12kW Samsung gen 6 short cycling

374 Posts
17 Users
63 Reactions
27.6 K Views
(@mike-h)
Reputable Member Member
1138 kWhs
Joined: 2 years ago
Posts: 121
 

Posted by: @craig1980

I was on what I believe is value #4. The one that says pump 3. This was giving the affect of short cycling. I'm listening by the UVC not the outside unit so my timings may be off as I was just basing it off of the noise of the water pumps. I'm not sure what tells it to turn off. 

PHE In and out are flow temps in and out. Not sure what relevance the Teva temps have to the system but interesting that yours has -50 too. 

 

Thanks Craig. What setting are you on now for 2092 and 2093? Also I note that you ran it for a short period without weather compensation at fixed flow temperatures. Can you outline the steps you took to do so? I can't work out how to do that.

 


   
ReplyQuote
(@craig1980)
Reputable Member Member
612 kWhs
Joined: 1 year ago
Posts: 144
Topic starter  

I'm on value 2 that says pump 1.

 

I used this YouTube clip to get away from WC. There is probably an easier/better way but this way served it's purpose. 

 


   
ReplyQuote
(@craig1980)
Reputable Member Member
612 kWhs
Joined: 1 year ago
Posts: 144
Topic starter  

@derek-m that is entirely possible. Would also explain the misuse of the description "indoor unit".


   
ReplyQuote



(@iantelescope)
Reputable Member Contributor
1357 kWhs
Joined: 1 year ago
Posts: 198
 

@derek-m Samsung gen 6 short cycling

Missing PWM Signal from SAMSUNG.

Following a recent visit by a SAMSUNG Engineer , one solution to my "short cycling" was the use of the PWM option shown in the SAMSUNG MANUAL .....

PWM MOTOR Controls 0001

 When told that I had tried to use the PWM Option to reduce the violent "short cycling" the SAMSUNG Engineer expressed no surprise , saying that he did not know "Why the PWM System did NOT WORK on many SAMSUNG HEAT PUMPS!.

A PWM Motor control "would reduce the violent switching apparent on the System Power load" .....

2178
RELAY ADDITION

The System was previously fitted with a 50 litre "Volumising tank" and a Heat Exchanger in vain attempts by my then "installer" at reducing the "short Cycling".

My "Installer" has now been "STUCK OFF TWICE by the MCS,NIC ,RECC ..........so it is down to me , to fix this.

Where can I get a SAMSUNG Control PCB with a working PWM Driver?

My Visiting SAMSUNG ENGINEER also proposed the "solution" on page 23 of the SAMSUNG Installation manual.

This additional relay would increase the unreliability with TWO Relays in series!

Something is amiss with the SAMSUNG Explanation.

ian

 


   
Craig1980 reacted
ReplyQuote
(@derek-m)
Illustrious Member Moderator
13719 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4164
 

@iantelescope

Are you operating your heat pump in Weather Compensation (WC) mode, and if so, what are the settings?


   
ReplyQuote
(@iantelescope)
Reputable Member Contributor
1357 kWhs
Joined: 1 year ago
Posts: 198
 

@derek-m Weather compensation settings.

My SAMSUNG HEAT PUMP has been run with Weather Compensation ( SAMSUNG WATER LAW ) since November.

Weather compensation saves about  7% on my other problem , the excessive Energy consumption caused by a low COP ( < 2.9 ) .

Weather compensation was enabled with field bit 2091 using options 2,3 or 4 experimentally. All settings in agreement with the visiting SAMSUNG Engineer.

The Volumising tank is connected by a valve and can be disconnected experimentally to no great effect.

After the excessive consumption during December the HOT WATER SYSTEM has been switched OFF relying on the Volumising tank to provide hot water to "complete de-icing", another problem with my Heat pump!

The visiting SAMSUNG Engineer visibly blushed when asked "why the PWM Motor systems does not work on many SAMSUNG Heat pumps".

It would appear that I need a Control PCB with a working PWM output to feed ONE of my TWO Grundfos PWM Hybrid FLEX AS PWM motors !

The rest , as they say,........................................................... is silence.

ian

 

 

 

 


   
ReplyQuote
(@derek-m)
Illustrious Member Moderator
13719 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4164
 

Posted by: @iantelescope

@derek-m Weather compensation settings.

My SAMSUNG HEAT PUMP has been run with Weather Compensation ( SAMSUNG WATER LAW ) since November.

Weather compensation saves about  7% on my other problem , the excessive Energy consumption caused by a low COP ( < 2.9 ) .

Weather compensation was enabled with field bit 2091 using options 2,3 or 4 experimentally. All settings in agreement with the visiting SAMSUNG Engineer.

The Volumising tank is connected by a valve and can be disconnected experimentally to no great effect.

After the excessive consumption during December the HOT WATER SYSTEM has been switched OFF relying on the Volumising tank to provide hot water to "complete de-icing", another problem with my Heat pump!

The visiting SAMSUNG Engineer visibly blushed when asked "why the PWM Motor systems does not work on many SAMSUNG Heat pumps".

It would appear that I need a Control PCB with a working PWM output to feed ONE of my TWO Grundfos PWM Hybrid FLEX AS PWM motors !

The rest , as they say,........................................................... is silence.

ian

 

 

 

 

Switching on WC may show some improvement in efficiency, but the settings need to be matched to the heat loss of your home. What are the WC settings and what are the LWT and RWT at different outside air temperatures? Do you have any thermostats or TRV's that are operating?

There are quite a number of threads on the forum at the moment, which are discussing the accuracy of energy measurements and COP calculations. A COP of 2.9 in colder weather is not too bad.

What is the size of your home and the electrical energy consumption?

Do you have a buffer tank, low loss header or plate heat exchanger within your system?

All heat pumps need to defrost during colder weather operation, so yours is not unique.

Was a PMW controlled water pump specified in the quotation, in which case a Control PCB should have been installed as part of the package.

 


   
ReplyQuote
(@iantelescope)
Reputable Member Contributor
1357 kWhs
Joined: 1 year ago
Posts: 198
 

@derek-m My SAMSUNG HEAT PUMP Problems.....

Given I live in Scotland I have moved the Water Law Curves down to a -5 C Outside temperature with a flow water temperature of 45 C.

Field bits 201,202 1nd 203 .

WL2 1

The Samsung Heat came fitted with an  unwanted,  Heat Exchanger.

A 50 litre Volumising tank was installed some four months after the initial installation , fitted to "allow the Heat Exchanger to complete DE-icing ( SAMSUNG Dalliam)".

 

The Heat pump is fitted with both Electrical power input meters and a  output Heat Water meter giving the Actual REAL COP as 

 

COP and REAL COP

My "installer" has now been Struck OFF TWICE by the NIC.

I have not been permitted to see the  SAMSUNG report into my "installation" but the audible silence from my "installer", the MCS,NIC,RECC Regulatory "Charities" and SAMSUNG themselves  speaks volumes..

The visiting SAMSUNG ENGINEER advised fitting the extra Relay " to prevent excessive arcing on the SAMSUNG PCB Relay" . Hmm.....!

See the

RELAY ADDITION

following diagram.

 

ian

 


   
ReplyQuote
(@derek-m)
Illustrious Member Moderator
13719 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4164
 

@iantelescope

Why TWICE? Did they allow him to rejoin after slapping his wrist?

I would suggest that you record the temperatures around your heat exchanger, since you could be loosing maybe 5C between primary and secondary water temperatures. Producing LWT 5C higher than required will lower the overall COP.

The only valid reason that I can think of to install a heat exchanger, would be to isolate the primary and secondary water, so that cheaper (toxic) anti-freeze can be used instead of the more expensive (none toxic) type.


   
ReplyQuote



(@ken-bone)
Eminent Member Member
178 kWhs
Expert
Joined: 3 years ago
Posts: 20
 

@iantelescope run the system open loop, adjust the curve settings down so you are not overshooting in comfort temperature.

Most systems I install,  are like this, including my own.

I have a Samsung 16kw 11 years old.

This is my heating  run cycles today.

Screenshot 20230411 190618

 

Heat pump installer


   
ReplyQuote
Graham Hendra
(@grahamh)
Reputable Member Member
1898 kWhs
Expert
Joined: 3 years ago
Posts: 100
 

11 years ago this was easy ken. But much harder now. Units over the last couple of years don't ramp down much below 30 or 40%. And they really hate running sub 30c flow. It's all to do with the low cops you get at low compressor speeds. Because of the wired obsession with cop not run cost the manufacturers cycle the unit as it gets a better cop. But not necessarily lower run costs. 

Heat pump expert


   
ReplyQuote
Graham Hendra
(@grahamh)
Reputable Member Member
1898 kWhs
Expert
Joined: 3 years ago
Posts: 100
 

It's all here

 

Heat pump expert


   
ReplyQuote