Below is an extract from the MIM-E03CN manual, which is the recommended controller for use with your heat pump.
Do you only have the one water pump?
Is your system still short cycling at the same frequency?
One possible problem could be incorrect settings within the controller. If possible go into the installer menu and make a note of any parameter settings that you can find, and then post the results.
@derek-m I have two pumps I believe. You can see both pumps in this pic.Â
I am still getting short cycling, yes.Â
What settings do you mean, sorry?Â
It's entirely possible the settings are incorrect, I've had to wing it to get as far as I have.Â
What is the temperature setting of the two thermostats, and what is their make and model?
Turn both thermostats up to 25C and see if this has any effect on the cycling.
@derek-m okay, I'm not at home at the moment. I'll do it later and report back. I've made various adjustment to water law which is Samsung for WC. The temp in the house is nice and the COP is acceptable too. Just the cycling. Thanks again
The Joule Samsung instructions are available on line, they don’t use a PWM pump. They have a separate interface PCB that comes after the MIM. I’ll see if I can find a link.
I would be inclined to get the installer to wire/plumb it up as per the Midsummer wholesale instructions that give details on how to fit a PWM pump and use the Samsung controller as the room stat.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
- 26 Forums
- 2,104 Topics
- 46.3 K Posts
- 103 Online
- 3,393 Members
Join Us!
Latest Posts
-
RE: Ecodan consuming 100kwh per day in new build!!!
It does indeed look like that, @skyefarmer. There is ...
By Majordennisbloodnok , 3 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist I found the switching between tariff jus...
By Toodles , 18 hours ago
-
RE: Plug and play solar. Thoughts?
Have a read of my previous posts on so-called Balcony S...
By Lucia , 21 hours ago
-
@editor @bart Hi, I can see a few problems with your in...
By Brendon Uys , 1 day ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 1 day ago
-
RE: Location of hot water isolation valve on cylinder
@rossowheels if you isolate the water supply in it will...
By ASHP-BOBBA , 2 days ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 2 days ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 2 days ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 3 days ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 3 days ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 3 days ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 3 days ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 4 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 4 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 4 days ago