I've just watched the outside temp on the display for the whole 8 min run. It starts at 6.6 degrees then by around 4 mins it's dropped to 6.3 degrees then in the last minute or so it climbs back to 6.6 where it cuts out for 20 seconds but starts again when still on 6.6.Â
I'm looking for something changing, during the 20 second period, from the heat pump switching off, to it restarting.
Correct me if I am wrong, that your heat pump runs for 8 minutes or so, switches off for 20 seconds, then runs for a further 8 minutes or so, etc. etc.
A further thing that I find quite surprising is how low are the temperatures of your radiators, your home must be very well insulated.
The next test to try would be to change the controller mode from WC to a fixed LWT of say 35C, and see what effect this has on how your heat pump operates, and what changes occur to the radiator temperatures and room temperatures.
Yes, that's correct. 8 mins on, 20 seconds off then 8 on ad infinitum. There is no change in the outside temp during the 20 seconds.Â
I'm not sure if it's that great on insulation. Cavity wall beads, loft insulation, large double glazed windows but heating sits at 18-18.5 all day. Heat pump is on 24-7.Â
Posted by: @craig1980Yes, that's correct. 8 mins on, 20 seconds off then 8 on ad infinitum. There is no change in the outside temp during the 20 seconds.Â
I'm not sure if it's that great on insulation. Cavity wall beads, loft insulation, large double glazed windows but heating sits at 18-18.5 all day. Heat pump is on 24-7.Â
The temperatures measured on your radiators would indicate that there is very little heat energy being transferred into your home.
Â
Try pulling up the 'Indoor Zone Status Information' as shown on page 18 in the manual shown below.
Thanks,
Now try monitoring the 'Master Indoor Zone Information', particularly as the 20 second off period ends and the heat pump restarts.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 41 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
@editor Well, it is not the Altherma range, they are de...
By Toodles , 56 seconds ago
-
RE: Big Changes Coming to Our Heat Pump System
Day one is done. The system’s been fully flushed and ...
By Mars , 14 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@jamespa - I think the key thing is the current (as in ...
By cathodeRay , 1 hour ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 2 hours ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 2 hours ago
-
So after asking the technical department for an update ...
By bontwoody , 2 hours ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 3 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 6 hours ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 1 day ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 1 day ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 1 day ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 1 day ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 3 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 3 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 4 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 4 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 4 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 4 days ago