The simple way to check if your water pumps are operating in PWM mode is count the number of cables that are connected, if there are two then it is probably being operated in PWM mode.
To check whether the pumps are capable of PWM mode if they only have one cable connected, check the model number or post a photo.
Posted by: @craig1980@derek-m both pumps operate whichever room stat is turned up/down. Both receiver's mounted on the wall by the cylinder acknowledge signal when turned up individually so that seems okay. Odd that both pumps work? Heat pump also kicks in whichever is turned up.
Turning both off will turn off the heat pump and water pump. Turning just one off makes a few clicks and that's all that changes. Same instantaneous power usage.
Without being able to see how it is actually piped up, I suspect that one pump is pushing the return water back to the heat pump, and hence required for either DHW heating or CH. The second pump is probably for the UFH.
Try the same exercise as described previously, but with DHW heating selected rather than CH.
A further thing to check is the position of the motorised valves, when the different thermostats are operated in the different operating modes, DHW or CH.
@derek-m I don't have under floor.
The room stats don't have an option for dhw. That is set up on the controller as a schedule or manually on/off. The temp can be adjusted within the controller menu.
Where might I find the motorised valves? Thanks
Posted by: @craig1980@derek-m I don't have under floor.
The room stats don't have an option for dhw. That is set up on the controller as a schedule or manually on/off. The temp can be adjusted within the controller menu.
Where might I find the motorised valves? Thanks
Hi Craig,
Sorry, I assumed that you would have UFH with a second water pump installed. So that may mean that you have a buffer tank or low loss header instead. Could you please try to identify all the items of equipment within your system, and how they are connected together.
@derek-m here's a pic of what I have.
So, two tanks above the main 150l cyclinder, the white one is an unvented cylinder expansion tank 18l, no idea what the other does but it appears to be plumbed via a pressure guage.
Two internal room stats, Samsung 12kw gen 6 heat pump, Joule 150l UVC, Samsung gen 6 wired controller. Salamander water pump which activates when hot tap is turned on but the pump is connected to the feed from the cold water tank in the loft. We are gravity fed.
Apparently it's a two zone system but when running just one or the other it isn't set up as upstairs and downstairs. When we had the flow temp at 45 one or two rads upstairs got hot and the others were very slightly warm.
As for the pumps running when dhw is turned on, both pumps engage when dhw on and turn off when not required.
Salamander make pumps for pressurised showers. Some have automatic pressure regularisation, which enables them to deliver hot and cold evenly when drawing from sources at different pressures.
I've zoomed in but can't read the Salamander part number. It's possible that it's related to your ASHP installation only peripherally in order to supply a bath/shower at a reasonable flow-rate. I doubt it has any aspect of 'control' from the rest of the HP system.
Save energy... recycle electrons!
@transparent yeah, I used to have one that was twin impeller so had a hot and cold feed (2 inlet, 2 outlet). This one is single impeller. Cold water comes from header tank and feeds in to pump then into system via a mixer valve. I told the guy we had poor flow from cold feed in to the house as we are on old 1/4" black pipe from the mains and this was his solution. We get a good pressure through the shower still.
Posted by: @derek-mThe simple way to check if your water pumps are operating in PWM mode is count the number of cables that are connected, if there are two then it is probably being operated in PWM mode.
To check whether the pumps are capable of PWM mode if they only have one cable connected, check the model number or post a photo.
Thanks. Just the one cable to each pump. The buffer tank means there is flow separation and I presume that makes a second pump necessary. With two pumps I also suspect that PWM mode would get quite complicated.
I have attached a photo, which shows the Grundfos pump.
- 26 Forums
- 2,208 Topics
- 48.7 K Posts
- 62 Online
- 5,868 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Mitsubishi Ecodan F8 error
@hjd F8 is uncommon and could indicate incorrect heat e...
By ASHP-BOBBA , 7 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@papahuhu at the end of the day if you are happy with h...
By benson , 25 minutes ago
-
RE: Can you recommend a Mitsubishi service engineer in the Rochdale area?
@dgclimatecontrol We'll all need annual servicing. How...
By Suzy-shadow , 43 minutes ago
-
RE: Renewables & Heat Pumps in the News
@transparent I’ve understood your point now. The point ...
By Judith , 1 hour ago
-
RE: Octopus tariffs - a quick comparison
Does indeed need checking, @tim441. Neither Homely ...
By Majordennisbloodnok , 1 hour ago
-
RE: How not to install a heat pump
Delighted to hear that the buffer has been replumbed as...
By JamesPa , 2 hours ago
-
-
RE: Daikin 9kW to 8kW Swap Offer from Octopus
Yes but 9kW is similarly the 16kW derated. So 8kW subs...
By JamesPa , 4 hours ago
-
Actually, there's a rather greater degree of cattle-her...
By Majordennisbloodnok , 4 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@davidnolan22 So far as I can tell from the 'other p...
By JamesPa , 8 hours ago
-
RE: 5 Star Service from Havenwise
I keep getting havenwise ads on my Facebook feed, so cl...
By benson , 10 hours ago
-
Automation options to maximuse efficiency & ToU tariffs
I started a conversation with ChatGPT. What automation...
By Tim441 , 15 hours ago
-
RE: 4 Year Ongoing Heat Pump Battle With Poor Heat Pump Installation
@jamespa Oh, I know some that are good and some not so....
By ASHP-BOBBA , 20 hours ago
-
RE: Samsung Heat pump with Yonos Pico circulating pump running all the time
I don't know how many pumps you have but I guess it's o...
By JamesPa , 21 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
That's just human nature unfortunately, not special to ...
By JamesPa , 21 hours ago
-
@bontwoody how long has it been now since you started t...
By Mars , 1 day ago
-
RE: Bosch CS5800i 5kW - Experience So Far
Yes, over the last few days I've been keeping a very cl...
By Steelbadger , 1 day ago
-
Absolutely. I am one of those members and I most certai...
By Majordennisbloodnok , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@darrell-p There's another new Forum Member, @wully who...
By Transparent , 1 day ago