Posted by: @craig1980@hughf well, that doesn't sound ideal. 😩
Whether it will make a whole lot of difference to your COP remains to be seen, but usually, with a modulating compressor (all modern ASHPs are inverter driven) and a modulating fan on the evaporator, you'd also want a speed controllable pump. This way when the ASHP modulates down, it can vary the pump speed to keep the delta-T within the optimum range.
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
That's a question to ask the installers.
Why did they suggest the Samsung unit?
Did they already have data to show that there was negligible increase in the COP by using an ASHP with the pump-speed variable?
Save energy... recycle electrons!
Samsung mono controller manual attached, this clearly shows the connection for external PWM pump control, Connection 10 on the main PCB.
It even says 'If you need an external inverter driven pump, make sure it is the same as that already installed' - then gives the grundfoss part number.
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @transparentThat's a question to ask the installers.
Why did they suggest the Samsung unit?
Did they already have data to show that there was negligible increase in the COP by using an ASHP with the pump-speed variable?
I doubt you'd get a meaningful answer from the installers.
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Hi Craig,
PWM stands for Pulse Width Modulation, it is a type of control signal used quite often to vary the speed of pump motors and the like. If you Google PWM you may find a detailed explanation.
@transparent I've had a chance to look through exactly what I have.Â
MCS certs for both.
NCIS certs for both.
Electrical installation certificate for both.
A copy of the G98 application.
No schematics or pre installation survey, I have asked for these so I'll see what I get.Â
Â
@transparent I doubt they'd know. They fit Samsung or Vaillant but normally Samsung in larger properties. The Vaillant they fit is not a monobloc.
Just as an update to this post yesterday's COP including water heating was very nearly 4. Electric usage was down at 11.1 with generation at 44. Happy with the numbers but still turning off for 20 seconds every 8 mins. I've turned the bedroom rad back on to see if more emitters would help but it hasn't.Â
Sat at between 18 and 19 all day except when solar gain took us above 21 degrees.
Also bled all rads today and got a decent amount of air out of 3 or 4 rads.Â
Posted by: @craig1980@hughf so, does this mean that had a different pump been connected we would be able to adjust pump speed? Thanks
If you wired it up with a pwm primary pump and used the samsung controller directly, I'd expect you'd see that COP up between 4 and 5 in the current weather.
If the Samsung controller had control of it's pump speed then it would be able to modulate all three components of the 'machine' - fan/pump/compressor.
I'm actually genuinely shocked that the Samsung monobloc isn't really very monobloc at all, and needs and external pump and flow switch. It makes me feel much more happy with my decision to go for an off-brand manufacturer for my own system (I went for a Cool Energy, made by SPRSUN in PRC, built on a complete Carel commercial refrigeration platform of parts)...
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 33 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
-
@rhh1, I’ll contact Daikin’s brand manager tomorrow and...
By Mars , 5 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
In a way I would like to agree with the final conclusio...
By JamesPa , 2 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
Day one is done. The system’s been fully flushed and ...
By Mars , 4 hours ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 5 hours ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 6 hours ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 6 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 9 hours ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 1 day ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 1 day ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 1 day ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 1 day ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 3 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 3 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 4 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 4 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 4 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 4 days ago