Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Do you have any thermostats or TRV's in your system? Are you using weather compensation control?
Do you have a buffer tank, low loss header or plate heat exchanger within your system?
Posted by: @grahamhlook i know its not what you want to hear but stop obsessing over the PWM output. Im afraid that most heat pumps dont really have a pwm function at all, they say they do in the book but the unit is not clever enough to control pump speed and inverter compressor speed. its just life. we have to move on. before we had PWM the units worked fine, they will do so now. if you have rapid cycling its not going to be fixed by altering the speed of the waiter through your unit.
Hi Graham,
Believe it or not but I agree with you !
Having looked over the last year at the poor , incompetent , support I have had from my "installer" .
I have to do something to reduce both the cycling and the bills .other than Change the Field parameters , get the PWM system at least working , what can I do?
I cannot replace pipes or tanks either physically or in the face of my aggressive "Installer".
I appreciate the difficulties involved in measuring actual flow rates and Temperatures within pipes! Difficult but not impossible to overcome.
Every temperature , pressure or flow rate Measurement currently involves inserting sensors into the pipe!......at Horrific expense!
If PWM pumps to not work properly , surely that is a problem for the Manufacturers. My old Gas boiler worked perfectly for seven years with PWM Motors, why can't Heat Pumps also work properly?
Surely, the computational power of the processors, built into , both the Heat pumps and their controllers, should, be capable or interrogating their environment?
Why do we not have a pc based program to design Heat pump environments ?
The "intuitive " non-numerical approach has surely past it's retirement age!
ian
Â
Â
Â
Â
Posted by: @grahamh...most heat pumps dont really have a pwm function at all,
we have to move on. before we had PWM the units worked fine, they will do so now.
In the time it's taken to discuss this matter here, we could've designed a micro-controller with a couple of temperature inputs and a genuine PWM output to a mains pump.
If that would be a useful 'product' to use across a range of heat pumps, then surely it's worthy of consideration.
Â
Posted by: @iantelescopeThe Second PWM Motor will have to be supplied with a home made "Arduino" source.
Yes... even an AT-Tiny85 would be adequate!
I have a solar-thermal controller with a PWM output. I connected it to the most common Grundfos 15/50, making sure that I set its 3-speed dial to 3 (full on).
So with the right design of separate PWM Driver Box, we don't need expensive pumps either.
Save energy... recycle electrons!
so I'm a little late to this thread but.. I have a samsung Gen6 16kw self installed. I have a grundfos UPMM 25-95 pump. physically I have a single circulation loop, open to all downstairs rads, upstairs on programmable TRV's. the pump PWM inputs are connected to the PWM terminals on the control PCB.
I haven't put a scope on the PWM (don't have a scope and no need because its working!). The system is behaving exactly as I expected it to. here is compressor frequency against flow rate against outdoor unit power consumption for this morning's heating run:
so as far as I can see, this unit is modulating down the flow rate in response to lower compressor freq, via PWM signal to the pump. because thats the only way it can be working in my house.
whether this is ideal for COP or not is another matter (I'm starting to come to the view that these long runs at low compressor output aren't that efficient, but I need more data)... but this discussion seemed to me to start from the premise that the PWM pump control on the samsung G6 doesn't work. I'm certain that it does. at least on mine!
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Hi Ian.
Following my trumpeting of my apparent success in correcting the losses in my heat pump I have to admit that the supposed improvement was an illusion!
Could I ask a question?
When working how does your Grundfos motor show that it is under PWM Control?
Is the green LED flashing at 12 HZ indicating External PWM Control.
Is the Green LED flashing at 1 Hz indicating that the Pump is under Manual control?
My "Grundfoss UPM3 FLEX AS" shows no sign that it is actually working despite being fed the correct 12 V PWM Signal .
Oh how I wish I had installed the system myself ...............You do not know the level of incompetence shown by some installers!
Â
iantelescope
Â
Â
Â
Â
Â
Â
Â
@iantelescope the UPMM pump which I have has no status LED's. It "just worked" - once I'd got the cabling correct. I did find that the labelling of GND and SIG was inconsistent on the control PCB versus the manual vs the printing on the inside of the cover. But trial and error approach found the right way round. I presume you've swapped the cables etc?
 the pump I have is specifically mentioned in the control kit install manual (page 22 - see below) and was recommended by my supplier. I have no information about the pump you're using.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @iancalderbank@iantelescope the UPMM pump which I have has no status LED's. It "just worked" - once I'd got the cabling correct. I did find that the labelling of GND and SIG was inconsistent on the control PCB versus the manual vs the printing on the inside of the cover. But trial and error approach found the right way round. I presume you've swapped the cables etc?
 the pump I have is specifically mentioned in the control kit install manual (page 22 - see below) and was recommended by my supplier. I have no information about the pump you're using.
-- Attachment is not available --
Â
What is the lowest capacity your heat pump can modulate?
Â
@dandee I didn't include output power on the previous graphs just for simplicity as was trying to show the group that flowrate / compressor / power will all modulate properly and PWM control is working...
so here's same graph with output power (calculated by Flow rate x DT every 30sec). the steady state power output in the latter part of the graph is 3.6-3.8kw with 1.0 - 1.15kw input.
I don't know that there are any published manufacturer modulation numbers.Â
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@dandeeÂ
Many thanks ......again I am astonished with the information about the SIG and REF inputs.............
specifically , How have you connected the SIG and REF wires ? What Grundfos cable colours are connected to your Sig/REF?
I have no idea about the minimum power rating allowing power control of my 5 kw Samsung but I guess about 25% of the 5 kkw Maximum rating,, circa 1.25 kw.
iantelescope
Â
@iantelescope  page 9 of this
 is quite clear
the SIG and REF terminals on the samsung controller board are connected to the PWM INPUT and REF cables on the pump. check your pump manual for colours. mine are
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Hi ian,
In frustration I have connected a Wave generator only to discover that you are right. The Wiring shown in the manuals is wrong the Ref appears to be connected to Blue wire while the PCB Output should be connected to the Brown wire.
I am very much NOT amused with Grundfos , Samsung or whoever is to blame.
Let me now try again.....some luck this time?
ian
 I wired it first of all following the instructions on the inside of the controller panel. didn't work. double checked everything. stuck a voltmeter on it and that gave me doubts as to which is GND and which is SIG. so I just thought - could it be as simple as they are wrong way round? and they were!
the grundfos pump cable labelling is right.
the naming of the PWM terminals on the samsung controller PCB , I believe is inconsistent (opposite) between the samsung manual and the labels on the inside of the controller panel.
I believe the instructions on the midsummer wholesale diagram are correct, but I only found that diagram after I'd got it working.
good luck.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 271 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Hush mode now released. I've not tried it yet. Should b...
By swwils , 58 minutes ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 1 hour ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 14 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 15 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 15 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 18 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago