As you say, nothing appears to be changing dramatically. Though I fail to understand how your home is maintaining an indoor temperature of 18C, with an outdoor temperature of 6C.
Now try setting your system in fixed LWT mode with a setting of 35C.
Â
@derek-m I've no idea. 🤣
I turned the system off for the Octopus saving session at 17:30 room stats showing 18. Went out and came back at 20:30. Turned back on and room stats were at 17.5. Not sure if you need that info but just in case it's relevant.Â
I'll have to work out how to set fixed lwt mode. I'll do it tomorrow. Thanks again.Â
@derek-m overnight it was 4 degrees and it has struggled to keep 18. The house is at 17.5 this morning. COP is down to 3.3 and it's using more power and running for longer. 15.6kw yesterday 13.3hours operation time (that's with turning off for 3hours)and a generation of 51.7.
@derek-m overnight it was 4 degrees and it has struggled to keep 18. The house is at 17.5 this morning. COP is down to 3.3 and it's using more power and running for longer. 15.6kw yesterday 13.3hours operation time (that's with turning off for 3hours)and a generation of 51.7.
Posted by: @craig1980Is this what you mean?
Â
Yes, that would appear to be the correct method. Try running with a LWT of 35C and see how the system responds, and if it stops the 20 second off periods.
Â
Okay, that's done. It was already on standard temperature "water outlet". Could that have been an issue?Â
How is the system operating now? Is it still running 8 mins on and 20 secs off?
What is happening with the room and radiator temps?
What are the flow and temperature readings etc?
Changing the way that the system is being operated is to try to find what is causing the 20 seconds shutdown.
So, it appears to run constantly but at quite high power usage of 1.9kw instantaneous power.Â
Rads feel warmer to the touch but room temp stays at around 18 according to room stats and thermometers that I used for radiator temps.Â
Outside temp is 6.0 according to wired remote.
Water outlet 35.4
Indoor 21.5 (remember, this is in the airing cupboard with the UVC).Â
Posted by: @craig1980So, it appears to run constantly but at quite high power usage of 1.9kw instantaneous power.Â
Rads feel warmer to the touch but room temp stays at around 18 according to room stats and thermometers that I used for radiator temps.Â
Outside temp is 6.0 according to wired remote.
Water outlet 35.4
Indoor 21.5 (remember, this is in the airing cupboard with the UVC).Â
Now measure the top and bottom temperatures on two or three relevant radiators, and the flow rate and temperature readings from the information screens.
Â
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 33 Online
- 5,656 Members
Join Us!
Podcast Picks
Latest Posts
-
Anyone still weathering it out with Agile?
Being curious, I have continued to monitor the daily ra...
By Toodles , 1 hour ago
-
RE: ASHP heat output monitoring
Thats true. Ideally the FT could go up a bit further i...
By JamesPa , 3 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 5 hours ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 24 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist I have never cleaned the mag filter myse...
By Toodles , 24 hours ago
-
RE: How much am I ‘saving’?
@old_scientist like for like comparisons are almost imp...
By Tim441 , 24 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 1 day ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 1 day ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 3 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 3 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 3 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 4 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@sandy, I'll send Vaillant an email tomorrow and see if...
By Mars , 4 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 4 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 5 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 1 week ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 1 week ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 1 week ago