Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Do you have any thermostats or TRV's in your system? Are you using weather compensation control?
Do you have a buffer tank, low loss header or plate heat exchanger within your system?
Posted by: @grahamhlook i know its not what you want to hear but stop obsessing over the PWM output. Im afraid that most heat pumps dont really have a pwm function at all, they say they do in the book but the unit is not clever enough to control pump speed and inverter compressor speed. its just life. we have to move on. before we had PWM the units worked fine, they will do so now. if you have rapid cycling its not going to be fixed by altering the speed of the waiter through your unit.
Hi Graham,
Believe it or not but I agree with you !
Having looked over the last year at the poor , incompetent , support I have had from my "installer" .
I have to do something to reduce both the cycling and the bills .other than Change the Field parameters , get the PWM system at least working , what can I do?
I cannot replace pipes or tanks either physically or in the face of my aggressive "Installer".
I appreciate the difficulties involved in measuring actual flow rates and Temperatures within pipes! Difficult but not impossible to overcome.
Every temperature , pressure or flow rate Measurement currently involves inserting sensors into the pipe!......at Horrific expense!
If PWM pumps to not work properly , surely that is a problem for the Manufacturers. My old Gas boiler worked perfectly for seven years with PWM Motors, why can't Heat Pumps also work properly?
Surely, the computational power of the processors, built into , both the Heat pumps and their controllers, should, be capable or interrogating their environment?
Why do we not have a pc based program to design Heat pump environments ?
The "intuitive " non-numerical approach has surely past it's retirement age!
ian
Â
Â
Â
Â
Posted by: @grahamh...most heat pumps dont really have a pwm function at all,
we have to move on. before we had PWM the units worked fine, they will do so now.
In the time it's taken to discuss this matter here, we could've designed a micro-controller with a couple of temperature inputs and a genuine PWM output to a mains pump.
If that would be a useful 'product' to use across a range of heat pumps, then surely it's worthy of consideration.
Â
Posted by: @iantelescopeThe Second PWM Motor will have to be supplied with a home made "Arduino" source.
Yes... even an AT-Tiny85 would be adequate!
I have a solar-thermal controller with a PWM output. I connected it to the most common Grundfos 15/50, making sure that I set its 3-speed dial to 3 (full on).
So with the right design of separate PWM Driver Box, we don't need expensive pumps either.
Save energy... recycle electrons!
so I'm a little late to this thread but.. I have a samsung Gen6 16kw self installed. I have a grundfos UPMM 25-95 pump. physically I have a single circulation loop, open to all downstairs rads, upstairs on programmable TRV's. the pump PWM inputs are connected to the PWM terminals on the control PCB.
I haven't put a scope on the PWM (don't have a scope and no need because its working!). The system is behaving exactly as I expected it to. here is compressor frequency against flow rate against outdoor unit power consumption for this morning's heating run:
so as far as I can see, this unit is modulating down the flow rate in response to lower compressor freq, via PWM signal to the pump. because thats the only way it can be working in my house.
whether this is ideal for COP or not is another matter (I'm starting to come to the view that these long runs at low compressor output aren't that efficient, but I need more data)... but this discussion seemed to me to start from the premise that the PWM pump control on the samsung G6 doesn't work. I'm certain that it does. at least on mine!
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Hi Ian.
Following my trumpeting of my apparent success in correcting the losses in my heat pump I have to admit that the supposed improvement was an illusion!
Could I ask a question?
When working how does your Grundfos motor show that it is under PWM Control?
Is the green LED flashing at 12 HZ indicating External PWM Control.
Is the Green LED flashing at 1 Hz indicating that the Pump is under Manual control?
My "Grundfoss UPM3 FLEX AS" shows no sign that it is actually working despite being fed the correct 12 V PWM Signal .
Oh how I wish I had installed the system myself ...............You do not know the level of incompetence shown by some installers!
Â
iantelescope
Â
Â
Â
Â
Â
Â
Â
@iantelescope the UPMM pump which I have has no status LED's. It "just worked" - once I'd got the cabling correct. I did find that the labelling of GND and SIG was inconsistent on the control PCB versus the manual vs the printing on the inside of the cover. But trial and error approach found the right way round. I presume you've swapped the cables etc?
 the pump I have is specifically mentioned in the control kit install manual (page 22 - see below) and was recommended by my supplier. I have no information about the pump you're using.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @iancalderbank@iantelescope the UPMM pump which I have has no status LED's. It "just worked" - once I'd got the cabling correct. I did find that the labelling of GND and SIG was inconsistent on the control PCB versus the manual vs the printing on the inside of the cover. But trial and error approach found the right way round. I presume you've swapped the cables etc?
 the pump I have is specifically mentioned in the control kit install manual (page 22 - see below) and was recommended by my supplier. I have no information about the pump you're using.
-- Attachment is not available --
Â
What is the lowest capacity your heat pump can modulate?
Â
@dandee I didn't include output power on the previous graphs just for simplicity as was trying to show the group that flowrate / compressor / power will all modulate properly and PWM control is working...
so here's same graph with output power (calculated by Flow rate x DT every 30sec). the steady state power output in the latter part of the graph is 3.6-3.8kw with 1.0 - 1.15kw input.
I don't know that there are any published manufacturer modulation numbers.Â
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@dandeeÂ
Many thanks ......again I am astonished with the information about the SIG and REF inputs.............
specifically , How have you connected the SIG and REF wires ? What Grundfos cable colours are connected to your Sig/REF?
I have no idea about the minimum power rating allowing power control of my 5 kw Samsung but I guess about 25% of the 5 kkw Maximum rating,, circa 1.25 kw.
iantelescope
Â
@iantelescope  page 9 of this
 is quite clear
the SIG and REF terminals on the samsung controller board are connected to the PWM INPUT and REF cables on the pump. check your pump manual for colours. mine are
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Hi ian,
In frustration I have connected a Wave generator only to discover that you are right. The Wiring shown in the manuals is wrong the Ref appears to be connected to Blue wire while the PCB Output should be connected to the Brown wire.
I am very much NOT amused with Grundfos , Samsung or whoever is to blame.
Let me now try again.....some luck this time?
ian
 I wired it first of all following the instructions on the inside of the controller panel. didn't work. double checked everything. stuck a voltmeter on it and that gave me doubts as to which is GND and which is SIG. so I just thought - could it be as simple as they are wrong way round? and they were!
the grundfos pump cable labelling is right.
the naming of the PWM terminals on the samsung controller PCB , I believe is inconsistent (opposite) between the samsung manual and the labels on the inside of the controller panel.
I believe the instructions on the midsummer wholesale diagram are correct, but I only found that diagram after I'd got it working.
good luck.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 990 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 2 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 10 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 10 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 14 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 14 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 15 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 16 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 18 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 18 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 1 day ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 5 days ago