spacing on the evaporator, and perhaps a hot gas injection defrost rather than reverse cycle. Cold store evaporators are designed to ice up and don't defrost as often, but an ASHP evaporator coil would need to be much bigger. Since most ASHPs are derived from air to air reversible heat pump products, they use 4 port reversing valves. Problem is, they take energy from the water circuit in defrost, which is why you see the water temperature suddenly drop, and then slowly recover.
Do you have any secondary heating? The LLH has a 3kW immersion installed which can be programmed to provide supplementary heating in very cold weather, heat energy during defrost cycles, or as a backup heater. Of course it could be expensive to run at 3kW and CoP of 1. One option if you have a low overnight tariff is to set the parameters at the Grant controller to enable it if the outside temperature falls below a certain value, and put a timer on the 240V supply to it, so that it's only energised during the low tariff.
32l/min flow rate sounds reasonable, perhaps a little low depending on your design temperature:
To get 17kW 'nameplate' out of your ASHP and with pure water circulating, that flow would be a flow and return delta T of 7.6. I've never seem my Grant Aerona 10 achieve anything higher than 6degC delta T, even though the flow rate is optimised and the delta T parameter set to 8. That may be a due to the size of my heat emitters and max flow temperature as opposed to the ASHP itself.
I would recommend checking the balancing of the LLH, which preferably means a flow setter/gauge on the secondary side, or digital temperature probes to do it thermally. I bought these, which are very cheap and reasonably reliable when the probe is secured to the copper pipe under close fitting insulation.
https://www.amazon.co.uk/dp/B07TY6HRL4?psc=1&ref=ppx_yo2ov_dt_b_product_details
Currently viewing this topic 1 guest.
- 27 Forums
- 2,541 Topics
- 59.2 K Posts
- 422 Online
- 6,822 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles If I ever catch myself feeling hubristic I ...
By Papahuhu , 2 hours ago
-
Why? Factor in 85% efficiency for that oil boiler and...
By Old_Scientist , 2 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
I've been watching this with interest as I would like s...
By JohnnyB , 3 hours ago
-
RE: Aerotherm 12+12kw cascade huge power utilisation
What the hell. There is exactly one reason to use a h...
By bobflux , 3 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Thanks for such a comprehensive response!!! ...
By errmm , 5 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Thanks, that’s a fair point and I agree th...
By Eliuccio , 9 hours ago
-
Daikin high temperature heat pump
Hello, I have a DAIKIN ERSQ 016AAV1 16KW. I have a BRC2...
By gajolos , 14 hours ago
-
RE: Setback savings - fact or fiction?
I changed the pump power to the actual value to see if ...
By RobS , 16 hours ago
-
RE: NIBE Heat Pump Warranty: What's an Adequate Engineer Attendance Time?
Totally agree. However the manufacturers know that fe...
By JamesPa , 1 day ago
-
-
RE: The law of unintended consequences....
Oh Thank you Major, I was just beginning to wonder wher...
By Toodles , 1 day ago
-
RE: Forum updates, announcements & issues
I know that the notifications are being delivered now w...
By Mars , 1 day ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli I have sent a direct message with the financial ...
By ChandyKris , 1 day ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Does it disappear when the heat pump is off? What abou...
By JamesPa , 2 days ago
-
RE: Fitting heat pump plumbing and pipes in advance?
Great tips, thanks. The PEX/Al/PEX option sounds much m...
By Jonatan , 2 days ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Those control valves on the UFH manifold could be an is...
By Travellingwave , 2 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 2 days ago
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 2 days ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 2 days ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 3 days ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 3 days ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 3 days ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 3 days ago